Hi all,
The search broadcast load is reduced in any case simply because the gateway only
has to connect when the first client starts up. Then even when the client
terminates, the connection is held open for 2 hours. So no client started within
the next two hours will generate a new search request. The CPU load should also
be reduced because the IOC has to update only one client.
I think the gateway open a maximum of two subscriptions to a channel,
value+alarm and archive+alarm monitors. And even that only with the option
-archive. As far as I remember without looking at the code, alarm monitors are
handled within the gateway: The gateway simply drops monitor events to
alarm-only clients when the alarm status did not change. This was one of the
changes in the recent version. I requested that because setting the mask in the
command line was not transparent enough.
Dirk
Ralph Lange wrote:
Ernest L. Williams Jr. wrote:
Ralph Lange wrote:
Caching/no-caching:
Among the GW's objectives are keeping load off the IOCs and acting
transparently. With certain aspects of Channel Access, e.g. answering
get requests, forwarding IOC-side beacons to the clients, and
forwarding client side name-resolution-requests to the IOCs, these
two objectives are contrary. If the GW acts 100% transparent, it does
not offload the IOCs (in some cases, it would even put more load onto
the IOCs). If the GW tries to shield the IOCs, it will not be able to
act completely transparent. While the original approach was trying to
implement a reasonable compromise, the direction that Dirk is
pursuing is certainly the right one: when the level of compromise is
made configurable for these aspects, the user can select the
appropriate behavior for each GW instance.
Ralph do you agree that with respect to TCP-circuit load the IOC does
get shielded?
So, yes the IOCs will get hit with search requests (UDP, BCAST) but
this is as you say a trade-off.
Also, statistically most connections to PVs are monitored as opposed
to cagets.
Hi Ernest,
yes, the TCP circuit load is reduced, as there's only one circuit
between the GW and the IOC. Note, though, that this usually only reduces
memory consumption. For the CPU load, update rate (number of
subscriptions and data rate) and search requests are more important.
Through a GW, only one TCP circuit is used, and the number of
subscriptions for a PV will be limited to three (worst case: one
subscription each for VALUE, ARCHIVE, and ALARM events). That's the
result of a CA design flaw: when a client (in this case: the GW) sets up
a subscription with multiple bits in the event type mask set, an
incoming data update will not have the information which event type it
is connected with. So, a GW with value, alarm and archive clients has to
subscribe for value, alarm, and archive events separately to be able to
send the right value updates to the right customers.
So, in the rare worst case (one client asking through a GW for value,
archive, and alarm) the number of subscriptions on the IOC will triple
compared to a non-GW direct connection. Even the update rate and network
load triple in the case of every PV change causing value, archive, and
alarm events.
Still, you are right, in most real-world cases (with most connections
being subscriptions), the GW will reduce the TCP circuit and the update
rate load on the IOCs.
Ralph
Dr. Dirk Zimoch
Paul Scherrer Institut, WBGB/006
5232 Villigen PSI, Switzerland
Phone +41 56 310 5182
- RE: GW status Jeff Hill
- Re: GW status Stephen Lewis
- Re: GW status Ralph Lange
- Re: GW status Ernest L. Williams Jr.
VWTime driver Kalantari Babak
<2009>
2025
2026
Re: GW status Dirk Zimoch
<2009>
2025
2026