1994  1995  1996  1997  1998  <1999>  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  <1999>  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: Watchdog record
To: [email protected], [email protected]
Cc: [email protected]
Date: Wed, 27 Oct 1999 16:51:09 -0500 (CDT)
> Has anyone created a record or simple pattern of records that acts as a
> watchdog?  In other words, one that will give a signal if a response does
> not come back from a hardware device within a setable time period.
Well, kind of.
A simple calc record that decrements every scan can act as a watchdog. If
whatever you are watchdogging simply loads a constant into the val field
often enough such that it doesn't decrement to 0, then a 0 would indicate
the timeout. If you make it a calcout record, you could poke something
else with the out link when the watchdog expired.
record(calcout,"$(S):imageBusy") {
        field(SCAN,"1 second")
        field(CALC,"A<=0?0:A-1")
        field(INPA,"$(S):imageBusy.VAL NPP NMS")
        field(OUT,"$(S):imageBusyReset.PROC PP MS")
        field(OOPT,"When Zero")
        field(DOPT,"Use OCAL")
        field(OCAL,"0")
Something better write to $(S):imageBusy.VAL before it gets to 0 ...
This can be used to determine in the database if a particular client is running.
The client simply writes a value to $(S):imageBusy.VAL periodically or the
database assumes its not active.
	Ned
Re: Watchdog record Maren Purves
Re: Watchdog record Ralph . Lange
Prev: ni gpib Marty Kraimer
Next: Re: Watchdog record Maren Purves
Index: 1994  1995  1996  1997  1998  <1999>  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: Re: ni gpib Marty Kraimer