Andrei,
> PC checks serial number and prints on terminal port if data was
> lost or come twice. Time to time (very seldom) I read both problems.
Within an EPICS IOC the scan tasks run at relatively high priority and the
CA server runs at relatively low priority. This design ensures proper
independence of scan tasks from introduced client load.
When a record is processed, and it needs to provide a subscription update to
the CA server, it places the update in a queue. When the CA server gets an
opportunity to run it reads any events that might be waiting on the queue
and sends them over the wire to the CA clients that are subscribed.
To protect the IOC, there is a quota limiting the maximum length of the CA
subscription update event queue. When this quota is exceeded the last event
on the queue for a particular subscription is replaced. This means that if
there is a (possibly brief) period where the scan tasks produce subscription
updates at a rate that exceeds the rate at which the server can send
subscription updates to the client or the rate at which the client processes
subscription updates then the buffering capacity of the event queue can be
exceeded. The bursty nature of CPU and network loads can make this situation
more likely to occur. CPU and network load reporting diagnostics tend to
report aggregate loads averaged over time, and do not tend to report load
burst statistics. That would require a strip chart or a histogram.
Furthermore, the memory management for the CA event queue is currently
optimized for use with scalar value / time stamp / alarm status tuple
updates. This means that multiple value updates might be queued together at
once allowing intermediate values to not be discarded during brief periods
of client or network load saturation. In contrast, array value / time stamp
/ alarm status tuples are not queued by the system. The quota for these
updates is exactly one update, and therefore it is very likely that
intermediate values can be discarded during brief intervals where the client
CPU load or network load saturate. This behavior is by design. We were very
careful to not call malloc/free for queuing of random sized arrays because
of concerns about excessive CPU loading and fragmentation of pool. Worse
yet, since array element values are not placed on the queue then, with
arrays, the event is only a signal that an update is required. The actual
value that is sent is whatever that might be in the database at the time
that the server reads the place holder array update event from the queue.
This means that the same update value might be sent twice (as you have
observed).
The above is a well known limitation of the system at this time. With EPICS
V4 we intend to eliminate this problem by transferring event queue memory
management responsibility to the event producer.
Jeff
> -----Original Message-----
> From: Liyu, Andrei [mailto:[email protected]]
> Sent: Monday, August 22, 2005 8:43 AM
> To: [email protected]
> Subject: CA loss package on 1 Hz rate
> Hi,
> SNS BLM system has 2 levels. First level is VME based/vxWorks
> (IOC). Second level is PC/Windows (PC) - similar CAGateway. IOC sends
> data one time per second to PC. Data is arrays (one array (720 floats)
> per detector; up to 32 detectors per IOC). Array has information about
> serial number of current package. PC checks serial number and prints on
> terminal port if data was lost or come twice. Time to time (very seldom)
> SNS works on 1 Hz now. IOC CPU loading ~ 3-5% and PC CPU loading
> 5%. On 60 Hz IOC will have 30% on 60 Hz. PC doesn't depend of
> accelerator rate but depends from clients quantity.
> I hoped to use CAArchive to find source of problem. But I met
> another problem. Archive lost connection to IOC when IOC/PC connection
> was Ok.
> Does anyone see this problem? Any other suggestions to find the
> source (IOC, network, PC)?
> Thanks, Andrei.
- CA loss package on 1 Hz rate Liyu, Andrei
Re: Suitable PC104 board for EPICS/Linux Rolf Keitel
<2005>
Re: CA loss package on 1 Hz rate Motoki Ooi
<2005>
