1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025
Subject: Re: Comms issue with New Focus 8752 motor driver
To: Mark Rivers <[email protected]>, "[email protected]" <[email protected]>, Michael Dunning <[email protected]>
Date: Thu, 22 Aug 2013 10:19:37 -0700
Hi Mark,
This is very interesting. Could it be that this effect is also responsible for my problems with Beckhoff devices? I have made modifications to both the drvAsynIPPort to test the return code from the poll() routine a few weeks ago when I started suspecting this. Unfortunately, shortly before I made the modification, the Beckhoff IOC errors stopped when the laboratory went into summer shutdown mode. I still don't understand what was causing the Beckhoff errors in the first place. I take it from your description of the problem that if area detector is running on the same Linux machine where an IOC which is using drvAsynIPPort is, then the IOC might be affected by the area detector generating an EINTR signal. I am not sure that this is exactly the situation here. I need to check into this. Could some other EPICS IOC do similar thing as the area detector does?
Zen
On 08/22/13 08:20, [email protected] wrote:
Following some off-line discussions with Mark, I can report the actual problem wasn't specific to the 8752 driver, but an interaction between the Prosilica AreaDetector camera driver (which my IOC was also running) and asyn which was causing the 8752 driver's asyn read call to return prematurely.  Mark described the problem much more eloquently than I can:
The Prosilica library uses Posix high-precision timer library.  That library uses signals that can cause Linux system functions to return
prematurely returning EINTR, so they must be restarted.  Andrew Johnson fixed this problem in base some time ago when I first discovered
the problem when using Prosilica cameras.
I am pretty sure the drvAsynIPPort module has a bug.  It is calling poll(), but not checking the response at all.  It assumes that if poll() returned
then the port has new data.  But this is incorrect, because according to the documentation poll() can return EINTR
Mark has now updated drvAsynIPPort.c in revision r2251 at https://svn.aps.anl.gov/epics/asyn/trunk/ which fixes the problem nicely, so doubtless it appear in the next asyn release also.
Many thanks to Mark for the fix, and to Eric and Kevin for their helpful suggestions.
Tim
-----Original Message-----
Date: Tue, 20 Aug 2013 19:25:19 +0000
To: "'[email protected]'" <[email protected]>,
Subject: RE: Comms issue with New Focus 8752 motor driver
It seems that sometimes when the VER command is issued the response does not arrive before the timeout expires.  But then it does eventually arrive, and screws up the expected response to the DRT command.  The timeout is defined on this line in the driver:
#define PMNC_TIMEOUT    3.0     /* Command timeout in sec. */
There is something I really don't understand in the output:
2013/08/20 17:37:57.709 192.168.42.31:23 write 4
VER\r
2013/08/20 17:37:57.716 192.168.42.31:23 read 1
send_recv_mess(): recv message = ""
send_recv_mess(): message = VER
2013/08/20 17:37:57.717 192.168.42.31:23 write 4
VER\r
send_recv_mess(): ERROR - staus =1, nread = 0
2013/08/20 17:37:57.736 192.168.42.31:23 write 4
VER\r
2013/08/20 17:37:57.742 192.168.42.31:23 read 16
Version 1.6.0\r\n>
send_recv_mess(): recv message = "Version 1.6.0
The line
Is coming from this code (note the typo on status, spelled staus):
     /* Perform atomic write/read operation  */
     status = pasynOctetSyncIO->writeRead(cntrl->pasynUser, send_com, size,
                                          recv_com, BUFF_SIZE-1,
                                          PMNC_TIMEOUT, &nwrite, &nread, &eomReason);
     if (eos)
       // Reset EOS to default
       pasynOctetSyncIO->setInputEos(cntrl->pasynUser,PROMPT_EOS,strlen(PROMPT_EOS));
     if (status != asynSuccess)
       int int_status = (int) status;
       Debug(3, "send_recv_mess(): ERROR - staus =%d, nread = %d\n", int_status, nread);
       recv_com[0] = '\0';
       return(MESS_ERR);
status=1 is asynTimeout.  So this is saying that the writeRead operation failed with a timeout on the read, and nread=0.
But look at the timestamps above. Only 19 ms has elapsed between the second 2 "write 4" messages, but in that time the read has timed out!  This does not make sense, there should be a 3 second delay in there before the read times out.
RE: Comms issue with New Focus 8752 motor driver Mark Rivers
RE: Comms issue with New Focus 8752 motor driver tim.hayton
Prev: RE: EPICS and MEDM with eclipse Brown, Garth
Next: RE: Comms issue with New Focus 8752 motor driver Mark Rivers
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025
Prev: RE: Comms issue with New Focus 8752 motor driver tim.hayton
ANJ, 20 Apr 2015 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions ·
