1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <2016>  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <2016>  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: Lock/Mutex to prevent "caget" from cutting in between updating multiple fields
To: "Zhang, Dehong" <[email protected]>, "Mooney, Tim M." <[email protected]>, "[email protected]" <[email protected]>, "Dalesio, Bob" <[email protected]>, "Williams Jr., Ernest L." <[email protected]>
Date: Mon, 2 May 2016 08:45:22 -0700
Dehong
First of all - these are not dumb questions but very important ones.
Ralph has already answered them in detail but there was a little confusion
around consistency of array data and timestamps.
In summary: even 3.14 guarantees that all array data along with timestamp
and status are obtained via CA as a consistent set.
Basically: both, database scanning (record processing) and CA use dbScanLock()
on the involved record(s)' lockset for synchronization.
HTH
- Till
On 05/01/2016 12:55 AM, Zhang, Dehong wrote:
Hi Tim, Till and Bob,
Thank you very much for the advices.  Could one of you, or any other EPICS experts
seeing this message, please spare a few minutes to compile a short summery, to answer
the following questions (for 3.14.12):
1. is it true that all the "process" functions of all the records within one IOC share ONE
    thread?  So we should avoid having within one IOC multiple records which have
    extensive calculations (including memory copying) in their "process" functions?
2. the CA server uses another thread(s) with lower priority for broadcasting to "camonitor"s
    and replying to "caget"s?  Is this thread(s) shared by all the records?
3. does the CA server have its own buffers for each field/broadcasts?  Or it shares the same
    memory locations with the records?
    Here the answer seems to be "yes" for scaler fields, BUT "no" for string or array fields:
    From section 15.6 of the AppDevGuide:
The function db_post_events is written so that record support will never be blocked attempting to post an event because a slow client is not able to process events fast enough. Each call to db_post_events causes the current value, alarm status, and time stamp for the field to be copied into a ring buffer. The thread calling db_post_events will not be delayed by any network or memory allocation overhead. A lower priority thread in the server is responsible for transferring the events in the event queue to the channel access clients that may be monitoring the process variable.
Currently, when an event is posted for a DBF_STRING field or a field containing array data the value is NOT saved in the ring buffer and the client will receive whatever value happens to be in the field when the lower priority thread transfers the event to the client. This behavior may be improved in the future.
    does this mean that there is NO guarantee that string/array fields will have the correct
    time stamps?
4. what happens when the CA server replies to "caget"?  Do we also have this "scalers are
    buffered, but string/arrays are not" issue?  Or "nothing is buffered, but takes whatever
    is available (old data and new time stamp, or new data and old time stamp etc) at that
    particular moment?
5. for completeness, a real dumb question: if I don't, or haven't have time yet to, call "db_post_event",
    the "camonitor"s will certainly not get anything, but can a "caget" still get the current value?
Sorry for all these dumb questions.  More and more we are using EPICS in a daq fashion.
From the above document, I see a great danger in correctly assigning time stamps to
string/array data.  Without patching EPICS base, it seems there is no lock/mutex will help
to close this hole.  Hopefully it is me who missed something.
(Or, we will have to embed the time stamp within/after the data?)
Please advice.
Thank you again, best regards,
Dehong
Sent: Friday, April 29, 2016 11:54 PM
To: Mooney, Tim M.; Zhang, Dehong; [email protected]
I would be a little bit more conservative and stress that this kind of thinking is very
dangerous.
Your scenario might work on a real-time system with properly assigned priorities
"most of the time".
However, if you have e.g., an unprivileged IOC running under linux then it will use
a time-sharing scheduler where every thread essentially has the same priority and
can be preempted when it's time-slice is consumed. Under such a scenario it can
happen that record processing is pre-empted and the IOC side of caget
could interfere.
Even under a RTOS your assumption is dangerous: assume that the caget thread
indeed has a lower priority than the record-processing one. It is still possible
for the effective priority of caget to be raised above record-processing e.g., as a
result of caget holding a priority-inheriting mutex on which a high-priority thread
is waiting and then caget could preempt record-processing.
Properly written code should IMHO use either lockfree algorithms or synchronization
devices and never rely on assumptions about scheduling for synchronization.
The good news are that EPICS is properly written code in that sense and caget
respects the database locking. So it is ensured that you never get a field value
with an incorrect timestamp since both are read 'atomically' by CA.
OTOH, you cannot read multiple fields atomically with caget (AFAIK). I.e.,
if your record has fields 'A' and 'B' then you cannot be sure caget(A); caget(B)
yields a consistent set. One could be new, one old.
There are work-arounds:
 - you can use an 'array' field. All elements of an array are accessed by CÁ atomically.
   E.g., when you caget a waveform record then you always get a consistent waveform
   (with a consistent timestamp), never a half-old, half-new one.
 - you could introduce locking semantics yourself. E.g., a 'LOCK' field. Record
   processing may not modify the essential fields while this is set. The user then
   has to caput(LOCK, 1); caget(FIELD1); caget(FIELD2), ...; caput(LOCK, 0);
   but you have to rely on the user observing the semantics.
-- Till
On 04/29/2016 09:56 PM, Mooney, Tim M. wrote:
Hi Dehong,
I don't think the IOC side of a caget is ever going to get any CPU cycles while your record is processing unless you voluntarily give up the processor - for example, by calling asynchronous device support, or by waiting for something (which record support isn't supposed to do anyway).  If all the fields that must be atomic are in the same record instance, I think you're ok.
Tim Mooney ([email protected]) (630)252-5417
Beamline Controls Group (www.aps.anl.gov)
Advanced Photon Source, Argonne National Lab
From: [email protected] [[email protected]] on behalf of Zhang, Dehong [[email protected]]
Sent: Friday, April 29, 2016 6:12 PM
To: [email protected]
Subject: Lock/Mutex to prevent "caget" from cutting in between updating multiple fields
In my custom record, I need to update multiple fields atomically so they stay
synchronized -- all updated, or none updated; not a few updated, but a few with the
old data.  If I use my own mutex, I suspect that "caget" can cut in between the
updating and gets, for example, new data with old time stamp, or old data with
new time stamp depending on the order of updating.
And I guess "camonitor" would not have this problem because it would be the server
pushing the whole set (field itself and time stamp for instance).  Is this right?
So to close this hole with "caget", which global lock should I use?  dbScanLock?
Thank you, best regards,
Dehong
RE: Lock/Mutex to prevent "caget" from cutting in between updating multiple fields Kim, Kukhee
Lock/Mutex to prevent "caget" from cutting in between updating multiple fields Zhang, Dehong
RE: Lock/Mutex to prevent "caget" from cutting in between updating multiple fields Mooney, Tim M.
Re: Lock/Mutex to prevent "caget" from cutting in between updating multiple fields Till Straumann
Re: Lock/Mutex to prevent "caget" from cutting in between updating multiple fields Zhang, Dehong
Prev: RE: EPICS 2016 Spring Meeting at ESS, Lund, Sweden Mark Rivers
Next: Re: Alarm Server start problem and how to compile JCA on Fedora20 64 bit system ? Kasemir, Kay
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <2016>  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: Re: Lock/Mutex to prevent "caget" from cutting in between updating multiple fields Till Straumann
Next: RE: Lock/Mutex to prevent "caget" from cutting in between updating multiple fields Kim, Kukhee
ANJ, 15 Jul 2016 · Home · News · About · Talk · Base · Modules · Extensions ·