Subject: Re: Motor record: No longer issues a stop command when motor already stopped?
To: "[email protected]" <[email protected]>, "[email protected]" <[email protected]>
Cc: EPICS <[email protected]>
Date: Fri, 7 Jul 2017 14:57:30 +0000
Hello James and Arvinder,
I apologize, James, for not responding to your tech-talk post. I see that I did not delete it from my inbox, so it (like so much else) must have fallen off my radar.
I am fairly confident that the change in behavior you are seeing is due to this change; or more accurately, this is a consequence of the "Allow moving out of invalid soft limit travel range toward valid soft limit travel range." change. The relevant modifications there are on lines #1341-1342 -> #1366-1368, where the limit violation error check was changed in two ways. First, the error check itself was changed from always being performed, to only being performed while commanded motion was active (jog, home or move). Second the error check was changed from using the feedback (drbv) to the reference (dval).
Ron
On 07/06/2017 10:24 AM, [email protected] wrote:
Hello,
we posted a topic on the mailing list not long ago about a change in behaviour of motor limits, and we didn't receive any replies.
As you are both listed as owners of the motor module, I was wondering if you may have an idea as to how the changes from 6-7-1 to 6-9 would change the motor limit behaviour from regularly registering a limit violation with a jittering encoder to not registering a limit violation once the motor has stopped.
The regular limit violations was causing stop signals to be sent, which caused an in vacuum motor to heat up. In upgrading motor, this problem went away, which is good, but we don't understand why, which is not quite as good.
If you could shed any light on this, it would be really appreciated. I have copied the original email sent to tech-talk below.
Yours sincerely,
Arvinder Palaha
Beamline Control Systems
DH G.63
T: +44-(0)1235-77-8137
E: [email protected]
At Diamond we often implement a software PLC on the motor controllers to disable the amplifier of in-vacuum motors (sending a kill command) when they have completed a move.  This is to avoid the motors overheating in vacuum.
However, recently we had an overheating problem on an in-vacuum motor because a motor amplifier was constantly being re-energised after this PLC had de-energised it.  This was due to the motor’s flickering encoder causing it to regularly register a soft limit condition.  Whenever the motor record went into a soft limit state it issued a Stop command to the motor re-energising its amplifier.  The PLC and the motor record would then ‘fight’ each other, one disabling the motor, the other enabling it.
We were using motor record version 6-7-1 when we encountered this issue.  After upgrading to 6-9 the problem appears to have gone away.  This is good news but I would like to understand what may have changed to avoid this situation?  I see a lot of limit related changes have happened between these two release numbers.  Can anyone point me to a change which may explain the fix we see?
The change must be to do with not sending a Stop command if the motor is already stopped?
Thanks for any guidance,
James
RE: Motor record: No longer issues a stop command when motor already stopped? James.OHea
Prev: EPUCS Qt release 3.5.1 Andrew C. Starritt
Next: Autosave for waveform with 1 element Paduan Donadio, Marcio
Prev: Motor record: No longer issues a stop command when motor already stopped? James.OHea
Next: RE: Motor record: No longer issues a stop command when motor already stopped? James.OHea
