1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026
Subject: Re: Question about "error calling writeRead" in modbus
From: "Wang, SuYin Grass via Tech-talk" <[email protected]>
To: "Rivers, Mark L." <[email protected]>
Date: Thu, 1 Jul 2021 16:22:25 +0000
Hi Mark,
Thank you for the quick reply.
The simulator is configured to support Modbus function 3 on those addresses.
I changed the pollMsec=0 and that removed the error. Thanks again!
Grass
Sent: Thursday, July 1, 2021 11:18 AM
To: Wang, SuYin Grass <[email protected]>
Cc: [email protected] <[email protected]>
Hi Grass,
Ø  drvModbusAsynConfigure("ctrl",      "RKamp",1,6,1, 3,0,100,"RKamp")
Ø  2021/07/01 09:55:26.074 drvModbusAsyn::doModbusIO port ctrl error calling writeRead, error=xxx.xxx.xxx.xxx:4502 timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
Your drvModbusAsynConfigure command has the following parameters:
-          asyn portName = “ctrl”
-          asyn tcpPortName = “RKamp”
-          slaveAddress = 1
-          modbusFunction = 6 (write single register)
-          modbusStartAddress = 1
-          modbusLength = 3
-          datatype = 0
-          pollMsec = 100
-          plcType = RKamp
Because function code 6 is a write operation and because you have set pollMsec to a non-zero value the Modbus driver will first try to do an initial read of those registers using Modbus function 3 (read holding registers).
I suspect your problem is that you have not configured your Modbus simulator to support Modbus function 3 on those addresses.  There are 2 solutions to avoid that error message:
1.      Configure your simulator to support Modbus function 3 on those addresses
2.      Set pollMsec=0 in that drvModbusAsynConfigure command.
From: Tech-talk <[email protected]> on behalf of Wang, SuYin Grass via Tech-talk <[email protected]>
Sent: Thursday, July 1, 2021 10:21 AM
To: [email protected]
Subject: Question about "error calling writeRead" in modbus
Hi Everyone,
I have a question about asyn and modbus
I am running the soft IOC with a modbus simulator. Since I don't have permission on the workstation running simulator, I am using port 4502 instead 502
The IOC and simulator run fine, according to "trace_debug.txt" the reading and writing are reasonable.
It is just when the IOC boot up, there is always one line of error about "error calling writeRead" right after the drvModbusAsynConfigure for the writing function.
Any advice?
Thanks!
Grass
===========st.cmd=================================================
##this line is for simulator; this is Modbus TCP, but for this device we must set noProcessEos to 0
drvAsynIPPortConfigure("RKamp","xxx.xxx.xxx.xxx:4502",0,0,0)
modbusInterposeConfig("RKamp",0,2000,0)
drvModbusAsynConfigure("UINT32",    "RKamp",1,3,1,70,0,2000,"RKamp")
drvModbusAsynConfigure("INT32",     "RKamp",1,3,1,70,4,2000,"RKamp")
========the  trace_debug.txt===================
2021/06/30 18:21:30.574 xxx.xxx.xxx.xxx:4502 write 12
00 09 00 00 00 06 01 03 00 01 00 46
2021/06/30 18:21:30.575 xxx.xxx.xxx.xxx:4502 read 149
00 09 00 00 00 8f 01 03 8c 00 00 00 00 00 00 00 00 00 00 00
01 00 00 00 00 00 00 00 c9 00 ca 00 cb 00 00 00 00 00 00 00
0b 00 0b 00 0b 00 0b 00 0b 00 0b 00 0b 00 0b 00 0b 00 0b 00
0b 00 0b 00 16 00 16 00 16 00 16 00 16 00 16 00 16 00 32 00
2021/06/30 18:21:31.511 xxx.xxx.xxx.xxx:4502 write 12
00 0a 00 00 00 06 01 03 00 01 00 01
2021/06/30 18:21:31.512 xxx.xxx.xxx.xxx:4502 read 11
00 0a 00 00 00 05 01 03 02 00 00
2021/06/30 18:21:31.513xxx.xxx.xxx.xxx:4502 write 12
00 0b 00 00 00 06 01 06 00 01 00 01
2021/06/30 18:21:31.513 xxx.xxx.xxx.xxx:4502 read 12
Re: Question about "error calling writeRead" in modbus Mark Rivers via Tech-talk
Question about "error calling writeRead" in modbus Wang, SuYin Grass via Tech-talk
Prev: Re: Question about "error calling writeRead" in modbus Mark Rivers via Tech-talk
Next: Re: Question about "error calling writeRead" in modbus Mark Rivers via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026