1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026
Subject: Re: Failed connection using e3-s7plc to Siemens S7-1500
From: Miklós Boros via Tech-talk <[email protected]>
To: Mateusz Nabywaniec <[email protected]>, "[email protected]" <[email protected]>, Dominik Domagała <[email protected]>, "[email protected]" <[email protected]>, Timo Korhonen <[email protected]>
Date: Thu, 28 Oct 2021 15:31:55 +0000
Dear Mateusz,
Usually the issue is in the PLC.
You can doublecheck it by telnet into the PLC IP on port 2000.
for example: telnet 192.168.0.100 2000
You should get an active connection and if you send something you should see it too in a binary form.
If you can't telnet it means the PLC does not open the port 2000 properly.
Check if you use the proper HW_ID for T_CON. X1 is usually 64 and X2 is 72.
The send block also needs a constant trigger.
Tell me if you need an example.
Cheers,
Miklós Boros
Feladó: Tech-talk <[email protected]>, Mateusz Nabywaniec via Tech-talk <[email protected]> nevében
Elküldve: 2021. október 28., csütörtök 15:42
Címzett: [email protected]; Dominik  Domagała; [email protected]; [email protected]
Tárgy: Failed connection using e3-s7plc to Siemens S7-1500
Hello,
Together with @Dominik  Domagała we are trying to connect with Siemens S7-1500 using e3-s7plc module (https://gitlab.esss.lu.se/e3/wrappers/communication/e3-s7plc) created by ESS.
We have EPICS 7.0.5 installed on CentOS 7 VM as well as E3 modules.
Here is our start cmd based on : http://epics.web.psi.ch/software/s7plc/YHLhtcPLCa.pdf
require s7plc
epicsEnvSet("TOP","$(E3_CMD_TOP)/..")
s7plcConfigure cpu1,192.168.0.1,2000,240,240,1,2000,500
dbLoadRecords ("$(TOP)/db/records.db")
iocInit
Unfortunetely we have the error:
`s7plcConnect cpu1: background connect to 192.168.0.1:2000 failed: Connection refused.`
The firewall on VM and host side are disabled.
PLC Program configuration:
-Full Access.
-Enabled PUT/GET connections.
-Data blocks ale with full access , not optimized
-TCON in stand by with status BUSY
TCON configuration:
-Active Est. ON
-Unspecified partner with IP address (E3 address)
-TCP connection type by port 2000.
When we are starting E3 server we are getting information as below
10/28/21 08:44:00.763 s7plcConnect cpu1: background connect to 192.168.0.1:2000 failed: Connection refused
We can’t get why E3-s7plc does not work on our machine. Does anybody had similar issue or successfully connected using e3-s7plc with Siemens S7-1513-1?
Thanks in advance,
Mateusz Nabywaniec
S2Innovation, Cracow, Poland
ODP: Failed connection using e3-s7plc to Siemens S7-1500 Mateusz Nabywaniec via Tech-talk
Prev: Re: [EXTERNAL] Failed connection using e3-s7plc to Siemens S7-1500 Hartman, Steven via Tech-talk
Next: Re: IOC in Docker not responding to caget from another host Pete Jemian via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026
Next: ODP: Failed connection using e3-s7plc to Siemens S7-1500 Mateusz Nabywaniec via Tech-talk