1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025
Subject: Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
From: "Wang, SuYin Grass via Tech-talk" <tech-talk at aps.anl.gov>
To: "tech-talk at aps.anl.gov" <tech-talk at aps.anl.gov>, "Rivers, Mark L." <rivers at cars.uchicago.edu>
Date: Fri, 20 May 2022 15:12:51 +0000
Hi Mark,
We are using 7.0.6.1 with MVME3100, TVME200 and IP408, and we have been running with this for a few month but didn't see any VME bus error.
The TVME200 is using A24. Our setting is listed below.
ipacAddTVME200("602680")
value = 0 = 0x0
## Print out report of IP modules
ipacReport(2)
  IP Carrier  0: TEWS TVME200, 4 slots
    C0 S0 : No Module - Int0: level 4    Int1: level 5
      ID = 0xd2006080, I/O = 0xd2006000, Mem = 0xd0800000
    C0 S1 : No Module - Int0: level 2    Int1: level 1
      ID = 0xd2006180, I/O = 0xd2006100, Mem = 0xd0900000
    C0 S2 : 0xa3/0x03 - Int0: level 4    Int1: level 5
      ID = 0xd2006280, I/O = 0xd2006200, Mem = 0xd0a00000
    C0 S3 : No Module - Int0: level 2    Int1: level 1
      ID = 0xd2006380, I/O = 0xd2006300, Mem = 0xd0b00000
value = 0 = 0x0
Grass
From: Tech-talk <tech-talk-bounces at aps.anl.gov> on behalf of Mark Rivers via Tech-talk <tech-talk at aps.anl.gov>
Sent: Friday, May 20, 2022 8:06 AM
To: tech-talk at aps.anl.gov <tech-talk at aps.anl.gov>
Subject: RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
I have now tested using base 7.0.5 rather than 7.0.6.1.  The problem does not occur with base 7.0.5.  I have switched back and forth twice, being certain to completely clean and rebuild all synApps modules and my own application first when doing so.
I am running 7 VME crates with vxWorks 6.9.4.1.  I am logging the IOC output for each of them with procServ.
I was running base 7.0.6.1 between about Wed May 18 15:00 and Thu May 19 15:00.  During that time I observed the following VME bus errors.
/home/epics/logs/13BMD.log:[Wed May 18 15:46:12 2022] VME Bus Error accessing A16: 0x3316
/home/epics/logs/13IDE.log:[Wed May 18 16:07:12 2022] VME Bus Error accessing A16: 0x317e
/home/epics/logs/13IDA.log:[Wed May 18 16:50:32 2022] VME Bus Error accessing A16: 0x3146
/home/epics/logs/13IDE.log:[Wed May 18 17:23:08 2022] VME Bus Error accessing A16: 0x317e
/home/epics/logs/13IDC.log:[Wed May 18 18:11:58 2022] VME Bus Error accessing A32: 0xbf57c014
/home/epics/logs/13BMD.log:[Wed May 18 18:12:43 2022] VME Bus Error accessing A16: 0x317e
/home/epics/logs/13BMA.log:[Wed May 18 18:16:04 2022] VME Bus Error accessing A16: 0x3136
/home/epics/logs/13IDE.log:[Wed May 18 18:20:22 2022] VME Bus Error accessing A32: 0xbf140014
/home/epics/logs/13IDA.log:[Wed May 18 20:23:06 2022] VME Bus Error accessing A16: 0x300e
/home/epics/logs/13BMD.log:[Thu May 19 11:13:34 2022] VME Bus Error accessing A16: 0x3046
/home/epics/logs/13IDC.log:[Thu May 19 12:03:54 2022] VME Bus Error accessing A32: 0xbf7db01c
/home/epics/logs/13BMD.log:[Thu May 19 12:42:30 2022] VME Bus Error accessing A32: 0xbffcac70
/home/epics/logs/13IDA.log:[Thu May 19 12:44:11 2022] VME Bus Error accessing A16: 0x300e
/home/epics/logs/13IDC.log:[Thu May 19 13:01:55 2022] VME Bus Error accessing A32: 0xbf554014
/home/epics/logs/13IDE.log:[Thu May 19 13:11:16 2022] VME Bus Error accessing A32: 0xbf2e001c
/home/epics/logs/13IDE.log:[Thu May 19 13:11:45 2022] VME Bus Error accessing A16: 0x315e
/home/epics/logs/13IDD.log:[Thu May 19 13:18:03 2022] VME Bus Error accessing A32: 0xbf390018
/home/epics/logs/13IDE.log:[Thu May 19 13:25:25 2022] VME Bus Error accessing A32: 0xbf140014
/home/epics/logs/13BMD.log:[Thu May 19 13:40:38 2022] VME Bus Error accessing A16: 0x317e
/home/epics/logs/13IDE.log:[Thu May 19 14:09:56 2022] VME Bus Error accessing A32: 0xbf140014
So there were about 20 errors in 24 hours.  I did reboot the IOCs a few times during this period, and the probability of an error is definitely higher in the few minutes after a reboot, perhaps as OPI displays reconnect their CA links.
At about Thu May 19 15:00 I switched to base 7.0.5 and ran for 3 hours, until about 18:00.  There were no bus errors.
At Thu May 19 17:45 I switched back to 7.0.6.1 for about 3 hours until 21:00.  I observed the following errors during this time.
/home/epics/logs/13IDE.log:[Thu May 19 17:58:59 2022] VME Bus Error accessing A32: 0xbf2e001c
/home/epics/logs/13BMD.log:[Thu May 19 18:09:48 2022] VME Bus Error accessing A16: 0x315e
/home/epics/logs/13IDD.log:[Thu May 19 19:16:00 2022] VME Bus Error accessing A16: 0x3206
At about Thu May 19 21:00 I switched to base 7.0.5 again.  That was 11 hours ago, and there have been no bus errors in that time.
It is clear that my systems fail with 7.0.6.1 and work fine with 7.0.5, all other software being identical. It is certainly possible that 7.0.6.1 is exposing a problem with the other software which 7.0.5 does not.  I cannot afford to experiment or test more with these 7 VME systems, since beam comes back soon.  I do have one other VME crate that can be used for testing.  It is not currently running, so I don’t know if it fails with 7.0.6.1, but I will turn it on today.
Note that prior to this week I had been running base 7.0.4 on these systems for over a year with no issues.  This week I did update to the latest versions of the synApps modules, but I did not change my IOC specific code at all.
Sent: Thursday, May 19, 2022 8:34 AM
To: Johnson, Andrew N. <anj at anl.gov>
Cc: tech-talk at aps.anl.gov
Subject: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
Folks,
I updated my VME crates from base 7.0.4 to 7.0.6.1, and also updated to the latest version of synApps modules. 5 of the 7 crates are now giving VME bus errors within a few minutes of booting.  Since it is happening on 5 crates it is highly unlikely to be a hardware problem.
The errors are all for a small set of addresses:
A16: 0x300e, 0x3136, 0x3172
These are in the address space of the first Industry Pack module on a VIPC616_01 or TVME200 IP carrier card
A32:  0xbf57c014
I am not sure what device this is.  The Joerger scalars are configured to start at address  0xB0000000, but I don’t think they use that much memory space.
The task generating the error is always “CAS-event”.
These are the errors:
13IDA crate:
[Wed May 18 20:23:06 2022] machine check
[Wed May 18 20:23:06 2022] Exception next instruction address: 0x03604600
[Wed May 18 20:23:06 2022] Machine Status Register: 0x0008b032
[Wed May 18 20:23:06 2022] Condition Register: 0x42000884
[Wed May 18 20:23:06 2022] Task: 0x55d8aa0 "CAS-event"
[Wed May 18 20:23:06 2022] 0x55d8aa0 (CAS-event): task 0x55d8aa0 has had a failure and has been stopped.
[Wed May 18 20:23:06 2022] 0x55d8aa0 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
[Wed May 18 20:48:19 2022] 0x4d50400 (timerQueue): callbackRequest: cbLow ring buffer full
13BMA crate
[Wed May 18 18:16:04 2022] machine check
[Wed May 18 18:16:04 2022] Exception next instruction address: 0x0141b5b8
[Wed May 18 18:16:04 2022] Machine Status Register: 0x0008b032
[Wed May 18 18:16:04 2022] Condition Register: 0x42000884
[Wed May 18 18:16:04 2022] Task: 0x3545520 "CAS-event"
[Wed May 18 18:16:04 2022] 0x3545520 (CAS-event): task 0x3545520 has had a failure and has been stopped.
[Wed May 18 18:16:04 2022] 0x3545520 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
13IDC crate:
[Wed May 18 18:11:58 2022] machine check
[Wed May 18 18:11:58 2022] Exception next instruction address: 0x013962a0
[Wed May 18 18:11:58 2022] Machine Status Register: 0x0008b032
[Wed May 18 18:11:58 2022] Condition Register: 0x42000884
[Wed May 18 18:11:58 2022] Task: 0x395e4b0 "CAS-event"
[Wed May 18 18:11:58 2022] 0x395e4b0 (CAS-event): task 0x395e4b0 has had a failure and has been stopped.
[Wed May 18 18:11:58 2022] 0x395e4b0 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
13BMD crate:
[Wed May 18 18:12:43 2022] machine check
[Wed May 18 18:12:43 2022] Exception next instruction address: 0x01395e40
[Wed May 18 18:12:43 2022] Machine Status Register: 0x0008b032
[Wed May 18 18:12:44 2022] Condition Register: 0x48000884
[Wed May 18 18:12:44 2022] Task: 0x3c73ae0 "CAS-event"
[Wed May 18 18:12:44 2022] 0x3c73ae0 (CAS-event): task 0x3c73ae0 has had a failure and has been stopped.
[Wed May 18 18:12:44 2022] 0x3c73ae0 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
13IDE crate:
[Wed May 18 16:07:12 2022] machine check
[Wed May 18 16:07:12 2022] Exception next instruction address: 0x01395c20
[Wed May 18 16:07:12 2022] Machine Status Register: 0x0008b032
[Wed May 18 16:07:12 2022] Condition Register: 0x48000884
[Wed May 18 16:07:12 2022] Task: 0x3a13c60 "CAS-event"
[Wed May 18 16:07:12 2022] 0x3a13c60 (CAS-event): task 0x3a13c60 has had a failure and has been stopped.
[Wed May 18 16:07:12 2022] 0x3a13c60 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
[Wed May 18 18:20:22 2022] machine check
[Wed May 18 18:20:22 2022] Exception next instruction address: 0x013959c0
[Wed May 18 18:20:22 2022] Machine Status Register: 0x0008b032
[Wed May 18 18:20:22 2022] Condition Register: 0x48000884
[Wed May 18 18:20:22 2022] Task: 0x3a2d780 "CAS-event"
[Wed May 18 18:20:22 2022] 0x3a2d780 (CAS-event): task 0x3a2d780 has had a failure and has been stopped.
[Wed May 18 18:20:23 2022] 0x3a2d780 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
This is the result of “tt” and “ti” on a couple of the crashed tasks:
ioc13ida> tt 0x55d8aa0
0x0012489c vxTaskEntry  +0x48 : epicsThreadEntry ()
0x036a6afc epicsThreadEntry+0x80 : 0x03604e20 ()
0x036050f8 db_start_events+0x458: db_delete_field_log ()
value = 0 = 0x0
ioc13ida> ti 0x55d8aa0
  NAME         ENTRY       TID    PRI   STATUS      PC       SP     ERRNO  DELAY
CAS-event   epicsThread>  55d8aa0 139 STOP+I      3604600  55d89b0       0     0
full task name : CAS-event
task entry     : epicsThreadEntry
process        : kernel
options        : 0x1009001
VX_SUPERVISOR_MODE  VX_DEALLOC_TCB      VX_FP_TASK          VX_DEALLOC_EXC_STACK
STACK      BASE     END       SP      SIZE    HIGH   MARGIN
execution  55d8aa0  55d5bc0  55d89b0   12000    3568    8432
exception  55d9bf0  55d8d80             3696    1344    2352
VxWorks Events
Events Pended on    : Not Pended
Received Events     : 0x0
Options             : N/A
r0         = 0x40050000   sp         = 0x055d89b0   r2         = 0x002f1ac0
r3         = 0x04e56c70   r4         = 0x05293e20   r5         = 0x00000001
r6         = 0x00000001   r7         = 0x00000000   r8         = 0x00000000
r9         = 0x0368a8b8   r10        = 0x00000000   r11        = 0x055d8920
r12        = 0x22000884   r13        = 0x00321e60   r14        = 0x036a5e98
r15        = 0x03fb9a44   r16        = 0x035ec8c0   r17        = 0x03fb99fc
r18        = 0x00000000   r19        = 0x036a3f3c   r20        = 0x03fb99bc
r21        = 0x0360461c   r22        = 0x00000001   r23        = 0x036045b4
r24        = 0x04341544   r25        = 0x0369d438   r26        = 0x0369d698
r27        = 0x05156b28   r28        = 0x03639dc8   r29        = 0x05b15c98
r30        = 0x05293e20   r31        = 0x05293e20   msr        = 0x0008b032
lr         = 0x036050f8   ctr        = 0x036045b4   pc         = 0x03604600
cr         = 0x42000884   xer        = 0x00000000   pgTblPtr   = 0x02310000
scSrTblPtr = 0x0230fe74   srTblPtr   = 0x0230fe74
fpcsr  =        0
fr0    =       -1   fr1    =      NaN   fr2    =      NaN   fr3    =      NaN
fr4    =      NaN   fr5    =      NaN   fr6    =      NaN   fr7    =      NaN
fr8    =      NaN   fr9    =      NaN   fr10   =      NaN   fr11   =      NaN
fr12   =      NaN   fr13   =      NaN   fr14   =      NaN   fr15   =      NaN
fr16   =      NaN   fr17   =      NaN   fr18   =      NaN   fr19   =      NaN
fr20   =      NaN   fr21   =      NaN   fr22   =      NaN   fr23   =      NaN
fr24   =      NaN   fr25   =      NaN   fr26   =      NaN   fr27   =      NaN
fr28   =      NaN   fr29   =      NaN   fr30   =      NaN   fr31   =      NaN
machine check
Exception next instruction address: 0xva0lue = 3604600
Machine Status Register: 0x00008b032
Condition Register: 0x = 420008840x
ioc13ide> tt 0x3a2d780
0x00121e7c vxTaskEntry  +0x48 : epicsThreadEntry ()
0x01437ebc epicsThreadEntry+0x80 : 0x013961e0 ()
0x013964b8 db_start_events+0x458: db_delete_field_log ()
value = 0 = 0x0
ioc13ide> ti 0x3a2d780
CAS-event   epicsThread>  3a2d780 133 STOP+I      13959c0  3a2d690       0     0
process        : kernel
options        : 0x1009001
execution  3a2d780  3a2a8a0  3a2d690   12000    2800    9200
exception  3a2e8d0  3a2da60             3696    1344    2352
VxWorks Events
Options             : N/A
r0         = 0x40050000   sp         = 0x03a2d690   r2         = 0x002e5010
r3         = 0x02dc8530   r4         = 0x0366ac00   r5         = 0x00000001
r6         = 0x00000001   r7         = 0x00000000   r8         = 0x00000002
r9         = 0x0141bc78   r10        = 0x00000000   r11        = 0x03a2d600
r12        = 0x28000884   r13        = 0x00313850   r14        = 0x01437258
r15        = 0x01d4ae04   r16        = 0x0137dc80   r17        = 0x01d4adbc
r18        = 0x00000000   r19        = 0x014352fc   r20        = 0x01d4ad7c
r21        = 0x013959dc   r22        = 0x00000001   r23        = 0x01395974
r24        = 0x020d2904   r25        = 0x0142e7f8   r26        = 0x0142ea58
r27        = 0x0351b4c8   r28        = 0x013cb188   r29        = 0x03a98e70
r30        = 0x0366ac00   r31        = 0x0366ac00   msr        = 0x0008b032
lr         = 0x013964b8   ctr        = 0x01395974   pc         = 0x013959c0
cr         = 0x48000884   xer        = 0x00000000   pgTblPtr   = 0x00af7000
scSrTblPtr = 0x00af65c4   srTblPtr   = 0x00af65c4
fpcsr  =        0
fr0    = -7.62951e-05   fr1    =      NaN   fr2    =      NaN   fr3    =      NaN
machine checkvalue =
Exception next instruction address: 0x0013959c0
Machine Status Register: 0x = 0008b032
Condition Register: 0x048000884x
Any ideas?
Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
Prev: RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
Next: Re: Modbus for Huber Pilotone Florian Feldbauer via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025
Next: RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
ANJ, 14 Sep 2022 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions ·
