1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
Subject: RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
To: Till Straumann <[email protected]>
Date: Tue, 7 Jun 2022 20:39:12 +0000
Hi Till,
I have checked out tag 85822f3 and only changed configure/CONFIG_SITE to build for vxWorks.
I ran the test that uses the IPAC hardware and got this crash after about 13 minutes.  This time it crashed with an A16 address error, in the address space for the IP330 module.  The crash is in db_delete_field_log, the same as the crash you analyzed.
iocexample>
VME Bus Error accessing A16: 0x345e
machine check
Exception next instruction address: 0x032a0fe0
Machine Status Register: 0x0008b032
Condition Register: 0x42000884
Task: 0x3570090 "CAS-event"
0x3570090 (CAS-event): task 0x3570090 has had a failure and has been stopped.
0x3570090 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
This is the stack trace:
iocexample> tt 0x3570090
0x0012489c vxTaskEntry  +0x48 : epicsThreadEntry ()
0x0334501c epicsThreadEntry+0x80 : 0x032a17f0 ()
0x032a1acc db_start_events+0x450: db_delete_field_log ()
value = 0 = 0x0
This is the register dump:
iocexample> ti 0x3570090
  NAME         ENTRY       TID    PRI   STATUS      PC       SP     ERRNO  DELAY
CAS-event   epicsThread>  3570090 133 STOP+I      32a0fe0  356ffa0       0     0
full task name : CAS-event
task entry     : epicsThreadEntry
process        : kernel
options        : 0x1009001
VX_SUPERVISOR_MODE  VX_DEALLOC_TCB      VX_FP_TASK          VX_DEALLOC_EXC_STACK
STACK      BASE     END       SP      SIZE    HIGH   MARGIN
execution  3570090  356d1b0  356ffa0   12000    2800    9200
exception  26f7ac0  26f6c50             3696    1344    2352
VxWorks Events
Events Pended on    : Not Pended
Received Events     : 0x0
Options             : N/A
r0         = 0x40000000   sp         = 0x0356ffa0   r2         = 0x002f1ac0
r3         = 0x03492cc0   r4         = 0x0356ab90   r5         = 0x00000001
r6         = 0x00000001   r7         = 0x00000000   r8         = 0x000a0008
r9         = 0x03326a90   r10        = 0x00000000   r11        = 0x0356ff10
r12        = 0x20000884   r13        = 0x00321e60   r14        = 0x033b6098
r15        = 0x03373c64   r16        = 0x03289478   r17        = 0x033424f0
r18        = 0x03373bdc   r19        = 0x03373c1c   r20        = 0x032a0ff8
r21        = 0x032a0f90   r22        = 0x00000000   r23        = 0x00000001
r24        = 0x033b609c   r25        = 0x03339340   r26        = 0x033390e0
r27        = 0x03442b90   r28        = 0x0356c870   r29        = 0x03556108
r30        = 0x032dad44   r31        = 0x0356ab90   msr        = 0x0008b032
lr         = 0x032a1acc   ctr        = 0x03326a90   pc         = 0x032a0fe0
cr         = 0x42000884   xer        = 0x00000000   pgTblPtr   = 0x02310000
scSrTblPtr = 0x0230fe74   srTblPtr   = 0x0230fe74
fpcsr  =        0
fr0    = -0.85893   fr1    =      NaN   fr2    =      NaN   fr3    =      NaN
fr4    =      NaN   fr5    =      NaN   fr6    =      NaN   fr7    =      NaN
fr8    =      NaN   fr9    =      NaN   fr10   =      NaN   fr11   =      NaN
fr12   =      NaN   fr13   =      NaN   fr14   =      NaN   fr15   =      NaN
fr16   =      NaN   fr17   =      NaN   fr18   =      NaN   fr19   =      NaN
fr20   =      NaN   fr21   =      NaN   fr22   =      NaN   fr23   =      NaN
fr24   =      NaN   fr25   =      NaN   fr26   =      NaN   fr27   =      NaN
fr28   =      NaN   fr29   =      NaN   fr30   =      NaN   fr31   =      NaN
machine checkvalue =
Exception next instruction address: 0x0032a0fe0
Machine Status Register: 0x = 0008b032
Condition Register: 0x420008840x
This is the memory dump of the address in R31:
iocexample> d 0x0356ab90
NOTE: memory values are displayed in hexadecimal.
0x0356ab90:  4000 0000 3d01 163d 3848 818a 0000 0000  *@...=..=8H......*
0x0356aba0:  000a 0008 0000 0001 bfeb 7c5b 7c5b 7c5b  *..........|[|[|[*
0x0356abb0:  0000 0000 0000 0000 0356 ac80 3d01 163d  *.........V..=..=*
0x0356abc0:  3848 818a 0000 0000 000a 0008 0000 0001  *8H..............*
0x0356abd0:  bfeb 405b 405b 405b 0000 0000 0000 0000  *..@[@[@[........*
0x0356abe0:  0356 a988 3d01 163d 3848 818a 0000 0000  *.V..=..=8H......*
0x0356abf0:  000a 0008 0000 0001 bfeb 2edb 2edb 2edb  *................*
0x0356ac00:  0000 0000 0000 0000 0356 a640 3d01 163d  *.........V.@=..=*
0x0356ac10:  3848 818a 0000 0000 000a 0008 0000 0001  *8H..............*
0x0356ac20:  bfeb 635b 635b 635b 0000 0000 0000 0000  *..c[c[c[........*
0x0356ac30:  0356 a5f0 3d01 163d 3848 818a 0000 0000  *.V..=..=8H......*
0x0356ac40:  000a 0008 0000 0001 bfeb 4f5b 4f5b 4f5b  *..........O[O[O[*
0x0356ac50:  0000 0000 0000 0000 0356 a618 3d01 163d  *.........V..=..=*
0x0356ac60:  3848 818a 0000 0000 000a 0008 0000 0001  *8H..............*
0x0356ac70:  bfeb 60db 60db 60db 0000 0000 0000 0000  *..`.`.`.........*
0x0356ac80:  0356 ab18 3d01 163d 3848 818a 0000 0000  *.V..=..=8H......*
value = 0 = 0x0
iocexample>
Another time I tested the same version it failed with an A32 address error in freeListFree called from db_delete_field_log
VME Bus Error accessing A32: 0xbfe26ed0
machine check
Exception next instruction address: 0x03326a90
Condition Register: 0x40000884
Task: 0x26fccd0 "CAS-event"
0x26fccd0 (CAS-event): task 0x26fccd0 has had a failure and has been stopped.
0x26fccd0 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
iocexample> tt 0x26fccd0
0x032a0fe4 db_delete_field_log+0x54 : freeListFree ()
value = 0 = 0x0
iocexample> ti
CAS-event   epicsThread>  26fccd0 133 STOP+I      3326a90  26fcbe0       0     0
process        : kernel
options        : 0x1009001
execution  26fccd0  26f9df0  26fcbe0   12000    2800    9200
exception  3444540  34436d0             3696    1344    2352
VxWorks Events
Options             : N/A
r0         = 0x40000000   sp         = 0x026fcbe0   r2         = 0x002f1ac0
r3         = 0x03492ce0   r4         = 0x03575a90   r5         = 0x00000001
r6         = 0x00000001   r7         = 0x00000001   r8         = 0x0354a4d0
r9         = 0x03326a90   r10        = 0x00000028   r11        = 0x026fcb50
r12        = 0x22000884   r13        = 0x00321e60   r14        = 0x033b6098
r27        = 0x03443078   r28        = 0x03443078   r29        = 0x03561a80
r30        = 0x032dad44   r31        = 0x03575a90   msr        = 0x0008b032
lr         = 0x032a0fe4   ctr        = 0x03326a90   pc         = 0x03326a90
cr         = 0x40000884   xer        = 0x00000000   pgTblPtr   = 0x02310000
fpcsr  =        0
fr0    = -0.576028   fr1    =      NaN   fr2    =      NaN   fr3    =      NaN
Exception next instruction address: 0x003326a90
Condition Register: 0x0x40000884
iocexample> l  0x003326a90
                        freeListFree:
0x3326a90  9421fff0    stwu        r1,-16(r1)
0x3326a94  7c0802a6    mfspr       r0,LR
0x3326a98  3d200334    lis         r9,0x334 # 820
0x3326a9c  392990e0    addi        r9,r9,0x90e0 # -28448
0x3326aa0  7d2903a6    mtspr       CTR,r9
0x3326aa4  90010014    stw         r0,20(r1)
0x3326aa8  93c10008    stw         r30,8(r1)
0x3326aac  7c9e2378    or          r30,r4,r4
0x3326ab0  93e1000c    stw         r31,12(r1)
0x3326ab4  7c7f1b78    or          r31,r3,r3
value = 0 = 0x0
I hope this helps.
I will work on the quick test program you sent next.
From: Tech-talk <[email protected]> On Behalf Of Till Straumann via Tech-talk
Sent: Thursday, June 2, 2022 11:34 AM
To: [email protected]
Subject: Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
On 6/2/22 16:21, Mark Rivers via Tech-talk wrote:
The problem can be explained if pfl->type is occasionally set to dbfl_type_ref when it should not be. In that case the union will contain data, perhaps floats from the ADC as Michael suggested. Because the ->type is wrong the value is being treated as an address, which leads to the A32 bus address error.
No - it actually can't explained by this. In the scenario you describe
there would be a read access to pfl->u.r.dtor when the function call
is executed. If that were the case then we should see the fault address
in the PC (and in 'r0' as well as in 'ctr', see analysis below).
In the disassembly which I quote here (comments apply
to preceding instructions):
00000034 <db_delete_field_log>:
    34:       94 21 ff f0     stwu    r1,-16(r1)
    38:       7c 08 02 a6     mflr    r0
    3c:       93 e1 00 0c     stw     r31,12(r1)
    40:       7c 7f 1b 79     mr.     r31,r3
copy 'pfl' arg (passed in r3) into r31 and set condition-code bits
    44:       90 01 00 14     stw     r0,20(r1)
    48:       41 82 00 40     beq     88 <db_delete_field_log+0x54>
if ( pfl == NULL ) goto cleanup/leave
    4c:       80 1f 00 00     lwz     r0,0(r31)
load pfl->type into 'r0'
    50:       2f 80 00 00     cmpwi   cr7,r0,0
test most-significant bit (this is the 'type' 1-bit bitfield)
    54:       40 9c 00 18     bge     cr7,6c <db_delete_field_log+0x38>
if type is 0 (*not* dbfl_ref) then skip the 'dtor' call and jump to address 0x6c
    58:       80 1f 00 18     lwz     r0,24(r31)
we get here if pfl->type == dbfl_type_ref and this instruction
loads pfl->u.r.dtor into register r0
(note that this is still a valid access even if r0 now contains a bad address)
****** r0 at this point holds the 'dtor' address ******
    5c:       2f 80 00 00     cmpwi   cr7,r0,0
comparison: pfl->u.r.dtor == 0
    60:       41 9e 00 0c     beq     cr7,6c <db_delete_field_log+0x38>
get here if pfl->u.r.dtor is NOT NULL
    64:       7c 09 03 a6     mtctr   r0
copy r0 to counter register
    68:       4e 80 04 21     bctrl
***** jump to the 'dtor' routine
***** this jump would cause a bus error
***** HOWEVER: the faulting address would still be in 'r0' (and 'ctr')
*****          and we would crash *here* not a few lines below
    6c:       3d 20 00 00     lis     r9,0
    70:       7f e4 fb 78     mr      r4,r31
copy r31 into r4, both hold 'pfl'
    74:       80 69 00 00     lwz     r3,0(r9)
load 'dbevFieldLogFreeList' into r3
    78:       3d 20 00 00     lis     r9,0
upper 16-bit of 'freeListFree' into r9
    7c:       39 29 00 00     addi    r9,r9,0
merge lower 16-bit of 'freeListFree' into r9
    80:       7d 29 03 a6     mtctr   r9
copy r9 into 'ctr'
    84:       4e 80 04 21     bctrl
***** OBSERVED EXCEPTION happens during execution of this jump
    88:       80 01 00 14     lwz     r0,20(r1)
    8c:       83 e1 00 0c     lwz     r31,12(r1)
    90:       38 21 00 10     addi    r1,r1,16
    94:       7c 08 03 a6     mtlr    r0
    98:       4e 80 00 20     blr
Note that we see
r0:  0x40000000
ctr: 0x03326a90
pc:  0x03326a90 (next instruction address)
=> if the fault were caused by loading an instruction from *pfl->u.r.dtor then
   pc and ctr should hold the bad address.
The register context is actually consistent with
 pfl->type == dbfl_type_val
i.e., from 0x54 we would jump to 0x6c with r0 still holding the 'type' and 'ctx' bit-fields.
Here the call to 'freeListFree()' is prepared. Note that nothing looks out of order:
 r9 == ctr == pc == 0x03326a90 = freeListFree
 r31 == r4 =='pfl'
 r0 == 0x40000000
Note how the type (msbit) is '0' and the 'ctx' is 1 (dbfl_context_event).
In conclusion: the register context gives no indication that anything went wrong.
In order to gather more data I would recommend to also dump the memory at 'pfl',
i.e., next time please post:
 - register dump
 - stack trace
 - other info you have provided in the past
 - memory (~100bytes should suffice) from the location reported in R31
If possible please always work with the 85822f305 commit so that we stay on the same page...
Cheers
- Till
Sent from my iPhone
On Jun 1, 2022, at 11:07 PM, Mark Rivers via Tech-talk <[email protected]> wrote:
We need to explain why adding 2 lines of code to examine the contents of pfl eliminates the failures completely.
It’s like a new type of quantum computer - making an observation changes the outcome!
Sent from my iPhone
On Jun 1, 2022, at 10:24 PM, Michael Davidsaver <[email protected]> wrote:
On 6/1/22 14:50, Mark Rivers wrote:
I checked out R7.0.6.1 and made the following change to dbEvent.c  It checks whether pfl or pfl->u.r.dtor are in the VME A32 address space.  If they are it prints an error and returns.
So, these addresses appear in pfl->u.r.dtor or eg. pfl->u.v.field.dbf_float
My question is then which part(s) of the db_field_log struct have incorrect values?
(eg. "\xbf\x3e\x00\x1e" as float32 is -0.74)
One straightforward, though a bit tedious, think to do would be to print a
dump of the contents of the db_field_log.  eg. I'd be interested to know
if db_field_log::time appears valid.
After making that change then one time when I started the IOC I got these messages right after iocInit, which is not when it usually fails.
This makes me wonder if these "addresses" are eg. somehow valid ADC values,
which just happen to track through the VME window sometimes.  Though if you've
only loading soft records, I don't see how this could be.
Further, I still don't see how these values aren't appearing in the register dump.
I don't think PPC has any instructions which do a double indirection.
Another odd ball idea which occurs to me is that maybe the compiler is mishandling
the db_field_log::type bit field.  The dbEvent.o which you send to Till and I has:
If I read things correctly, I think this is meant to correspond to
'pfl->u.r.type==dbfl_type_val==0", however it is testing the whole word, and would
mis-trigger because 'pfl->u.r.ctx == dbfl_context_event == 1` for a monitor update.
When I look at the result of a local RTEMS build, I think the corresponding is:
 8:   89 24 00 00     lbz     r9,0(r4)
 c:   71 29 00 80     andi.   r9,r9,128
Which is testing the high bit as it should.
For completeness.  Disassembly of db_delete_field_log() from dbEvent.o.
Note that this is object code, with incomplete relocations.
    98:       4e 80 00 20     blr
From my local build for RTEMS-mvme3100
void db_delete_field_log (db_field_log *pfl)
  if (pfl) {
 0:   7c 64 1b 79     mr.     r4,r3
 4:   4d 82 00 20     beqlr
      /* Free field if reference type field log and dtor is set */
      if (pfl->type == dbfl_type_ref && pfl->u.r.dtor) pfl->u.r.dtor(pfl);
10:   40 82 00 10     bne     20 <db_delete_field_log+0x20>
      /* Free the field log chunk */
      freeListFree(dbevFieldLogFreeList, pfl);
14:   3d 20 00 00     lis     r9,0
18:   80 69 00 00     lwz     r3,0(r9)
1c:   48 00 00 00     b       1c <db_delete_field_log+0x1c>
20:   81 24 00 50     lwz     r9,80(r4)
24:   2f 89 00 00     cmpwi   cr7,r9,0
28:   41 be ff ec     beq     cr7,14 <db_delete_field_log+0x14>
2c:   94 21 ff f0     stwu    r1,-16(r1)
30:   7c 08 02 a6     mflr    r0
34:   7d 29 03 a6     mtctr   r9
38:   90 01 00 14     stw     r0,20(r1)
3c:   90 81 00 08     stw     r4,8(r1)
40:   4e 80 04 21     bctrl
44:   80 01 00 14     lwz     r0,20(r1)
48:   3d 20 00 00     lis     r9,0
4c:   80 81 00 08     lwz     r4,8(r1)
50:   80 69 00 00     lwz     r3,0(r9)
54:   7c 08 03 a6     mtlr    r0
58:   38 21 00 10     addi    r1,r1,16
5c:   48 00 00 00     b       5c <db_delete_field_log+0x5c>
Re: [EXTERNAL] Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Hartman, Steven via Tech-talk
Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Till Straumann via Tech-talk
Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Michael Davidsaver via Tech-talk
Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
Prev: Re: Building EPICS MOTOR with just a subscription to only the motorNewport module Kevin Peterson via Tech-talk
Next: dbLoadRecords and substitute Knap, Giles (DLSLtd,RAL,LSCI) via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
Prev: Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
Next: Re: [EXTERNAL] Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Hartman, Steven via Tech-talk
