I’m having problems with an epics IOC re-establishing network connections to a PLIZ PLC, after a network cable disconnection, then reconnection 10 minutes or so later. The IOC is running on a Ubuntu 22.04 PC and communicating to the PLC
using modbus interpose layer and asyn over TCP/IP.
After re-connection, the Asyn.CNCT PV repeatedly reports Connect then Disconnect. This can go on for approx. 20 mins before finally the problem resolves itself and the connection remains Connected. During this period of instability, whilst
I can happily ping the PLC, the IOC is unable to read any of its values through modbus. This would make sense if the PLC has closed its socket.
When the issue occurs, I’ve examined the network socket for port 502 (the PLC port) using netstat -at | grep 502. This reports the socket is an a CLOSE_WAIT state. I understand this indicates the PLC has closed its connection, but the socket
is still open at the IOC end. I’m unsure how to get asyn to recognise this situation and resolve it, maybe by closing the socket and establishing a new one?
I had hoped using asynSetOption("$(PORT)", 0, "disconnectOnReadTimeout", "Y"), would resolve the issue but it didn’t.
Other options I’ve tried include:
Adjusting the linuc tcp_keepalive_time from 7200 s (120 mins) to 20 s, using /sbin/sysctl -e net.ipv4.tcp_keepalive_time = 20, but it didn’t help
disabling/enabling asyn
disconnectOnReadTimeout() and moving its position in st.cmd
varying modbusInterposeConfig() read write timeout
enabling/disabling noProcessEos in drvAsynIPPortConfigure()
but the problem remains.
Below is a section of my st.cmd
epicsEnvSet("DEVICE_IP", "109.0.201.1")
epicsEnvSet("DEVICE_PORT", "502")
epicsEnvSet("PORT", "PILZ")
drvAsynIPPortConfigure("$(PORT)","$(DEVICE_IP):$(DEVICE_PORT)",0,0,1) #IP address of simulated plc
modbusInterposeConfig("$(PORT)",0,0,0)
drvModbusAsynConfigure("BI", "$(PORT)", 0, 3, 107, 56, 0, 100, "pilz")
## Load record instances
dbLoadRecords("$(ASYN)/db/asynRecord.db", "P=$(SHORT_NM), R=:Asyn, PORT=$(PORT), ADDR=0, IMAX=20, OMAX=20")
I think the cause of the problem is the PLC closes the socket, but asyn in the IOC is leaving it open. How do I get asyn to recognise the CLOSE_WAIT status of the socket, close it then establishes a new one? I’m wondering if this may be
an issue with modbus interposed in the asyn?
Any help or advice would be much appreciate, thanks.
Kind regards
Paul Richardson