1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024>  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024>  2025  2026
Subject: Re: Streamdevice - record only completes processing every other activation
From: Zimoch Dirk via Tech-talk <[email protected]>
To: "[email protected]" <[email protected]>, "[email protected]" <[email protected]>
Date: Thu, 21 Mar 2024 15:23:13 +0000
Hi Evan,
Here is what happens:
Initially
epics> dbgf _SRAM_TEST:SWEEP_CMD_EXSC
DBF_DOUBLE:         0
epics> dbpf SRAM_TEST:SWEEP_CMD_EXSC 1
DBF_STRING:         "Sweep"
Now the record outputs.
DBF_DOUBLE:         1
DBF_STRING:         "Sweep"
Nothing happens.
DBF_DOUBLE:         0
Because "Transition To Non-zero" does not apply now.
You have
field(INPA, "$(D):SWEEP_CMD_EXSC")
and probably you think SWEEP_CMD_EXSC falls back to 0 after HIGH=0.5 seconds, so
it should work the next time the user writes a 1.
But the output record is still busy waiting for a reply from the hardware.
StreamDevice is asynchronous, thus the trigger record can actually fall back to
0 while the output record is busy waiting. But the output record cannot be
processed again by the fanout while it is busy. Thus it misses the trigger
record going to 0.
Only next time the user writes, A goes to 0. (I actually wonder why.) But now
"Transition To Non-zero" prevents the record from writing.
If I make HIGH much longer, say 5 seconds, it works (if the user waits for 5
seconds between writes) because now the output record is no longer busy when the
trigger falls back to 0.
It may take me a bit longer to give you a working solution. The idea is to do
the "Transition To Non-zero" in an earlier stage, not in the record that does
the asynchronous I/O.
Some other remark:
Record _$(D):SWEEP_CMD_EXSC references field B in a complicated way:
out "fullsweep4 c %(_\$1:SWEEP_CMD_EXSC.B)#x";
You can simply use %(B)#x in this case.
And if the record had
    field(DOPT, "Use OCAL")
    field(OCAL, "B")
you could even simply use %#x.
Of course this does not affect the behavior you see.
Dirk
On Thu, 2024-03-21 at 14:13 +0000, Zimoch Dirk via Tech-talk wrote:
> Hi Evan,
> This is a hard to debug without your device.
> I am a bit surprised about the "\r\0\n" line terminators in your code but if
> that is what the device sends, so may it be.
> BTW: I usually break such long lines for readability:
>     in "\r\0\n\r\0\n"
>        "Chip: 0\r\0\n"
>        "# of Events: %(\$1:EVT_RD_CHIP0)d\r\0\n"
>        "Chip: 1\r\0\n"
>        "# of Events: %(\$1:EVT_RD_CHIP1)d\r\0\n"
>        "Chip: 2\r\0\n"
>        "# of Events: %(\$1:EVT_RD_CHIP2)d\r\0\n"
>        "Chip: 3\r\0\n"
>        "# of Events: %(\$1:EVT_RD_CHIP3)d";
> As far as I know, RPRO goes to 1 when something writes to a record while it is
> still processing (and thus locked). I thought that should make the record
> process again once the current processing has finished.
> To me this looks like the record is waiting for something and thus has not
> finished processing. Probably for 2 seconds (ReadTimeout=2000).
> Have you tried with 'var streamDebug 1'?
> Dirk
> On Wed, 2024-03-20 at 18:11 +0000, Daykin, Evan via Tech-talk wrote:
> > Hi,
> > I have an unusual issue I haven’t seen before. I have a mode selector, activation bo, directed through a fanout (single output with SELL), which finally sends out a read command, like this:
> > record(mbbo, "$(D):MODE_CMD_SWEEP"){
> >     field(ZRST, "Fullsweep")
> >     field(ZRVL, "0")
> >     field(ONST, "Fullsweep4") <- SELECTED
> >     field(ONVL, "1")
> >     field(TWST, "Simulsweep4")
> >     field(TWVL, "2")
> > #User presses this to execute a scan, stays high for 0.5s
> > record(bo, "$(D):SWEEP_CMD_EXSC"){
> >     field(ZNAM, "Idle")
> >     field(ONAM, "Sweep")
> >     field(HIGH, "0.5")
> >     field(VAL, "0")
> >     field(FLNK, "_$(D):SWEEP_EXSC")
> > record(fanout, "_$(D):SWEEP_EXSC"){
> >     field(SELM, "Specified")
> >     field(SELL, "$(D):MODE_CMD_SWEEP")
> >     field(LNK0, "_$(D):SWEEP_CMD_DBG")
> >     field(LNK1, "_$(D):SWEEP_CMD_EXSC") <- SELECTED
> >     field(LNK2, "_$(D):SWEEP_CMD_SIM")
> > record(calcout, "_$(D):SWEEP_CMD_EXSC"){
> >     field(DTYP, "stream")
> >     field(INPB, "$(D):PAT_CSET_SWEEP")
> >     field(CALC, "A")
> >     field(OOPT, "Transition To Non-zero")
> >     field(OUT, "@sram.proto fullsweep4($(D)) $(HOST)")
> > The protocol file entry looks like this:
> > fullsweep4{
> >     ReadTimeout=2000;
> >     InTerminator="\r\0\n\r\0\n>";
> >     in "\r\0\n\r\0\nChip: 0\r\0\n# of Events: %(\$1:EVT_RD_CHIP0)d\r\0\nChip: 1\r\0\n# of Events: %(\$1:EVT_RD_CHIP1)d\r\0\nChip: 2\r\0\n# of Events: %(\$1:EVT_RD_CHIP2)d\r\0\nChip: 3\r\0\n# of Events: %(\$1:EVT_RD_CHIP3)d";
> > it wants a message of the form:
> > Chip: 0
> > # of Events: 131072
> > Chip: 1
> > # of Events: 131072
> > Chip: 2
> > # of Events: 131072
> > Chip: 3
> > # of Events: 131072
> > But, the last record (calcout) _SWEEP_CMD_EXSC only fires every other time I activate the bo SWEEP_CMD_EXSC, and wireshark confirms it’s only sending out the inquiry every other click as well. Setting TPRO shows:
> > epics> ca:daykin@diag-cam: dbProcess of '_SRAM_TEST:SWEEP_CMD_EXSC'
> > cbLow: dbProcess of '_SRAM_TEST:SWEEP_CMD_EXSC' <- Nothing actually happened, nothing in wireshark, readback records don’t update
> > cbLow: dbProcess of Active '_SRAM_TEST:SWEEP_CMD_EXSC' with RPRO=0 <- Record fired correctly, readback records update
> > What does this indicate? What is RPRO doing?
> > Thank you,
> > Evan
Re: Streamdevice - record only completes processing every other activation Zimoch Dirk via Tech-talk
Streamdevice - record only completes processing every other activation Daykin, Evan via Tech-talk
Prev: Re: Converting Archiver Appliance status to EPICS PVs Sky Brewer via Tech-talk
Next: Re: Streamdevice - record only completes processing every other activation Zimoch Dirk via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024>  2025  2026
Prev: RE: Streamdevice - record only completes processing every other activation Daykin, Evan via Tech-talk