1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024>  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024>  2025  2026
Subject: Re: RE: [SPAM] Re: autoConnect could not connect when reading a register by modbus relative addressing
Date: Sat, 23 Nov 2024 15:17:38 +0000
  • For example, if the starting address is 0x6000 and the address of thefarthest register to be read is 0x602C, even though it is quite far, I should at least set the modbusLength to 44(0x2C)+1?
Yes, that is correct.
Sent: Saturday, November 23, 2024 2:09 AM
To: Mark Rivers <[email protected]>
Cc: [email protected] <[email protected]>
Is your suggestion that while using the modbus module, the modbusLength in drvModbusAsynConfigure should be set to at least the number of the registers that are needed, from the first register to the last register? For example, if the starting address is 0x6000 and the address of thefarthest register to be read is 0x602C, even though it is quite far, I should at least set the modbusLength to 44(0x2C)+1?
Best regards,
Zhibang
发件人: "Mark Rivers" <[email protected]>
发送时间: 2024-11-23 07:58:23
收件人: "[email protected]" <[email protected]>
抄送: "[email protected]" <[email protected]>
主题: RE: [SPAM] Re: autoConnect could not connect when reading a register by modbus relative addressing
  • I change the modbusLength to 4 as what is done in motorAMCI. And I continuously read the values of 5 neighbor registers, like:
If you set the length to 4 then you can’t read 5 registers, you can only read 4.  You need to increase the length to at least 5.
This is the first I heard that you are using a Modbus simulator, not the actual motor controller.  Is this correct?
  • The modbus slave simulator shows that the master and slave only communicated once. And the autoConnect issue is reported at the last time.
Looking back at your original message I understand why they only communicated once.  You set the poll time in this command to 0, which means it does not poll.
  • drvModbusAsynConfigure("DM2C_1_1_In_Word", "L0", 1, 3, 24576, 2, 0, 0, "DM2C_stepper")
You need to set a non-zero poll time.  For example, this will poll every 100 ms.
  • drvModbusAsynConfigure("DM2C_1_1_In_Word", "L0", 1, 3, 24576, 2, 0, 100, "DM2C_stepper")
Sent: Friday, November 22, 2024 4:44 PM
Subject: Re: [SPAM] Re: autoConnect could not connect when reading a register by modbus relative addressing
Dear Mark,
Thank you for your response. I can tell when will this issue happen with an example.
> status = pC_->readReg16(0, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
> status = pC_->readReg16(1, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
> status = pC_->readReg16(2, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
> status = pC_->readReg16(3, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
> status = pC_->readReg16(4, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
> readReg16: reg = 0, value= 2020
> readReg16: reg = 1, value= 2021
> readReg16: reg = 2, value= 2022
> readReg16: reg = 3, value= 2023
> 2024/11/23 06:24:07.881 DM2C_1_1_In_Word 4 autoConnect could not connect:
> readReg16: reg = 4, value= 2023
I mean this autoConnect error occurs when I want to send message for the second time.
Best regards,
Zhibang
发送时间: 2024-11-22 23:03:21
收件人: "[email protected]" <[email protected]>, 沈治邦 <[email protected]>
主题: [SPAM] Re: autoConnect could not connect when reading a register by modbus relative addressing
I think I see the problem.
That creates a driver that will use function code 3 to read from register location  24576 (0x6000).  It will read 2 registers (the Modbus length argument), so it will read registers 0x6000 and 0x6001.
・               status = pC_->readReg16(44, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
However, here you are telling it to read relative register 44 (0x2c) which is absolute register 0x602c. That is invalid because you only configured the driver to read 2 registers.  You need to increase the number of registers in the drvModbusAsynConfigure to include all registers you will be accessing.
From: Tech-talk <[email protected]> on behalf of 沈治邦 via Tech-talk <[email protected]>
Sent: Friday, November 22, 2024 4:31 AM
To: [email protected] <[email protected]>
Subject: autoConnect could not connect when reading a register by modbus relative addressing
I am encountering an issue while developing a modbus communication-based motor controller program, similar to the module motorAMCI.
I am attempting to read the values in registers with function code 3 by relative address. For instance, if I want to read the value located in 0x602C, which represents the current position of the motor. I set the starting address to 0x6000 by the command in st.cmd
Then to read the motor position, I called the function in driver.cpp with sentence
24657 is 0x6000 and 44 is 0x2C, then I believe that the value at 0x602c could be accessed.
The definition of the readReg16 is the same with the method ANG1Controller::readReg16()
Consequently, I am unable to retrieve the correct register value, and an error is showed:
2024/11/22 17:57:00.751 DM2C_1_1_In_Word 2 autoConnect could not connect:
Could someone please help me figure out what might be causing this issue?
Thank you!
Best regards,
Shen Zhibang
autoConnect could not connect when reading a register by modbus relative addressing 沈治邦 via Tech-talk
Re: autoConnect could not connect when reading a register by modbus relative addressing Mark Rivers via Tech-talk
Re: [SPAM] Re: autoConnect could not connect when reading a register by modbus relative addressing Zhibang Shen via Tech-talk
RE: [SPAM] Re: autoConnect could not connect when reading a register by modbus relative addressing Mark Rivers via Tech-talk
Re: RE: [SPAM] Re: autoConnect could not connect when reading a register by modbus relative addressing Zhibang Shen via Tech-talk
Prev: Re: RE: [SPAM] Re: autoConnect could not connect when reading a register by modbus relative addressing Zhibang Shen via Tech-talk
Next: Re: RE: [SPAM] Re: autoConnect could not connect when reading a register by modbus relative addressing Mark Rivers via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024>  2025  2026
Next: Re: RE: [SPAM] Re: autoConnect could not connect when reading a register by modbus relative addressing Zhibang Shen via Tech-talk