1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>
Subject: Re: eiger2 vacuum sequencing power status
From: "Jemian, Peter R via Tech-talk" <tech-talk at aps.anl.gov>
To: "tech-talk at aps.anl.gov" <tech-talk at aps.anl.gov>, Keith Surrena <ks2339 at cornell.edu>
Date: Wed, 11 Feb 2026 21:09:40 +0000
You need this protection to be available, even if EPICS is not working.  Don't rely on EPICS for machine protection work.
Sent: Wednesday, February 11, 2026 3:08 PM
To: tech-talk at aps.anl.gov; Keith Surrena
To avoid arcing high-voltage ion gauges in the intermediate vacuum region (of a double-crystal monochromator), I used a thermocouple vacuum gauge.  The gauge controller has setpoints for this range.  Each setpoint was connected to a relay contact.  The PLC (outside the vacuum chamber) sensed those contacts and operated a relay to energize when conditions allow.  Being the brutal sort, that relay switched on/off the mains power for the device being protected.
Pete
From: Tech-talk <tech-talk-bounces at aps.anl.gov> on behalf of Keith Surrena via Tech-talk <tech-talk at aps.anl.gov>
Sent: Wednesday, February 11, 2026 2:38 PM
Subject: eiger2 vacuum sequencing power status
We’re working on some PLC control for protecting our eiger2 4M that will live in vacuum and I’m looking for some feedback. Dectris specifies that it must be unpowered while chamber pressure is between 1bar and .01 mbar, so we’re interested in using an IoT relay to disable the power supply remotely. To verify that the detector is off, I was thinking about querying detector state with the State_RBV record. I noticed that so long as the read status rate is set reasonably, this should return “Error” as the state, instead of “Idle”. I could create logic based around these states but I’m worried that I could be missing a different interpretation of the “Error” state that could lead to believing the detector is unpowered when it isn’t. Are there any other records that would be useful for verification?
Keith Surrena
Research Support Specialist
Cornell High Energy Synchrotron Source
RE: eiger2 vacuum sequencing power status Keith Surrena via Tech-talk
Re: eiger2 vacuum sequencing power status Jemian, Peter R via Tech-talk
Prev: Re: eiger2 vacuum sequencing power status Jemian, Peter R via Tech-talk
Next: RE: eiger2 vacuum sequencing power status Keith Surrena via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>