1994  1995  1996  1997  1998  <19992000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  <19992000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: curious OMS58 Problem / Waveform-Size-Limitation
To: "Jens Eden" <[email protected]>, <[email protected]>
Date: Wed, 15 Sep 1999 16:11:52 -0600
> we experienced a strange behaviour of an OMS58 Motor-card.
> If the OMS58-card is jumpered for base address 0xc000, the motor
> suddenly stops, starts again and it needs several retries to reach its
> destination.
> We tried various cards in different crates and this only happens if the
> card has base address 0xc000, even if there are no other cards in the
> crate.
> Anyone an idea, what this could be?
The address 0xc000 sounds suspiciously like the base address for
VXI devices in VME A16. Do you have a VXI device driver or resource
manager installed into your system?
> Another question concerns the maximum message size of CA-messages.
> We use Mark Rivers MCA-Record with the Canberra AIM556 MCA, which is
> based on the Waveform-Record. If I try to read more than 4090 channels
> (~16360 bytes), we get the CA-error "data does not fit in a CA-message".
> In caProto.h MAX_MSG_SIZE is defined with 16384 (16*MAX_UDP).
> Is it safe to define MAX_MSG_SIZE at least to 33*1024, (for CA-Server
> and Client)
> or is there another way to do it?
In theory, you could increase MAX_MSG_SIZE up to a maximum of 65,535 as long
as you are certain that this change has been compiled into _all_
participating
clients and servers. Note that this change to the source code has not been
tested.
I intend to eliminate this 16k byte barrier in the coming months.
Jeff