Liyu, Andrei wrote: I assume you are concerned about performance and thus want to directly access the array.I would like to write to waveform record (long or float type) directly. At first, I can use dbPutField( ...) but it would take much time because I need to change 30% of record's array. At second, I will also assume that your code is not run under a scan task, i.e. it is not part of record or device support or a subroutine connected to a record. Do the following: At initialization: struct dbAddr addr; dbCommon *pdbCommon; rset *prset;
Now get ready to access the array long no_elements,offset,nNew;
double *pdata; dbScanLock(pdbCommon);
status = prset->get_array_info(&addr,&no_elements,&offset)
/* check the following things to see if your code can handle the array
Is offset 0?
The current number of elements is no_elements.
The maximum number of elements is addr.no_elements.
Are these OK with you?
Is addr.field_type OK with you?
You probable want DBF_DOUBLE.
This example assumes double
if(addr.field_type!=DBF_DOUBLE) /*ERROR handle it*/
pdata = (double *)addr.pfield;
/* You can now write the data. also set nNew */
status = put_array_info(&addr,nNew);
status = dbProcess(pdbCommon);
dbScanUnlock(pdbCommon);