1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  <20062007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  <20062007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: R3.13.10 ca_event problem [sls]
To: "Jeff Hill" <[email protected]>, <[email protected]>
Date: Wed, 25 Jan 2006 08:49:59 -1000
Title: Message
Hey Jeff
Interestingly, one of the Adaptive Optics IOCs had the identical problem (a couple of months back) with R3.13.0beta12 and generated the identical invalid address. To correct the problem Erik increased the ring buffer to 3000. However, the problem occurred again on that IOC, yesterday, and with the same 0x30303030 address. Erik stated he tried ‘tt’ but it failed.
tt 0x1e3a648
> trcStack aborted: error in top frame
This is identical to the ‘tt’ attempt on the R3.13.10 empowered IOC last Friday (per K. Tsubota).
Seems to me that the overflow affects taskWd in such a way that the memory corruption occurs at a low level and not from within the application code (two different memory maps on two different IOCs with two wildly different EPICS versions generating the same invalid instruction address). If taskWd simply attempts to suspend the offending task then does that mean the corruption occurs when the ring buffer overflow message is generated (perhaps something as simple as a malformed log message)?
I believe that the highest rate of interrupts, on the IOCs affected, are from the encoder counter boards (40 hz) and that has been solid for more than a decade, and unchanged since 1998. Of course one of the bar code readers could cause a burst of interrupts greater than that but doubtful during the aforementioned events.
Next time the problem occurs I will try to remember to check the processor loading, however, during the events when the ring buffer overflows occurred but a task was not suspended, the loading did not seem excessive.
I have not reviewed the callback request code and will not have time to do so today but I will when I get a chance.
AH
-----Original Message-----
Sent: Tuesday, January 24, 2006 10:10 AM
To: Al Honey; [email protected]
Allan,
The "callbackRequest ring buffer full" message comes from the database function
callbackRequest(). This typically indicates that a device's interrupt production rate
exceeds the the record processing rate (due to CPU saturation). This is related to
a device/record that are configured "scanned on interrupt".
> task 36a5718 CA_event suspended
My best guess at this time is that there is object code
corruption resulting from a wild pointer, but that is only
a wild guess, based on very limited information.
To debug this, we of course need the stack trace from that CA event thread after
this instruction access exception occurs. Type "tt ( event thread's task id )".
> appeared to lose it’s connections to all it’s clients
This would happen if there is CPU saturation. Also watch out for MBUF starvation
occurring with newer versions of vxWorks (which dont dynamically expand the
MBUF pool should it becomes depleted).
Jeff
Sent: Tuesday, January 24, 2006 12:03 PM
To: [email protected]
Subject: R3.13.10 ca_event problem
Aloha
Finally, 8 years after deploying R3.13.0beta12, we at the Keck observatory are attempting to deploy R3.13.10.
During about 80 hours of testing we have had 3 events of the form “ring buffer overflow” within a CA_event task. On two of those occasions the Vxworks 5.3.1 system (pPC), on which the error occurred  appeared to lose it’s connections to all it’s clients, even other EPICS empowered IOC systems. The events lasted for 7-12 minutes, after which most connections were re-established (at least one channel to another IOC did not reconnect!). On the third such event a CA_event task was suspended and the following was in the iocLog:
tdc2:1040 Fri Jan 20 13:42:39 2006 filename="../taskwd.c" line number=159
tdc2:1040 Fri Jan 20 13:42:39 2006 task 36a5718 CA_event suspended
tdc2:1040 Fri Jan 20 13:43:28 2006 interrupt: ./taskwd.c" line number=159
tdc2:1040 Fri Jan 20 13:43:28 2006 callbackRequest ring buffer full
It so happened that I was monitoring the IOC via a telnet connection, thereby logging the following, which was not in the iocLog:
instruction access
Exception next instruction address: 0x30303030
Machine Status Register: 0x4000b030
Condition Register: 0x42000040
Task: 0x36a5718 "CA_event"^G
interrupt: callbackRequest ring buffer full
Seeing as the instruction address 0x30303030 is outside of the address space…  life does not seem too good.
I was not physically present during this event so I did not get a chance to perform a task trace before the IOC was rebooted.
I really hate to think that there is an errant pointer somewhere.
Any thoughts would be appreciated.
            Al Honey
            Kevin Tsubota
RE: R3.13.10 ca_event problem [sls] Jeff Hill
Re: R3.13.10 ca_event problem [sls] Andrew Johnson
Prev: Re: Using AAI records under EPICS Tim Mooney
Next: RE: R3.13.10 ca_event problem [sls] Jeff Hill
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  <20062007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: RE: Using AAI records under EPICS Steven Hartman
