1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  <2006>  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  <2006>  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: Motion control failure at APS
To: "Ronald L. Sluiter" <[email protected]>, "Emmanuel Mayssat" <[email protected]>
Cc: "EPICS" <[email protected]>, <[email protected]>
Date: Mon, 13 Nov 2006 15:45:28 -0600
The transition cards that the APS BCDA group built to connect the
OMS58/MAXv and the ACS Step-Pak drivers have on-board de-glitching
capacitors.  These increase the time constant on the limit switch lines
so that we never see problems, even with very long lines from the
controller to the driver.
This is generally a simple and cheap solution.
> -----Original Message-----
> From: Ronald L. Sluiter [mailto:[email protected]]
> Sent: Monday, November 13, 2006 2:15 PM
> To: Emmanuel Mayssat
> Cc: EPICS
> Subject: Re: Motion control failure at APS
> The OMS VME58 is susceptible to noise on the limit switch lines.
> This has been the most frequent problem that I have been called on
> the diagnose.
> Kurt Goetze and I did some testing to see if this is a
> problem with the
> MAXv.  Of course we can't quantify it, but it appears that OMS has
> done a much better job with the MAXv on this issue.
> Ron
> Emmanuel Mayssat wrote:
> >I actually had the exact opposite problem.
> >My motor controller would barely start a move.
> >The limit switches were reported as not closed, and the
> apparatus was in
> >a safe position to operate. The problem was due to glitches
> on the limit
> >switch cables (we actually never observed those glitches).
> The problem
> >was reproducible in a controlled environment (engineering bench).
> >As of today, we think it was due to cable length and cross talking.
> >We rebuild and shortened the cables. It immediately worked.
> >Food for thoughts and... time for lunch,
> >Emmanuel
> >On Mon, 2006-11-13 at 12:56 -0600, Mark Rivers wrote:
> >>Folks,
> >>We have seen failures in the past where a motor moved
> constantly at a
> >>slow rate right past limit switches on an OMS58.  It
> happened only on a
> >>single axis, not on all 8 axes.
Re: Motion control failure at APS Kurt Goetze
Re: Motion control failure at APS Bill Nolan
Prev: Re: Motion control failure at APS Josh Stein
Next: Re: Motion control failure at APS Kurt Goetze
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  <2006>  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: Re: Motion control failure at APS Ronald L. Sluiter