In the incident Tim describes, a faulty motor/drive connection led to the
motor driver heating up. This particular drive was not fault tolerant, in
the sense that it did not have the capability to shut down when overheated.
Overheating led to the insulation on a toroid melting, and as a result, 48V
was connected directly to the limit line(s). As Tim mentions, these limit
lines are directly connected to the OMS VME58 board's PAL, via the P2
connector. The connector, transition electronics, VME58 board traces,
and PAL were all damaged. The backplane survived and is still in use.
Although we have had several other issues with the MAXv, to my knowledge
we have not seen the problem Ian describes, yet.
Kurt
Tim Mooney wrote:
The most plausible cause I can think of is a short in or across the
motor connector that put motor-drive voltage (~48V in our case) on a
limit-switch line, perhaps only momentarily. I don't know about the
MAXv, but the VME58 has limit-switch lines going straight to a PAL,
which would certainly get crispy under this kind of assault.
We had an OMS VME58 (I think) burn up several years ago (eight,
maybe?). I think Kurt
Goetze has the best handle on what happened, and he's out for a couple
of weeks. I talked to
one of the staff at the beamline where the incident occurred, but I
didn't get a sense that they knew exactly what led up to the incident.
Gillingham, IJ (Ian) wrote:
On the night of 30th December 2007, a fire broke out in one of our
control system's VME crates. Considerable damage was inflicted on the
crate, but fortunately the fire did not spread. On examination of
the crate and VME cards, the P1 connector, to which a "MAXv 8000"
card was connected, had been destroyed by heat/flame. Electrical
burning of some components was evident on the MAXv card, these
components were well away from the direct heat of the main area of
combustion (components close to the fire were of course destroyed).
We are presently trying to ascertain which component caused the
failure (the MAXv card, P1 connector or VME backplane).
Has anyone else experienced this type of event, in particular with
the MAXv motor control card?
Ian Gillingham
Diamond Light Source
This e-mail and any attachments may contain confidential, copyright
and or privileged material, and are for the use of the intended
addressee only. If you are not the intended addressee or an
authorised recipient of the addressee please notify us of receipt by
returning the e-mail and do not use, copy, retain, distribute or
disclose the information in or attached to the e-mail.
Any opinions expressed within this e-mail are those of the individual
and not necessarily of Diamond Light Source Ltd.
Diamond Light Source Ltd. cannot guarantee that this e-mail or any
attachments are free from viruses and we cannot accept liability for
any damage which you may sustain as a result of software viruses
which may be transmitted in or with the message.
Diamond Light Source Limited (company no. 4375679). Registered in
England and Wales with its registered office at Diamond House,
Harwell Science and Innovation Campus, Didcot, Oxfordshire, OX11 0DE,
United Kingdom
- VME Toaster - has anyone else experienced this? Gillingham, IJ (Ian)
- Re: VME Toaster - has anyone else experienced this? Tim Mooney
subArray / waveform problem Shepherd, EL (Emma)
Re: asynRecord immutable fields Eric Williams
<2008>
2025
2026
Re: VME Toaster - has anyone else experienced this? Korhonen Timo
<2008>
2025
2026