1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  <2008>  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  <2008>  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: Inexpensive PLC Ethernet w/EPICS Driver
To: "Luchini, Kristi" <[email protected]>, <[email protected]>
Cc: "Lam, Briant" <[email protected]>
Date: Mon, 17 Mar 2008 23:31:04 -0500
Hi Kristi,
I've read the manual for the Web Server Module that you mentioned.  It is very different from Modbus or similar communications protocols.  With Modbus one can send a command to directly read and write I/O points in the PLC without having to do anything special in the ladder logic.  The Web server module requires writing the ladder logic to use "Communications instructions".  Furthermore, the Web Server Module is actually connected to the PLC via a serial link, so you will not get Ethernet speeds to and from the PLC.
From: [email protected] on behalf of Luchini, Kristi
Sent: Mon 3/17/2008 7:42 PM
To: [email protected]
Cc: Lam, Briant
Subject: Inexpensive PLC Ethernet w/EPICS Driver
Hello,
Can anyone suggest a low-cost options for a plc w/ethernet, touch panel and an existing epics driver?
We current we are looking at the IDEC PLC and Mark Rivers recommended the Koyu from Automation Direct which works with MODBUS.
 - Thanks,
   Kristi
PLC (IDEC) Hardware
Model          Description              Cost
FC5A-D16RK1    Processor               $ 248
FC4A-HPC1      RS232 Module            $  44
FCA-ENET       Ethernet Module         $ 249   http://www.idec.com/language/english/manual/WebServerModuleManual.pdf
FC4A-J8C1      8 Channel (diff) Ai      $ 260
FC4A-K2C1      2 Channel Ao             $ 139
FC4A-N16B3     16 Channel Di            $ 136
FC4A-N16S3     16 Channel Do            $ 192
HG3F-FT22TFB   10.4 Inch Touch Panel    $1650
BX1D-S20A      Terminal Block           $  29
FC9Z-H100A20   Terminal Block Cable     $  34
FC4A-KC2CA     PLC-to Touch Panel Cable $  20
-----Original Message-----
Sent: Monday, March 10, 2008 12:43 PM
To: Luchini, Kristi; [email protected]
Cc: Lam, Briant
Subject: RE: PLC Ethernet Driver for the IDEC MicroLogix 1100
Hi Kristi,
I could not find an online manual for the  FC4A-ENET.  However, some
documentation I saw online for the FC5A-D16RK1 suggests that it is
Modbus compatible.  If so, then you may be able to use my Modbus driver,
which works with Ethernet or serial:
http://cars.uchicago.edu/software/epics/modbus.html
Note that Koyu PLCs from Automation Direct are also less expensive than
Allen Bradley, and they are definitely Modbus compatible.
> [mailto:[email protected]] On Behalf Of Luchini, Kristi
> Sent: Monday, March 10, 2008 12:45 PM
> Cc: Lam, Briant
> Subject: PLC Ethernet Driver for the IDEC MicroLogix 1100
> Hello,
> Has anyone written an EPICC PLC Ethernet Driver for the IDEC
> ethernet module FC4A-ENET
> using MicroLogic 1100. The processor is model FC5A-D16RK1
> This is a much cheaper PLC Model than Allen-Bradley and we
> hope that someone else out there may have already had some
> experience with this hardware.
> Thanks
> - Kristi
PLC Ethernet Driver for the IDEC MicroLogix 1100 Luchini, Kristi
RE: PLC Ethernet Driver for the IDEC MicroLogix 1100 Mark Rivers
Inexpensive PLC Ethernet w/EPICS Driver Luchini, Kristi
Prev: RE: Inexpensive PLC Ethernet w/EPICS Driver Mark Rivers
Next: Re: Memory Problem related to CA? Schoeneburg, Bernd
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  <2008>  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Next: Synergy SVGM5 SBC Matt Rippa
