1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  <20092010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  <20092010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: Schneider Electric - BMXP342020 - CPU340-20
Date: Wed, 21 Jan 2009 09:24:22 +1100
Hi Mauro
Although I have not much of a  chance to play with the M340 series CPU I have looked at the configuration of them in UnityPro and see no reason that the configuration Mark described here (that is used on a Schneider Premium CPU) will not work on the M340.
I’m happy to help with the PLC end if you need any
Regards
Bryce Karnaghan | Controls Specialist | Australian Synchrotron
p: (03) 8540 4135 | f: (03) 8540 4200 | m: 0423 844 592
[email protected] | www.synchrotron.org.au
800 Blackburn Road, Clayton, Victoria 3168
From: [email protected] [mailto:[email protected]] On Behalf Of Mark Rivers
Sent: Wednesday, 21 January 2009 5:45 AM
To: Mauro Giacchini
Cc: [email protected]
Hi Mauro,
The Koyo PLCs support reading the X inputs and Y outputs directly over Modbus.
The Modicon PLCs do not support this, they can only read the M or MW memory locations over Modbus.  Thus, you will need to modify your ladder logic to copy the inputs and outputs you need to M or MW locations (note that you may already be doing this for other purposes).
Here is an example script I run for a Modicon PLC.  I am using the MW locations to read 16-bit analog values and logic bits grouped into 16-bit words.
I am using the M locations as outputs to write bits from EPICS to the PLC.  These are used to request that the PLC perform certain actions if it is safe to do so.
# Modicon PLC
drvAsynIPPortConfigure("Modicon","10.114.2.71:502",0,1,1)
modbusInterposeConfig("Modicon",0,0)
# Read locations %MW0 to %MW16 as words.      Function code=3.
drvModbusAsynConfigure("M1_W000_In",   "Modicon", 3,    0,  16,     0,  100, "Modicon")
# Read locations %MW100 to %MW199 as words.   Function code=3.
drvModbusAsynConfigure("M1_W100_In",   "Modicon", 3,  100,  100,    0,  100, "Modicon")
# Write locations %MW100 to %MW199 as words.  Function code=6.
drvModbusAsynConfigure("M1_W100_Out",  "Modicon", 6,  100,  100,    0,    1, "Modicon")
# Read locations %MW200 to %MW299 as words.   Function code=3.
drvModbusAsynConfigure("M1_W200_In",   "Modicon", 3,  200,  100,    0,  100, "Modicon")
# Read locations %MW300 to %MW399 as words.   Function code=3.
drvModbusAsynConfigure("M1_W300_In",   "Modicon", 3,  300,  100,    0,  100, "Modicon")
# Write locations %MW300 to %MW399 as words.  Function code=6.
drvModbusAsynConfigure("M1_W300_Out",  "Modicon", 6,  300,  100,    0,    1, "Modicon")
# Access 32 bits %M128 to %M160 as outputs.   Function code=5.
drvModbusAsynConfigure("M1_B128_Out",  "Modicon", 5,  128,   16,    0,    1, "Modicon")
# Hex trace format on TCP server
asynSetTraceIOMask("Modicon",0,4)
# Turn on asynError and asynTraceIODriver on TCP server
#asynSetTraceMask("Modicon",0,9)
dbLoadTemplate "$(TOP)/db/Modicon.substitutions"
This is a part of the contents of Modicon.substitutions, the EPICS database:
# asyn record for the underlying asyn TCP port
file "$(ASYN)/db/asynRecord.db" { pattern
{P,              R,               PORT,      ADDR,   IMAX,    OMAX}
{SR05ID01PLC01:  ASYN_REC,        Modicon,     0,      80,      80}
# These are the Mn inputs done with word access (%MW0 - %MW15)
file "$(MODBUS)/db/bi_word.template" { pattern
{P,                R,                            PORT,     OFFSET,       MASK,       ZNAM,        ONAM,       ZSV,      OSV,        SCAN}
{SR05ID01CCG01:,   PRESS_STATUS,                 M1_W000_In,    0,     0x0001,         OK,       Fault,  NO_ALARM,    MAJOR,  "I/O Intr"}
{SR05ID01CCG01:,   PRESS_LATCH_STATUS,           M1_W000_In,    1,     0x0001,         OK,       Fault,  NO_ALARM,    MAJOR,  "I/O Intr"}
{SR05ID01CCG02:,   PRESS_STATUS,                 M1_W000_In,    0,     0x0002,         OK,       Fault,  NO_ALARM,    MAJOR,  "I/O Intr"}
{SR05ID01CCG02:,   PRESS_LATCH_STATUS,           M1_W000_In,    1,     0x0002,         OK,       Fault,  NO_ALARM,    MAJOR,  "I/O Intr"}
{SR05ID01CCG03:,   PRESS_STATUS,                 M1_W000_In,    0,     0x0004,         OK,       Fault,  NO_ALARM,    MAJOR,  "I/O Intr"}
{SR05ID01CCG03:,   PRESS_LATCH_STATUS,           M1_W000_In,    1,     0x0004,         OK,       Fault,  NO_ALARM,    MAJOR,  "I/O Intr"}
{SR05ID01CCG04:,   PRESS_STATUS,                 M1_W000_In,    0,     0x0008,         OK,       Fault,  NO_ALARM,    MAJOR,  "I/O Intr"}
{SR05ID01CCG04:,   PRESS_LATCH_STATUS,           M1_W000_In,    1,     0x0008,         OK,       Fault,  NO_ALARM,    MAJOR,  "I/O Intr"}
{SR05ID01CCG05:,   PRESS_STATUS,                 M1_W000_In,    0,     0x0010,         OK,       Fault,  NO_ALARM,    MAJOR,  "I/O Intr"}
{SR05ID01CCG05:,   PRESS_LATCH_STATUS,           M1_W000_In,    1,     0x0010,         OK,       Fault,  NO_ALARM,    MAJOR,  "I/O Intr"}
Let me know if you have questions or problems:
-----Original Message-----
Sent: Tuesday, January 20, 2009 12:15 PM
To: Mark Rivers
Hi Mark,
the goal to me is monitoring few Inputs/Outputs of those PLC,
therefore, I'm looking to a driver/device support.
Have you got someone EPICS ioc application example to me?
I'm reading your documentation but I've found only the Koyo
documentation, not the PLC Schneider.
Thank you very much to your support.
Mauro.
On Jan 20, 2009 06:33 PM, Mark Rivers <[email protected]> wrote:
> Hi Mauro,
> I'm not sure exactly what you are looking for, but I have used my
> EPICS
> Modbus driver and standard asyn device support with these Schneider
> Modicon PLCs:
> http://cars.uchicago.edu/software/epics/modbus
> Mark
> [mailto:[email protected]] On Behalf Of Mauro Giacchini
> Sent: Tuesday, January 20, 2009 10:55 AM
> To: [email protected]
> Subject: PLC: Schneider Electric - BMXP342020 - CPU340-20
> Dear all,
> Has anyone a device driver for the PLC Schneider Electric - BMXP342020
> CPU340-20 ?
> Thanks,
> Mauro.
> Mauro Giacchini
> Istituto Nazionale di Fisica Nucleare - Laboratori Nazionali di
> Legnaro
> V.le dell'Universita', 2
> 35020 LEGNARO (PD) - ITALY
> Tel. +39.049.8068558
> Fax. +39.049.641925
> Skype yakman000
> EPICS _at_ LNL: http://www.lnl.infn.it/~epics/
Mauro Giacchini
Istituto Nazionale di Fisica Nucleare - Laboratori Nazionali di Legnaro
V.le dell’Universita', 2
35020 LEGNARO (PD) – ITALY
Fax. +39.049.641925
EPICS _at_ LNL http://www.lnl.infn.it/~epics/
This message and any attachments may contain proprietary or confidential information. If you are not the intended recipient or you received the message in error, you must not use, copy or distribute the message. Please notify the sender immediately and destroy the original message. Thank you.
PLC: Schneider Electric - BMXP342020 – CPU340-20 Mauro Giacchini
RE: Schneider Electric - BMXP342020 - CPU340-20 Mark Rivers
Prev: RE: CA.DLL for Windows ? Mark Rivers
Next: CA Problem Szalata, Zenon M.
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  <20092010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: RE: Schneider Electric - BMXP342020 - CPU340-20 Mark Rivers
ANJ, 31 Jan 2014 · Home · News · About · Talk · Base · Modules · Extensions ·