Hi Graham,
The waveform record allocates memory for the waveform at boot time,
according to NELM. All links (including local db links on the same IOC)
store the address of the memory at the time they connect. Thus the
memory must not be re-allocated after booting. Channel access clients
receive the size information when they connect. There is no support in
Channel Access for dynamic array sizes.
As you can see, no part of EPICS is prepared to deal with changing
number of elements. You have to set NELM to the maximum possible number
of elements. The device support may change NORD to indicate the actual
number of valid elements. But a client has to connect to an array with
NELM elements. It has to monitor NORD in addition to VAL to find out the
real array size. The array is filled up with 0 if NORD < NELM.
Best regards,
Dirk
[email protected] wrote:
Hi All,
I am integrating a turn-by-turn BPM system into EPICS and would like to
store the raw BPM pickup data in a waveform record. Due to the nature
of the system, each run can result in a different number of samples for
each BPM pickup, so the array size is unknown in advance and could
potentially be different every run.
Is it possible to resize the number of waveform record elements in my
device support, or do I have to size the waveform record in advance for
the maximum number of samples that could be expected. Most of the
examples of waveform device support I see read the nelm field and return
this fixed amount of data via the records bptr.
Graham