1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <20112012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <20112012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: VMEbus ACFAIL* glitch causes OMS VME58 reboot
To: EPICS <[email protected]>
Date: Fri, 14 Jan 2011 09:13:42 -0600
We recently diagnosed an insidious problem here at the APS.
As with most really insidious problems, this one is caused by
a combination of errors.
We have a Tracewell System 22 VME crate with field swappable
power supply and fan tray that has been experiencing "Oms58_motor"
task crashes for over a year with increasing frequency.
After lots of board swapping, unplugging and plugging things in
and out, we finally determined that the Tracewell VME Power
Monitor is outputting ACFAIL* glitches (~ 7ns) on the VMEbus.
This, combined with the fact that the OMS VME58 board
processes the ACFAIL* line unfiltered, resulted in the VME58
board intermittently rebooting, which in turn caused a VME bus
error, which in turn caused the "Oms58_motor" task to crash.
(Note that the OMS MAXv does not monitor the ACFAIL* signal;
so this problem cannot happen with a MAXv.)
Lesson learned; if you have intermittent VME bus errors on the
memory address of an OMS VME58 board, and board swapping
does not resolve the problem, then check the ACFAIL* signal for
glitches.
Hoping this saves someone days of frustration,
Ron