1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: ether_ip driver for ControlLogix PLCs and 'BOOL' tags
To: "Sinclair, John William" <[email protected]>
Date: Thu, 25 Aug 2011 08:26:53 -0400
Hello:
"Writes set individual bits of a DINT."
That's exactly it.
That's why it works perfectly and efficiently when you assign bi, bo, mbbi,
mbbo records to bits of a DINT, DINT[], BOOL[].
But when you assign a bo to a plain BOOL, this is what happens:
Writing 'true' will write a 0x01 to the PLC.
The PLC, however, will read that back as 0xFF.
When the BO record will next be instructed to write a 'false' value,
it will write a 0 for the first bit, i.e. it will write 0xFE.
If the record was indeed attached to just a bit in a bigger number
( DINT, DINT[], BOOL[] ), that's correct.
But if the tag is just a plain non-array BOOL, the PLC will consider
0xFE==true and still return 0xFF
-> Once you write a '1' (true) to a BOOL tag, it will stay 'true'==0xFF.
You can never get it back to 0 (false).
-Kay
On 8/24/11 22:26 , "John William Sinclair" <[email protected]> wrote:
> I routinely define records as shown below an never see such behavior. Writes
> set individual bits of a DINT. Why is that fundamentally different?
> record(bi,"$(db):BlvIr1:OpnSR") {
>   field(SCAN,"1 second")
>   field(ZNAM, "0")
>   field(ONAM, "1")
>   field(DTYP, "EtherIP")
> # field(INP, "@hrenbt02Cpu1 BlvIr1_OpnSR")
>   field(INP, "@hrenbt02Cpu1 epics_inputs[3] B 11")
> record(bi,"$(db):BlvIr1:ClsSR") {
>   field(ZNAM, "0")
>   field(ONAM, "1")
> # field(INP, "@hrenbt02Cpu1 BlvIr1_ClsSR")
>   field(INP, "@hrenbt02Cpu1 epics_inputs[3] B 12")
> Best,
> John Sinclair
> Kasemir, Kay wrote:
>> Hi:
>> Martin Smith @ APS has found a quirk in the way the ether_ip driver for
>> ControlLogix PLCs and the PLC handle 'BOOL' tags that might be of interest
>> to those that use the driver.
>> The short summary is that you cannot use BI or BO records with plain BOOL
>> tags on the PLC.
>> The binary record support in the ether_ip driver is meant for efficient
>> handling of _bits_. It can read and write bits in a BOOL[], DINT, DINT[]
>> tag. In those cases it reads or writes the whole numbers over the network,
>> then dispatches the individual bits to records.
>> For example, say record A is attached to BOOL[0] or DINT.0,
>> record B is attached to BOOL[1] or DINT.1 and so on.
>> Meaning the records are attached to the bits of a DINT, DINT[] or BOOL[].
>> That all works fine: The driver reads or writes the whole DINT or DINT array
>> or BOOL array and performs the appropriate bit fiddling to interface the
>> bits to records.
>> But if you attach a binary record to a plain, scalar BOOL tag on the PLC,
>> the following happens:
>> The driver still wants to read or write individual bits.
>> A BO record with OUT="@plc MyBOOLTag" will read or write 0 and 1 values.
>> The PLC, however, returns 0 for 'false' and 255 for 'true'.
>> The mismatch between 1 and 255 is the issue at the root of the problem that
>> Martin found in a setup:
>> A BO record would write a "1". The PLC now actually sets the BOOL tag to
>> 255, and the driver from now on sees 255 as a value.
>> If the driver is instructed to write a "0" for the BO record, it will write
>> 254, i.e. the received value of 255 with the first bit set to 0.
>> The PLC, however, considers 254!=0 also as 'true' and keeps the BOOL tag at
>> 255.
>> Longer summary:
>> Use binary records (BI, BO, MBBI, MBBO) with BOOL[], DINT or DINT[].
>> Not with individual BOOL tags, which - even if it were supported - would be
>> slower than array transfers anyway.
>> Thanks,
>> Kay
Re: ether_ip driver for ControlLogix PLCs and 'BOOL' tags John William Sinclair
Prev: RE: Dynamic images in BOY Mark Rivers
Next: Re: Installing virtual linac. Permission denied (noob question) J. Lewis Muir
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: Re: ether_ip driver for ControlLogix PLCs and 'BOOL' tags John William Sinclair
Next: Installing virtual linac. Permission denied (noob question) Tim Fulcher