1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: Modbus data to float32 ?
To: "Mark Rivers" <[email protected]>
Cc: [email protected]
Date: Wed, 21 Sep 2011 08:13:52 -0700
Now that I read my solution in the cold light of dawn I think that I should have included how to read the two 16-bit values in a way that should minimize the possibility of mixing old/new data.
Q. My PLC returns floating point values as two 16 bit integers.  How can
I convert these to a floating point value?
A. Here's a CALC record that can do this.   The expression is longer
than 40 characters but that's a problem only if a client tries to read
the expression as an EPICS string.
# Assume that the registers are processsed in order
# so the low word (offset N) value is ready by the time
# that the high word (offset N+1) forward link is processed.
record(longin,"$(P)vacuumHiWord") {
    field(DESC, "R2089")
    field(DTYP, "asynInt32")
    field(INP,  "@asyn(rfDrive_r0i, 92, 1)")
    field(SCAN, "I/O Intr")
    field(FLNK, "$(P)vacuumLoWord")
record(longin,"$(P)vacuumLoWord") {
    field(DESC, "R2088")
    field(INP,  "@asyn(rfDrive_r0i, 91, 1)")
    field(FLNK, "$(P)vacuum")
# Convert to IEEE-754 32-bit float.
# No INF/NAN, no denormalized numbers.
record(calc,"$(P)vacuum") {
    field(INPA, "$(P)vacuumHiWord")
    field(INPB, "$(P)vacuumLoWord")
    field(INPC, "0x8000")   # Hi word, sign bit
    field(INPD, "0x7F80")   # Hi word, exponent mask
    field(INPE, "0x00FF")   # Hi word, mantissa mask (incl hidden bit)
    field(INPF, "150")      # Exponent offset plus 23-bit mantissa shift
    field(INPG, "0x0080")   # Mantissa hidden bit
    field(INPJ, "65536")    # Hi/Lo mantissa ratio
    field(CALC, "(A&D?(A&C?-1:1):0)*((G|A&E)*J+B)*2^((A&D)/G-F)")
    field(PREC, "4")
On Sep 21, 2011, at 7:43 AM, Mark Rivers wrote:
> I'll see if I can beat Eric Norum in responding to this!  He solved the
> same problem and sent me a solution yesterday.
Eric Norum
[email protected]
Modbus data to float32 ? Olivier Zimmermann
RE: Modbus data to float32 ? Mark Rivers
Prev: RE: Modbus data to float32 ? Mark Rivers
Next: Fwd: Time, technology and leaping seconds Andrew Johnson
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Next: Epics C# Library problems Perrier Pierre