1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: using tcp with modbus over asyn
To: "Mark Rivers" <[email protected]>
Cc: [email protected]
Date: Fri, 18 Nov 2011 13:07:31 -0800
I suspect that that 40150 is really supposed to be 400150 (register 150 in the 'read holding registers' region) and that the salient portion is actually the 150 (maybe plus or minus 1 to deal with starting counting at 0 or 1 -- modbus documentation seems to be really bad at distinguishing which).
On Nov 18, 2011, at 1:00 PM, Mark Rivers wrote:
> James,
> You could try leaving off the leading 40 in 40150, i.e. just 150 and see
> what you get.  It says in my documentation that:
> " Note that 16-bit Modbus addresses are commonly specified with an
> offset of 400001 (or 300001). This offset is not used by the modbus
> driver, it uses only the 16-bit address, not the offset."
> This does not seem to apply in your case, since the address you list is
> a valid 16-bit number, but it's worth a try.
> Also, do you have the exact startup script syntax you used with the old
> ModbusTCP driver?  I could then look at that old code and see if it is
> doing something differently.
> I notice from your e-mail address that you are at the APS?  I could walk
> over and take a look if you'd like.
> Mark
> -----Original Message-----
> From: Eric Norum [mailto:[email protected]]
> Sent: Friday, November 18, 2011 1:24 PM
> To: Mark Rivers
> Cc: James Stevens; [email protected]
> Could your equipment have another level of mapping/offset being applied
> somewhere?
> As an illustration, I am reading the values from a Horner PLC -- here's
> the salient portion of the st.cmd file:
> # ModbusStartAddress = Horner Register Number + 2999
> #       i.e. Horner %R1 is Modbus Offset 3000
> # Read 97 starting at Modbus 4996: Horner %R1997 through %R2093,
> inclusive
> drvModbusAsynConfigure("rfDrive_r0i", "rfDrivePLC_1", 0, 3, 4996, 97, 0,
> 1000, "Horner")
> # Write 1 starting at Modbus 3999: Horner %R1000
> drvModbusAsynConfigure("rfDrive_r0o", "rfDrivePLC_1", 0, 6, 3999,  1, 0,
> 2000, "Horner")
> You can see that there's an offset of 2999 between the register number
> in the PLC and the number passed in the Modbus packet....
> On Nov 17, 2011, at 9:01 PM, Mark Rivers wrote:
>> Hi James,
>> OK, so it appears the slave address is OK.
>> The device is definitely answering your query.
>> On page 85 of that manual it shows that where the Modbus slave module
> gets its data is configurable.  Is it possible that this meter is not
> configured to get the data you think it is at addess 40150?
>> Does this same exact meter work correctly with the older ModbusTCP
> driver?  If so then you may need to run "ethereal" and capture network
> packets to see what the difference is between the old driver and the new
> asyn driver.
>> Mark
>> ________________________________
>> From: James Stevens [mailto:[email protected]]
>> Sent: Thu 11/17/2011 6:49 PM
>> To: Mark Rivers
>> Mark,
>> Thank you for your response.
>> On page 85 of the user guide it states
>> that "The Modbus Unit ID of the meter
>> over Ethernet is 100."
> http://www.sea.siemens.com/us/internet-dms/btlv/PowerDistributionComm/Po
> werDistribution/Docs/9510_9610_User_Guide.pdf
>> When I tried setting the slave address to
>> zero, I got a timeout error.
>> epics> 2011/11/17 18:46:33.771 drvModbusAsyn::doModbusIO port
> UPSDASHCP2 error calling writeRead, error=164.54.2.216:502 timeout:
> Resource temporarily unavailable, nwrite=6/6, nread=0
>> 2011/11/17 18:46:38.269 S:UPS:CP2:I4ai:AI devAsynInt32 process read
> error
>> 2011/11/17 18:46:38.270 S:UPS:CP2:IAvgMax:AI devAsynInt32 process read
> error
>> 2011/11/17 18:46:38.270 S:UPS:CP2:IAvgMin:AI devAsynInt32 process read
> error
>> 2011/11/17 18:46:38.271 S:UPS:CP2:aa:AI devAsynInt32 process read
> error
>> 2011/11/17 18:46:38.271 S:UPS:CP2:f:AI devAsynInt32 process read error
>> 2011/11/17 18:46:38.271 S:UPS:CP2:p1a:AI devAsynInt32 process read
> error
>> 2011/11/17 18:46:38.271 S:UPS:CP2:p2a:AI devAsynInt32 process read
> error
>> 2011/11/17 18:46:38.271 S:UPS:CP2:p3a:AI devAsynInt32 process read
> error
>> Regards--Jim Stevens
>> ----- Original Message -----
>> From: "Mark Rivers" <[email protected]>
>> To: "James Stevens" <[email protected]>, [email protected]
>> Sent: Thursday, November 17, 2011 6:23:43 PM
>> Subject: RE: using tcp with modbus over asyn
>> Hi James,
>>> How can I verify that I am reading the correct base address?
>> Here is the message that was sent to the Modbus device:
>> 00 01 00 00 00 06 64 03 9c d6 00 10
>> The first 6 bytes of this message are the modbusMBAPHeader:
>> typedef struct modbusMBAPHeader_str
>>   unsigned short transactId;
>>   unsigned short protocolType;
>>   unsigned short cmdLength;
>> } modbusMBAPHeader;
>> They are not very interesting, but they look correct.  cmdLength=6,
>> which is the length of the modbusReadRequest below.
>> The next part of the message is the modbusReadRequest
>> typedef struct modbusReadRequest_str
>>   unsigned char    slave;
>>   unsigned char    fcode;
>>   unsigned short   startReg;
>>   unsigned short   numRead;
>> } modbusReadRequest;
>> So slave = 0x64 = 100
>> That is the slave address you told it to use in
>> drvModbusAsynConfigure().  Are you sure this is correct?  All Modbus
> TCP
>> devices I have used had a slave address of 0.
>> fcode = 03
>> That is the function code you told it to use.  That seems correct,
>> 3=Read Holding Registers.
>> startReg = 9c d6 = 40150
>> That is the base address you told it to use.
>> numRead = 00 10 = 16
>> That is the length you told it to read.
>> So it appears to me that the message being sent to the device is
>> correct.
>> Here is the response you are getting from the device:
>> 00 01 00 00 00 23 64 03 20 ff ff ff ff ff ff ff ff ff ff ff
>> ff ff ff ff ff ff ff ff ff ff ff ff ff ff ff ff ff ff ff ff
>> ff
>> The first 6 bytes of the response are again the modbusMBAPHeader:
>> } modbusMBAPHeader;
>> So the cmdLength = 0x23 = 35.
>> I believe that what comes next is the slave address (0x64=100), though
>> that is skipped in the driver.
>> Next comes the modbusReadResponse:
>> typedef struct modbusReadResponse_str
>>   unsigned char  byteCount;
>>   unsigned char  data[1];
>> } modbusReadResponse;
>> So the fcode=03 which is correct.  If the device returns an error it
>> changes the fcode on the return to "or" it with MODBUS_EXCEPTION_FCN.
>> #define MODBUS_EXCEPTION_FCN            0x80
>> That is tested as follows:
>>   if (readResp->fcode & MODBUS_EXCEPTION_FCN) {
>>       exceptionResp = (modbusExceptionResponse *)pPlc->modbusReply;
>>       asynPrint(pPlc->pasynUserTrace, ASYN_TRACE_ERROR,
>>                 "%s::doModbusIO port %s Modbus exception=%d\n",
>>                 driver, pPlc->portName, exceptionResp->exception);
>> byteCount = 0x20=32, so it is returning you 32 bytes.  That is
> correct,
>> since you asked for 16 holding registers.
>> So it looks like the device is responding as expected.  I don't know
> why
>> your data is wrong, except that perhaps you are using the wrong slave
>> address?
>> Cheers,
>> Mark
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of James Stevens
>> Sent: Thursday, November 17, 2011 5:43 PM
>> To: [email protected]
>> Subject: using tcp with modbus over asyn
>> Let me restate my last post.
>> I am trying to update a soft IOC using the modbusIP
>> driver (version 1-1-asd6) from the Canadian Light
>> Source to Mark Rivers' modbus over asyn version
>> 2-1.
>> The soft IOC is reading a Siemens 9610 Power
>> Meter on the accelerator network.
>> I started by trying to read an unsigned 16 bit
>> register at the 40150 decimal base address, but
>> the values read back from the power meter are
>> all ff's.
>> base address?
>> #ups-cp2
>> drvAsynIPPortConfigure("L0","164.54.2.216:502",0,0,1)
>> modbusInterposeConfig("L0",0,5500,0)
> drvModbusAsynConfigure("UPSDASHCP2","L0",100,3,40150,16,0,5000,"9610PM")
>> #asynSetTraceMask("L0",0,3)
>> asynSetTraceIOMask("L0",0,2)
>> ## Load record instances
>> dbLoadRecords("db/SIEM9610.vdb","L=CP2")
> dbLoadRecords("db/asynRecord.db","P=SR:,R=SIEM:9610,PORT=L0,ADDR=0,OMAX=
>> 0,IMAX=0")
>> cd /home/helios5/JBS/upsmbus/1/iocBoot/siocupsmon
>> iocInit
>> Starting iocInit
>> ## EPICS R3.14.11-asd1 $R3-14-11$ $2009/08/28 18:47:36$
>> ## EPICS Base built Aug 28 2009
>> cas warning: Configured TCP port was unavailable.
>> cas warning: Using dynamically assigned TCP port 52753,
>> cas warning: but now two or more servers share the same UDP port.
>> cas warning: Depending on your IP kernel this server may not be
>> cas warning: reachable with UDP unicast (a host's IP in
>> EPICS_CA_ADDR_LIST)
>> iocRun: All initialization complete
>> epics> 2011/11/17 17:40:24.571 164.54.2.216:502 write 12
>> 2011/11/17 17:40:24.574 164.54.2.216:502 read 41
>> ff
> Eric Norum
> [email protected]
Eric Norum
[email protected]
Re: using tcp with modbus over asyn James Stevens
RE: using tcp with modbus over asyn Mark Rivers
Re: using tcp with modbus over asyn Eric Norum
Prev: Re: using tcp with modbus over asyn James Stevens
Next: Re: using tcp with modbus over asyn James Stevens
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: RE: using tcp with modbus over asyn Mark Rivers
