1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: CARS modbus output record initialization
To: "'John Dobbins'" <[email protected]>, EPICS Tech-Talk <[email protected]>
Date: Fri, 3 Feb 2012 16:04:02 +0000
Hi John,
We need to figure out if this is a general problem in the EPICS modbus driver, or something specific to the Wago.  I don't think it is anything that has changed since Modbus R1-2, because there is nothing in the release notes about it.
I do seem to vaguely recall that the Wago may be different from other Modbus devices in that the Modbus address for register read operations may be different from the Modbus address for register write operations.  That was the reason for the final plcType argument to drvModbusAsynConfigure, so we could do any model-dependent differences.  But there is no model-dependent code in the driver yet, because we have not yet found a need for it. But perhaps the Wago will need it.
Here's what I suggest you do.  You need to turn on asynTrace debugging beginning in the drvModbusAsynConfigure() function. This will let us see that the initial readOnce data read back from the device is correct. However, that is before you could specify change the asynTrace flags in your startup script for that port, because it is the port creation function.
If you were running asyn R4-11 or later you could do the following in your startup script before the drvModbusAsynConfigure command:
asynSetTraceIOMask "",0,2
asynSetTraceMask "",0,255
That would set the default asynTrace mask, so you would get debugging information even in the drvModbusAsynConfigure function.  However, since you are running R4-9 you cannot do this.  Instead you need to temporarily modify the source code as follows:
    /* Connect to device */
    status = pasynManager->connectDevice(pPlc->pasynUserTrace, pPlc->portName, 0);
    if (status != asynSuccess) {
        errlogPrintf("%s::drvModbusAsynConfigure port %s"
                     " connectDevice failed %s\n",
                     driver, pPlc->portName, pPlc->pasynUserTrace->errorMessage);
         return(asynError);
pasynTrace->setTraceIOMask(pPlc->pasynUserTrace, 2);
pasynTrace->setTraceMask(pPlc->pasynUserTrace, 255);
You are adding the last 2 lines above.
That should provide complete debugging information starting near the end of the drvModbusAsynConfigure function, when it does the readOnce operation on output records.
You need to see whether the initial value read from the device and the initial values passed to the ao device support from the readInt32() function are correct.
You should also read the Wago documentation to see if my vague memory is correct: are the Modbus addresses used to read the registers different from the Modbus addresses used to write the registers?
Cheers,
-----Original Message-----
From: [email protected] [mailto:[email protected]] On Behalf Of John Dobbins
Sent: Friday, February 03, 2012 8:52 AM
To: EPICS Tech-Talk
Subject: CARS modbus output record initialization
I am using the CARS modbus device support with a WAGO I/O System (controller 750-341)
One thing I am having trouble getting to work is output record initialization. This is an old version of modbus support R1-2, asyn R4-9, base R3.14.9
Specifically, for modbus function code 6 I create a block
# Write 1 register,  Function code=6
drvModbusAsynConfigure("WAGO_OUTS", "WAGO", 6, 0, 4, 0,    1, "WAGO_750_341")
There are four analog output records attached to this block which look like
record(ao,"wagoTest_out_0") {
    field(DTYP,"asynInt32")
    field(OUT, "@asynMask(WAGO_OUTS 0 -16 1000)")
    field(LINR,"LINEAR")
    field(EGUL,"-10")
    field(EGUF,"10")
    field(LOPR,"-10")
    field(HOPR,"10")
    field(PREC, "3")
 When the IOC starst up only the first of the four records is initialized with the value currently in the controller.
All four records show UDF = 0, the second has a non-zero but incorrect value, the third and fourth have the value zero.
Thanks for you advice.
John Dobbins
Cornell University
Re: CARS modbus output record initialization John Dobbins
Prev: CARS modbus output record initialization John Dobbins
Next: Re: CARS modbus output record initialization John Dobbins
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
