1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: [StreamDevice] ?
Date: Mon, 4 Jun 2012 17:06:24 +0400
Hey Mark!
Do you mean I should uncomment this line:  in "CH\$1:SCA?"; ?
setY {
    ReplyTimeout = 5000;
    out 'CH\$1:SCA %g';
    in "CH\$1:SCA?";
    @init {
            out "CH\$1:SCA?";
        in ":CH\$1:SCALE %g";
This won't work because when the probe_ch1 is processed it causes CHx_Voltage ($(P)$(R)setY1) to process, the latter will send the command to set the current vertical resolution - so it will first set the current value, then will read the current value, not the new value. You see - I have to either use open_loop or closed_loop, not both at the same time. Or I could add another readback record, but this will mess up the HMI with another widget.
On Mon, Jun 4, 2012 at 3:31 PM, Mark Rivers <[email protected]> wrote:
I would suggest having  CHx_Voltage read the current vertical resolution.  Leave this record Passive.  But have the  probe_ch1 record's FLNK be CHx_Voltage, so it reads the vertical scale once each time you change the probe attenuator.
From: [email protected] [[email protected]] on behalf of Pavel Masloff [[email protected]]
Sent: Monday, June 04, 2012 3:23 AM
To: Rod Nussbaumer; EPICS Tech Talk
Subject: [StreamDevice] ?
Hi Rod,
You mentioned you are using StreamDevice to talk to your Tek scopes. I am having difficulties with the Probe Attenuator setting. So you basically change it say from 1 to 10, and the scope automatically changes the voltage on a channel from say 1V to 10V/DIV.
I don't want StreamDevice to poll the scope once a second (or even worse I/O interrupt) to get this change (wanna leave it Passive), so I can change my Attenuator PV (Passive record) it then forwards the CHx_Voltage to ask the scope the current Y-axis resolution.
The problem is that the AO record can be either closed-loop (via db links) or open-loop (via CA).
I don't know what to do.
In other words:
On the screenshot is my HMI (http://imageshack.us/photo/my-images/337/scope.jpg/). So when I change the Attenuator_1 setting (probe_ch1) from 1 to 10, my CH_1 voltage (setY1) remains the same = 0,2 V, when in fact on the scope it is 2 V. Is there a way my setY1 could update its value, but not process?
record(ao, "$(P)$(R)setY1")
   field(DESC, "Set VOLTS/DIV channel 1")
   field(DTYP, "stream")
   field(OUT,  "@devTPS20xx.proto setY(1) $(PORT) $(A)")
   field(EGU, "V")
record(ao, "$(P)$(R)probe_ch1") {
 field(DESC, "Probe voltage attenuation 1")
 field(OUT, "@devTPS20xx.proto probe(1) $(PORT) $(A)")
setY {
    out 'CH\$1:SCA %g';
   #in "CH\$1:SCA?";
   @init {
           out "CH\$1:SCA?";
probe {
   out 'CH\$1:PRO %g';
   @init {
           out 'CH\$1:PRO?';
       in ':CH\$1:PROBE %g';
#getY {
#    out 'CH\$1:SCA?';
#    in "%g";
Hope everything is understandable.
Best regards,
Pavel Maslov, MS
Controls Engineer at Pulsed power Lab
Efremov Institute for Electro-Physical Apparatus
St. Petersburg, Russia
Mobile: +7 (951) 672 22 19
Landline: +7 (812) 461 01 01
Best regards,
Pavel Maslov, MS
[StreamDevice] ? Pavel Masloff
RE: [StreamDevice] ? Mark Rivers
Prev: RE: [StreamDevice] ? Mark Rivers
Next: Quiz for C experts Andrew Johnson
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Next: Re: [StreamDevice] ? Pavel Masloff