1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <2013>  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <2013>  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Horner PLC %T readout
To: EPICS Tech-Talk <[email protected]>
Date: Thu, 13 Jun 2013 14:10:43 -0700
Has anyone used the EPICS Modbus support to read %T ("Coil Status") values from a Horner PLC?
The document describing the mapping to Modbus register offsets is
Attachment: Cscape User & Programming Reference Manual, m031304 page 78.pdf
Description: Adobe PDF document
The vendor that supplied the equipment with a Horner PLC embedded in it provided a spreadsheet that shows the interlock status values as T513 through T624, inclusive.
According to the table, T513 would be Modbus offset 6512 and read with function code 1 (Read Coil Status).
The IOC startup script has the following line
drvModbusAsynConfigure("etmHPA_r0b", "etmHPAPLC_2", 0, 1, 6512, 112, 0, 1000, "Horner")
which says to read 112 registers starting at offset 6512 with function code 1.
The first binary-in record is
record(bi,"$(P)T513") {
    field(DESC, "HPA Door Open (H)")
    field(DTYP, "asynInt32")
    field(INP,  "@asyn(etmHPA_r0b, 0, 1)INT16")
    field(SCAN, "I/O Intr")
    field(ZNAM, "OK")
    field(ONAM, "Fault")
which says that it gets its value from the first register in the block read by the command shown above.
This all looks right to me.
But…..
all the interlock binary-in records always show a value of 0.
I'm clearly doing something wrong, but I can't tell what.
Advice, suggestions, etc. gratefully accepted.
Eric Norum
[email protected]
RE: Horner PLC %T readout Mark Rivers
Prev: Re: calc DTYP James F Ross
Next: RE: Horner PLC %T readout Mark Rivers
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <2013>  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026