1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: Modbus
To: Zenon Szalata <[email protected]>
Date: Tue, 6 Aug 2013 00:45:50 +0000
The timeout used  by the drvAsynIPPort driver is the one passed in pasynUser->timeout, which is taken from pPvt->timeout in modbusInterpose.c.
The pasynOctet->read() routine is the readIt function in drvAsynIPPort.c.
When readIt fails what is the return code, and what is eomReason?
Sent: Monday, August 05, 2013 3:01 PM
To: Mark Rivers
Cc: Williams Jr., Ernest L.; [email protected]
Subject: Re: Modbus
Hi Mark,
I think that the timeout you refer to is controlled via the third
argument to modbusInterposeConfig routine.  This is set to 1000 for all
Beckhoff IOCs.
I have not used the asyn trace facility because there are large number
of IOs happening in one second.  I will try it.
I verified using a print statement in the readIt routine in
modbusInterpose.c that the pPvt->timeout is 1.0, so, if this is the real
timeout, then it is not used in the IO request.
Is there a timeout in the drvAsynIPPort driver?
I am looking at modbusInterpose.c and I find it difficult to tell what
timeout the read routine is using.  Here is the line from modbusInterpose.c:
       status = pPvt->pasynOctet->read(pPvt->octetPvt, pasynUser,
                        pPvt->buffer, nRead, &nbytesActual, eomReason);
I can't tell how the pasyOctet->read routine is coded; not sure where it
is defined and what timeout is used in the routine which ultimately
issues the modbus read request.
Now, in my new code, I put print statements in the writeIt and readIt
routines in the modbusInterpose.c file and I see that the readIt fails
immediately after writeIt completes with no perceivable delay.
So I am confused.
In the case of the IOCs using your modbus support module, there could be
some other effect causing the error.
For better or worse in these IOCs, I am setting up the IOCs such that
drvModbusAsynConfigure is called for each Beckhoff bus terminal type.  I
use 100 ms period for the poller loop in each.  I think each thread
loops asynchronously with respect other threads. Therefore it is
conceivable that often a write is issued from one thread when the
coupler is not ready as it is processing some IO from another thread.  I
did not test this to see if this is indeed happening.
To avoid this I have created a separate modbus IO class object in my new
code, which uses a message queue to coordinate orderly execution of IO
requests, which is done in a poller loop in this class. Requests for IO
from multiple threads are scheduled for execution via the message queue.
Thanks Mark,
Zen
On 08/05/13 10:23, Mark Rivers wrote:
> Hi Zen,
> What timeout are you using for your TCP read?  The read does not actually put anything on the Ethernet, it just waits for a message to arrive from the Beckoff.  So if you use a timeout of 1 second or so then it should never time out, assuming the module really does answer within 20 ms or so.
> You need to turn on asynTrace in the underlying drvAsynIPPort driver to see exactly the timing of what is being sent and received by that driver.
> Mark
> From: Zenon Szalata [[email protected]]
> Sent: Monday, August 05, 2013 11:33 AM
> To: Mark Rivers; Ernest Williams; [email protected]
> Subject: Modbus
> Hi Mark,
> I am nearly done with my version of modbus TCP for use with Beckhoff
> hardware.  I have a few IOCs using this support module and all seems to
> be working well in my test area.
> I have deployed an IOC for a couple of stepper motors controlled by
> Beckhoff devices in a production area and discovered that the IOC is
> generating many errors.
> The error is:
>    2013/08/05 08:55:14.982 modbusAsyn::doModbusIO port BKH15 error
> calling writeRead, error=sioc-esb-bkh15:502 timeout: Resource
> temporarily unavailable, nwrite=6/6, nread=0
> Now, modbusAsyn is the name I used for the file which has the two
> routines I took from your file drvModbusAsyn.  Looking at the log files
> of the IOCs used in the same production area which control Beckhoff
> devices and which are built with your modbus support module, I see that
> the same errors are generated.  Here is an example:
> 2013/06/16 13:19:25.918 drvModbusAsyn::doModbusIO port BKH10_CPL_R0
> error calling writeRead, error=sioc-esb-bkh10:502 timeout: Resource
> People who use these IOCs ignored these errors because mostly they did
> not matter.
> In the case of the stepper motor controller IOC it does matter. First of
> all I realized that the difference between my testing environment and
> that of production is the computer speed and a different networking
> environment.  The production computer used for the Beckhoff IOCs is much
> faster.  So it seems that there is some timing issue at work here.
> After putting print statements in various places, I see that the routine
> writeIt in modbusInterpose.c file always succeeds but the routine readIt
> in the same file fails from time to time.  I reread the manual for the
> Beckhoff BK9000 Ethernet coupler and came across a statement saying that
> the coupler takes from 13 to 15 ms to process a modbus message.  So it
> seems that the read comes too soon after the write.  In my version of
> the modbus support module for Beckhoff, I have added a 20 ms delay after
> the pasynOctet->write in modbusInterpose.c and this has mostly solved
> the problem.  I say mostly, because I still see this error message but
> very infrequently.
> I am writing all this because I don't understand why this error is
> generated so I am not sure if the direction I took to fix the problem is
> correct.  I also think that your modbus support module may need to be
> modified if it is to be used with Beckhoff devices.
> I would like to hear what you think about this.
> Thanks,
> Zen
Re: Modbus Zenon Szalata
RE: Modbus Mark Rivers
Prev: Re: Modbus Zenon Szalata
Next: Re: Modbus Zenon Szalata
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026