Hi Dirk
Thank you for the explanation. I think, I noticed some discussions whether StreamDevice should manage autoconnection or not.
So without the autoconnect part in StreamDevice, should the manual connection management (connect/disconnect protocol commands) do the job ?
Our IOCs with sockets are fine, calling disconnect protocol command cause TCP socket close and connect gets it connected back.
I think, USB serial devices are tricky with the fact, that Linux kernel removes the device when they are physically disconnected. This happens if some controlled lab equipment has RS232->USB converted integrated (like our case).
I managed to configure udev to keep its device name and file persistent. e.g.: udevrule for all Prolifics 2303"
KERNEL=="ttyUSB*", ATTRS{idVendor}=="067b", ATTRS{idProduct}=="2303", OPTIONS="ignore_remove", NAME+="ttyUSBPIC"
# (use of ATTRS{serial}=="FTFCFOX8" instead of Vendor/Device ID provides really unique identification, but it is not set in every usb device)
However, even if the rule is applied, major & minor of the device file changes whenever udev increments number of usb-serial devices in system. I didn't investigate what e..g: read() syscall gets if this change occurs, I'm afraid.
When a serial HW is permanently present in system (like UART chip and so /dev/ttyS0), IOC still can talk to it in some way. This is big difference, I think.
Tomas
Od: [email protected] [[email protected]] za uživatele Dirk Zimoch [[email protected]]
Odesláno: 11. dubna 2014 9:22
Komu: [email protected]
Předmět: Re: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort
Hi Tomáš,
I will have a look. In older versions of StreamDevice, I check the
connection state at each access and try to connect if necessary. But I
have been told that this is wrong behavior and I should better leave it
to asyn to do the auto connect. So I removed the connect code from
StreamDevice. This worked fine with sockets. But I have to investigate
what is missing with USB to serial. I also check with Mark and Eric. But
it may take a while...
Dirk
On 10.04.2014 13:24, Mazanec Tomáš wrote:
> In synApps 5.7, if the usb-serial device is physically disconnected,
> while the IOC is running, the command:
> asynReport(10, PORT) says the asyn port is still connected:
> PORT multiDevice:No canBlock:Yes autoConnect:Yes
> enabled:Yes connected:Yes numberConnects 1
> nDevices 0 nQueued 0 blocked:No
> asynManagerLock:No synchronousLock:Yes
> exceptionActive:No exceptionUsers 2 exceptionNotifys 0
> interposeInterfaceList
> asynOctet pinterface 0x7fbbfb51f6a0 drvPvt 0x1489670
> interfaceList
> asynCommon pinterface 0x7fbbfb51ca80 drvPvt 0x1486740
> asynOption pinterface 0x7fbbfb51caa0 drvPvt 0x1486740
> asynOctet pinterface 0x7fbbfb51ee40 drvPvt 0x1486740
> Serial line /dev/ttyUSBPIC: Connected
> fd: 5
> Characters written: 164
> Characters read: 287
> What also happens, and I didn't noticed, is IOC's process takes 100% CPU
> usage and traceFlow bit within traceMask in Asyn reports hundreds of
> these lines in a second:
> 2014/04/10 13:06:39.575 /dev/ttyUSBPIC read.
> However, an attempt to reconnect asyn port with asynRecord ends with no
> success and this messsage output:
> 2014/04/10 13:04:32.374 EEE:asynrec: special queueRequest timeout
> Thanks,
> Tomas
> *Od:* Mark Rivers [[email protected]]
> *Odesláno:* 8. dubna 2014 18:47
> *Komu:* Mazanec Tomáš; [email protected]
> *Předmět:* RE: Streamdevice 2.6 autoconnection failure using
> drvAsynSerialPort
> In synApps 5.7 what happens if you use an asynRecord to force the
> asynPort to reconnect. Does StreamDevice then start working?
> When the device is disconnected does asyn report that it is
> disconnected? Use the following command when the device is disconnected:
> asynReport 10 ASYN_PORT_NAME
> Mark
> *From:*Mazanec Tomáš [mailto:[email protected]]
> *Sent:* Tuesday, April 08, 2014 9:20 AM
> *To:* Mark Rivers; [email protected]
> *Subject:* RE: Streamdevice 2.6 autoconnection failure using
> drvAsynSerialPort
> Hi Mark
> Thanks for a quick response.
> The IOC runs on Scientific Linux 6.5 x86-64 and its default kernel.
> Yes, I have upgraded it (from 6.4 to 6.5) prior to SynApps upgrade.
> Linux udev system is configured in a way that my usb-serial device gets
> always the same device name (/dev/ttyUSBPIC) no matter what other
> devices are present (major, minor device numbers can change).
> I've double-checked Asyn 4.21 re-connection ability using asynRecord
> (.CNCT, .PCNCT).
> It works fine, so the issue might be a glitch in the new StreamDevice.
> Nevertheless, I've kept SynApps-5-6 installed and compared re-connection
> behavior to 5.7.
> The older version is fine -- If my usb-serial device is physically
> disconnected, IOC with SynApps-5-6 reports:
> 2014/04/07 16:55:20.994 PORT EEE:volts: connection closed in write
> 2014/04/07 16:55:25.994 PORT EEE:volts: pasynCommon->connect() failed:
> /dev/ttyUSBPIC Can't open No such device
> 2014/04/07 16:55:25.994 PORT EEE:volts: Protocol aborted
> and when the usb-serial device is connected back, R/W operations
> continue as usual.
> Whereas with the new version (5.7), IOC shell is kind of silent unless I
> try to reload StreamDevice protocol :
> epics> streamReload EEE:volts
> 2014/04/08 11:46:52.567355 _main_ StreamCore::finishProtocol(EEE:volts):
> Still waiting for writeSuccess()
> 2014/04/08 11:46:52.567398 _main_ EEE:volts: Protocol aborted
> or unless I try to use StreamDevice's connect command (through the
> EEE:CONNECT PV):
> epics> dbpf EEE:CONNECT 1
> DBR_STRING: "ON"
> epics> 2014/04/07 17:10:06.446437 timerQueue EEE:CONNECT: Connect failed
> 2014/04/07 17:10:06.446482 timerQueue EEE:CONNECT: Protocol aborted
> ?2014/04/07 17:10:07.536724 timerQueue EEE:CONNECT: Connect failed
> ?2014/04/07 17:10:07.536747 timerQueue EEE:CONNECT: Protocol aborted
> but the connection is not re-established anyway. Furthermore, protocol
> reload makes IOC shell stuck.
> There is an older post about different connection issue, but also with
> StreamDevice & Asyn.
> So, with the new version (5.7), I've checked whether the timerQueue
> thread is OK and checked for any locked mutexes.
> The thread is OK.
> There is a mutex reported as locked once the usb-serial device is
> diconnected, however it remains locked when the device is connected back.
> epics> epicsMutexShowAll 1
> ellCount(&mutexList) 112 ellCount(&freeList) 0
> epicsMutexId 0x1d5bfd0 source ../../asyn/asynDriver/asynManager.c line 1868
> No mutexes remain locked after the usb-device re-connection with the
> older version (5.6). But this could be just a result of the issue.
> Tomas
> *Od:*Mark Rivers [[email protected]]
> *Odesláno:* 7. dubna 2014 18:36
> *Komu:* Mazanec Tomáš; [email protected] <mailto:[email protected]>
> drvAsynSerialPort
> Hi Tomas,
> There were no substantive changes in the drvAsynSerialPort code between
> asyn 4.18 and asyn 4.21. SVN tag 1917 is asyn 4.18 and tag 2203 is asyn
> 4.21.
> Here are the differences:
> corvette:asyn/asyn/drvAsynSerial>svn diff -r1917:2203 drvAsynSerialPort*
> Index: drvAsynSerialPort.c
> --- drvAsynSerialPort.c (revision 1917)
> +++ drvAsynSerialPort.c (revision 2203)
> @@ -103,12 +103,12 @@
> if ((ioctl(tty->fd, FIOBAUDRATE, tty->baud) < 0)
> && (ioctl(tty->fd, SIO_BAUD_SET, tty->baud) < 0)) {
> epicsSnprintf(pasynUser->errorMessage,
> pasynUser->errorMessageSize,
> - "SIO_BAUD_SET failed: %s\n",
> strerror(errno));
> + "SIO_BAUD_SET failed: %s",
> strerror(errno));
> return asynError;
> if (ioctl(tty->fd, SIO_HW_OPTS_SET, tty->termios.c_cflag) < 0) {
> - "SIO_HW_OPTS_SET failed: %s\n",
> strerror(errno));
> + "SIO_HW_OPTS_SET failed: %s",
> strerror(errno));
> return asynError;
> #else
> @@ -116,7 +116,7 @@
> tty->termios.c_cflag |= CREAD;
> if (tcsetattr(tty->fd, TCSANOW, &tty->termios) < 0) {
> - "tcsetattr failed: %s\n",
> strerror(errno));
> + "tcsetattr failed: %s",
> strerror(errno));
> return asynError;
> #endif
> @@ -253,12 +253,12 @@
> if(cfsetispeed(&tty->termios,baudCode) < 0 ) {
> epicsSnprintf(pasynUser->errorMessage,pasynUser->errorMessageSize,
> - "cfsetispeed returned %s\n",strerror(errno));
> + "cfsetispeed returned %s",strerror(errno));
> return asynError;
> if(cfsetospeed(&tty->termios,baudCode) < 0 ) {
> - "cfsetospeed returned %s\n",strerror(errno));
> + "cfsetospeed returned %s",strerror(errno));
> return asynError;
> @@ -452,7 +452,7 @@
> tcflush(tty->fd, TCOFLUSH);
> #endif
> #ifdef vxWorks
> - ioctl(tty->fd, FIOCANCEL, NULL);
> + ioctl(tty->fd, FIOCANCEL, 0);
> * Since it is possible, though unlikely, that we got here before the
> * slow system call actually started, we arrange to poke the thread
> @@ -509,14 +509,14 @@
> if ((tty->fd = open(tty->serialDeviceName,
> O_RDWR|O_NOCTTY|O_NONBLOCK, 0)) < 0) {
> - "%s Can't open %s\n",
> + "%s Can't open %s",
> strerror(errno));
> return asynError;
> #if defined(FD_CLOEXEC) && !defined(vxWorks)
> if (fcntl(tty->fd, F_SETFD, FD_CLOEXEC) < 0) {
> - "Can't set %s close-on-exec flag: %s\n",
> + "Can't set %s close-on-exec flag: %s",
> strerror(errno));
> close(tty->fd);
> tty->fd = -1;
> @@ -578,7 +578,7 @@
> asynPrint(pasynUser, ASYN_TRACE_FLOW,
> "%s write.\n", tty->serialDeviceName);
> asynPrintIO(pasynUser, ASYN_TRACEIO_DRIVER, data, numchars,
> - "%s write %d\n", tty->serialDeviceName,
> numchars);
> + "%s write %lu\n", tty->serialDeviceName,
> (unsigned long)numchars);
> if (tty->fd < 0) {
> "%s disconnected:",
> @@ -672,7 +672,7 @@
> if (maxchars <= 0) {
> - "%s maxchars %d Why
> <=0?\n",tty->serialDeviceName,(int)maxchars);
> + "%s maxchars %d Why <=0?",tty->serialDeviceName,(int)maxchars);
> return asynError;
> if (tty->readTimeout != pasynUser->timeout) {
> @@ -775,8 +775,8 @@
> data[nRead] = 0;
> else if (gotEom)
> *gotEom = ASYN_EOM_CNT;
> - asynPrint(pasynUser, ASYN_TRACE_FLOW, "%s read %d, return %d\n",
> - tty->serialDeviceName, *nbytesTransfered,
> status);
> + asynPrint(pasynUser, ASYN_TRACE_FLOW, "%s read %lu, return %d\n",
> + tty->serialDeviceName, (unsigned
> long)*nbytesTransfered, status);
> return status;
> So the changes are removing “\n” from the end of epicsSNprintf formats,
> and some other minor changes to avoid compiler warnings.
> Is this on Linux?
> Have you upgraded the OS?
> I think any change in behavior is likely due either to a change in
> StreamDevice or a change in the OS, and not due to any change in asyn.
> Mark
> *From:*[email protected]
> [mailto:[email protected]] *On Behalf Of *Mazanec Tomáš
> *Sent:* Monday, April 07, 2014 11:13 AM
> *To:* [email protected] <mailto:[email protected]>
> *Subject:* Streamdevice 2.6 autoconnection failure using drvAsynSerialPort
> Hello
> Automatic re-connection seems to be broken with recent streamdevice & asyn.
> Recently, we upgraded SynApps from 5.6 to version 5.7 and so
> streamdevice 2.5.1 & Asyn 4.18 to streamdevice 2.6 & Asyn 4.21.
> One of IOCs here is using serial port ( as /dev/ttyUSBxxx ) and device
> controlled by it disconnects often.
> With SynApps 5.6, everything ran smoothly. After the upgrade to SynApps
> 5.7, the IOC is not able to reconnect anymore.
> As far as I've tested, drvAsynIPPort reconnects well with both SynApps
> 5.6 and 5.7, so its just serial port variant which is affected.
> Could you anyone address this issue and provide some hints or fix.
> Regards,
> Tomas Mazanec
> ELI Beamlines Czech Republic
> http://www.eli-beams.eu
> +420 26605 2566
> +420 601 555 066
> Address:
> Institute of Physics, Academy of Sciences
> Na Slovance 2
> 182 21 Prague
> Czech Republic
> *** DB template file:
> record(ai, "$(NAME):volts")
> field(DTYP, "stream")
> field(INP, "@$(SCONF) get_volts $(ASYNPORT)")
> field(SCAN, "5 second")
> field(PINI, "YES")
> field(VAL, "0")
> field(PREC, "2")
> field(EGU, "V")
> record(bo, "$(NAME):CONNECT") {
> field(OUT, "@$(SCONF) connect $(ASYNPORT)")
> field(PINI, "NO")
> field(HIGH, "0.1")
> field(ZNAM, "OFF")
> field(ONAM, "ON")
> *** streamdev protocol file:
> get_volts {out "\x11\x3f\x76\x04"; in "\x76%f\x04\x00" }
> connect {
> ExtraInput = Ignore;
> connect 1000;
> *** EPICS IOC shell LOG file:
> epicsEnvSet("SYSNAME","EEE")
> # streamdevice protocol file-name
> epicsEnvSet("SYSSCONF","proto.sdp")
> # name of asyndriver port (arbitrary)
> epicsEnvSet("SYSASYNPORT","PORT")
> # For streamdevice
> epicsEnvSet STREAM_PROTOCOL_PATH :protocols:./cfg
> # Setup asyn driver
> drvAsynSerialPortConfigure ("PORT","/dev/ttyUSBPIC", 0, 1, 0)
> asynSetOption ("PORT", 0, "baud", "9600")
> asynSetOption ("PORT", 0, "bits", "8")
> asynSetOption ("PORT", 0, "parity", "none")
> asynSetOption ("PORT", 0, "stop", "1")
> asynReport(1, "PORT")
> PORT multiDevice:No canBlock:Yes autoConnect:No
> enabled:Yes connected:No numberConnects 0
> asynManagerLock:No synchronousLock:No
> exceptionActive:No exceptionUsers 1 exceptionNotifys 0
> Serial line /dev/ttyUSBPIC: Disconnected
> fd: -1
> Characters written: 0
> Characters read: 0
> asynSetTraceIOMask("PORT",0,0x4)
> asynSetTraceMask("PORT",0,0x9)
> dbLoadRecords("aaa.template","NAME=EEE, SCONF=proto.sdp, ASYNPORT=PORT")
> iocInit()
> Starting iocInit
> ## EPICS R3.14.12.4 $Date: Mon 2013-12-16 15:51:45 -0600$
> ## EPICS Base built Mar 11 2014
> iocRun: All initialization complete
> 2014/04/07 17:07:24.528 /dev/ttyUSBPIC write 4
> 11 3f 76 04
> 2014/04/07 17:07:24.542 /dev/ttyUSBPIC read 1
> 76
> 2014/04/07 17:07:24.543 /dev/ttyUSBPIC read 1
> 35
> 2014/04/07 17:07:24.544 /dev/ttyUSBPIC read 1
> 2e
> 2014/04/07 17:07:24.545 /dev/ttyUSBPIC read 1
> 31
> 2014/04/07 17:07:24.547 /dev/ttyUSBPIC read 1
> 39
> 2014/04/07 17:07:24.548 /dev/ttyUSBPIC read 1
> 04
> 2014/04/07 17:07:24.549 /dev/ttyUSBPIC read 1
> 00
> 2014/04/07 17:07:29.026 /dev/ttyUSBPIC write 4
> 11 3f 76 04
> 2014/04/07 17:07:29.039 /dev/ttyUSBPIC read 1
> 76
> 2014/04/07 17:07:29.041 /dev/ttyUSBPIC read 2
> 35 2e
> 2014/04/07 17:07:29.042 /dev/ttyUSBPIC read 1
> 31
> 2014/04/07 17:07:29.043 /dev/ttyUSBPIC read 1
> 39
> 2014/04/07 17:07:29.044 /dev/ttyUSBPIC read 1
> 04
> 2014/04/07 17:07:29.046 /dev/ttyUSBPIC read 1
> 00
> epics>
> epics>
> epics>
> epics> scanppl
> Records with SCAN = '5 second' (0 over-runs):
> EEE:volts
> epics> dbgf EEE:volts
> DBR_DOUBLE: 5.19
> epics>
> epics> dbpr EEE:volts 111
> ACKS: INVALID ACKT: YES ADEL: 0 ALST: 5.19
> AOFF: 0 ASG: ASLO: 1 ASP: (nil)
> BKPT: 00 DESC: DISA: 0 DISP: 0
> DISS: NO_ALARM DISV: 1 DPVT: 0x1911dd0 DSET:
> 0x7fa011b09a40
> DTYP: stream EGU: V EGUF: 0 EGUL: 0
> EOFF: 0 ESLO: 1 EVNT: 0 FLNK:CONSTANT 0
> HHSV: NO_ALARM HIGH: 0 HIHI: 0 HOPR: 0
> HSV: NO_ALARM HYST: 0 INIT: 0
> INP:INST_IO @proto.sdp get_volts PORT LALM: 5.19 LBRK: 0
> LCNT: 11 LINR: NO CONVERSION LLSV: NO_ALARM LOLO: 0
> LOPR: 0 LOW: 0 LSET: 0x1917c90 LSV: NO_ALARM
> MDEL: 0
> MLIS: 30 69 02 b0 9f 7f 00 00 30 69 02 b0 9f 7f 00 00 01 00 00 00
> MLOK: 40 76 90 01 00 00 00 00 MLST: 5.19 NAME: EEE:volts
> NSEV: NO_ALARM NSTA: NO_ALARM ORAW: 0 PACT: 1
> PBRK: (nil) PHAS: 0 PINI: YES PPN: (nil)
> PPNR: (nil) PREC: 2 PRIO: LOW PROC: 0
> PUTF: 0 RDES: 0x1885ff0 ROFF: 0 RPRO: 0
> RSET: 0x7fa0118c7a80 RVAL: 0 SCAN: 5 second
> SDIS:CONSTANT SEVR: INVALID SIML:CONSTANT SIMM: NO
> SIMS: NO_ALARM SIOL:CONSTANT SMOO: 0 SPVT: 0x1913f00
> STAT: SCAN SVAL: 0 TIME: 2014-04-07 17:07:34.247219579
> TPRO: 0 TSE: 0 TSEL:CONSTANT UDF: 0
> VAL: 5.19
> epics>
> epics> dbgf EEE:volts.SEVR
> DBR_STRING: "INVALID"
> epics>
> DBR_STRING: "ON"
> epics> ?[31;1m2014/04/07 17:10:06.446437 timerQueue EEE:CONNECT: Connect
> failed
> ?[0m?[31;1m2014/04/07 17:10:06.446482 timerQueue EEE:CONNECT: Protocol
> aborted
> ?[0m?[31;1m2014/04/07 17:10:07.536724 timerQueue EEE:CONNECT: Connect
> failed
> ?[0m?[31;1m2014/04/07 17:10:07.536747 timerQueue EEE:CONNECT: Protocol
> aborted
> ?[0m
> epics>
> epics> var streamDebug 1
> 2014/04/07 17:10:35.596373 _main_ StreamEpics.cc:711:
> Stream::process(EEE:CONNECT) start
> 2014/04/07 17:10:35.596411 _main_ StreamCore.cc:410:
> StreamCore::startProtocol(EEE:CONNECT, startMode=StartNormal)
> 2014/04/07 17:10:35.596426 _main_ StreamCore.cc:552:
> StreamCore::evalCommand(EEE:CONNECT): activeCommand = connect
> 2014/04/07 17:10:35.596436 _main_ AsynDriverInterface.cc:1347:
> AsynDriverInterface::connectRequest EEE:CONNECT
> 2014/04/07 17:10:35.596446 _main_ StreamEpics.cc:723:
> Stream::process(EEE:CONNECT): protocol started
> DBR_STRING: "ON"
> epics> 2014/04/07 17:10:36.591508 timerQueue
> AsynDriverInterface.cc:1473:
> AsynDriverInterface::handleTimeout(EEE:CONNECT)
> ?[31;1m2014/04/07 17:10:36.591531 timerQueue EEE:CONNECT: Connect failed
> ?[0m2014/04/07 17:10:36.591539 timerQueue StreamCore.cc:517:
> StreamCore::finishProtocol(EEE:CONNECT, status=Fault) not bus owner
> 2014/04/07 17:10:36.591545 timerQueue AsynDriverInterface.cc:1416:
> AsynDriverInterface::finish(EEE:CONNECT) start
> 2014/04/07 17:10:36.591551 timerQueue AsynDriverInterface.cc:1426:
> AsynDriverInterface::finish(EEE:CONNECT) done
> ?[31;1m2014/04/07 17:10:36.591557 timerQueue EEE:CONNECT: Protocol aborted
> ?[0m2014/04/07 17:10:36.591589 cbLow StreamEpics.cc:896:
> streamRecordProcessCallback(EEE:CONNECT) processing record
> 2014/04/07 17:10:36.591622 cbLow StreamEpics.cc:691:
> Stream::process(EEE:CONNECT) error status=UDF (17)
> 2014/04/07 17:10:36.591646 cbLow StreamEpics.cc:901:
> streamRecordProcessCallback(EEE:CONNECT) processing record done
> 2014/04/07 17:10:36.686741 cbLow StreamEpics.cc:711:
> 2014/04/07 17:10:36.686766 cbLow StreamCore.cc:410:
> 2014/04/07 17:10:36.686779 cbLow StreamCore.cc:552:
> 2014/04/07 17:10:36.686785 cbLow AsynDriverInterface.cc:1347:
> 2014/04/07 17:10:36.686796 cbLow StreamEpics.cc:723:
> 2014/04/07 17:10:37.681881 timerQueue AsynDriverInterface.cc:1473:
> ?[31;1m2014/04/07 17:10:37.681901 timerQueue EEE:CONNECT: Connect failed
> ?[0m2014/04/07 17:10:37.681909 timerQueue StreamCore.cc:517:
> 2014/04/07 17:10:37.681916 timerQueue AsynDriverInterface.cc:1416:
> 2014/04/07 17:10:37.681922 timerQueue AsynDriverInterface.cc:1426:
> ?[31;1m2014/04/07 17:10:37.681927 timerQueue EEE:CONNECT: Protocol aborted
> ?[0m2014/04/07 17:10:37.681958 cbLow StreamEpics.cc:896:
> 2014/04/07 17:10:37.681981 cbLow StreamEpics.cc:691:
> 2014/04/07 17:10:37.681994 cbLow StreamEpics.cc:901:
> epics>
> epics>
> epics>
- Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Mazanec Tomáš
- RE: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Mark Rivers
- RE: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Mazanec Tomáš
- Re: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Dirk Zimoch