1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  <2014>  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  <2014>  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: EPICS alarming on VAL != X
To: <[email protected]>
Date: Mon, 21 Jul 2014 12:41:41 +0200
On Saturday 19 July 2014 10:45:39 Jameson Graef Rollins wrote:
> On Fri, Jul 18 2014, "Johnson, Andrew N." <[email protected]> wrote:
> > This seems to be a rather unusual case. It's easy to implement this
> > behavior using a calc record to do the equality comparison, but
> > equality is actually a fairly rare comparison to use for floating
> > point values (other than zero). If X is really an integer you could
> > use longin or longout records instead, you just have to set the LOW
> > and HIGH alarm levels to one either side of X and HYST to zero. If X
> > is not an integer and is read from an ADC say, you could calculate
> > the ADC values in engineering units adjacent to X and use them for
> > the LOW and HIGH fields of your ai/ao record. If X really is a
> > double value you could even calculate the next higher and lower
> > double values and use them, but you need an understanding of IEEE
> > floating point to do that properly.
> Hi, Andrew.  Thanks so much for the response.
> I imagine we are doing some a bit non-standard.  We use ai records for
> system parameters that need to take on non-integer values, such as
> digital gains.  As you suggest, we could calculate the next
> higher/lower double values and set the alarms to those, but that
> requires more intermediate work when setting the alarms.
> It seems, though, that this case could be easily covered if either the
> HIGH or LOW alarm were changed to strictly greater/less than the
> alarm value.  Can you think of some reason this behavior would not be
> desired?
Why don't you just set DRVL=DRVH=<the desired value>. In that case the
record simply can't take on any other value. No need to even think about
alarms for situations that can never arise...
Cheers
Ben
"Make it so they have to reboot after every typo." ― Scott Adams
Attachment: signature.asc
Description: This is a digitally signed message part.
Re: EPICS alarming on VAL != X Jameson Graef Rollins
Re: EPICS alarming on VAL != X Dirk Zimoch
Re: EPICS alarming on VAL != X Johnson, Andrew N.
Prev: Re: EPICS on VxWorks6.9 Dirk Zimoch
Next: RE: EPICS on VxWorks6.9 Mark Rivers
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  <2014>  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: Re: EPICS alarming on VAL != X Jameson Graef Rollins
Next: Re: EPICS alarming on VAL != X Jameson Graef Rollins
ANJ, 17 Dec 2015 · Home · News · About · Talk · Base · Modules · Extensions ·