1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  <20142015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  <20142015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: Serial device server timeouts, overwhelmed by load?
To: "'[email protected]'" <[email protected]>, "[email protected]" <[email protected]>
Date: Fri, 31 Oct 2014 00:05:02 +0000
Have you tried replacing the Moxa with a different unit or different model?  I seem to recall past tech-talk messages that mentioned bad Moxa firmware?
We have Moxa boxes with similar or higher loads than yours with no problems.
-----Original Message-----
From: [email protected] [mailto:[email protected]] On Behalf Of [email protected]
Sent: Thursday, October 30, 2014 6:51 PM
To: [email protected]
Subject: Serial device server timeouts, overwhelmed by load?
We observe frequent StreamDevice ReplyTimeouts when communicating
through a Moxa serial device server.  Details follow.  We ask
whether this is expected (or can be mitigated) given our conditions.
We wonder whether we should use some other communication method
(USB to serial adaptors, for example).
Jon Jacky
We have a soft IOC that controls three RS232 serial devices, via
StreamDevice on Asyn communicating over Ethernet to TCP/IP ports on a
Moxa 5610 serial device server.  The devices use a variety of commands but
usually they are just polled about once a second: the IOC sends
a command and the device sends some data back.  Usually each device
responds to a command in a fraction of a second, but frequently
(several times an hour, or more) we observe incidents where no
response arrives before our 5 sec StreamDevice ReplyTimeout is
exceeded.
We monitored RS232 traffic between the Moxa and each serial device and
found each device never fails to respond promptly to a command.  But
each time StreamDevice reports a ReplyTimeout, the command fails to
appear on the Moxa serial port after the IOC sends the command to the
corresponding Moxa TCP/IP port.  We used Wireshark to monitor TCP/IP
traffic between the IOC and the Moxa.  We found that during these
timeout incidents, the IOC sends several TCP Retransmission packets
and TCP Dup ACK packets to the Moxa port, the Moxa port also sends
some TCP Retransmission packets to the IOC.  So it appears there is a
problem in the network or in the Moxa.  We have not noticed any other
unusual network activity or problems during the timeouts, so we
suspect the Moxa.
We see timeouts on all three serial devices, but one device accounts
for most of the traffic (due to a higher data rate and more data).  We
removed the high-traffic device from the Moxa and instead connected it
to a USB port on the same IOC, through a USB to R232 converter.  In this
configuration, we no longer observe timeouts on any of the three
devices, so it appears the traffic from that one device was
interfering with communications for other two also.
The high-volume device communicates at 9600 baud.  In each 1-sec polling
cycle, the IOC sends about 80 characters and the device responds with
about 300 characters.  The two other devices use 1200 baud, commands are
about 10 characters and responses are about 75 characters.
Is it expected that this amount of traffic should
overwhelm the Moxa?  Is there some other likely explanation for the
timeouts?
PS - This is not the same problem as I reported in "Asyn disconnects,
reconnects to serial device server", in
http://www.aps.anl.gov/epics/tech-talk/2014/msg01460.php, but it does
involve the same devices and the same Moxa.  We only saw that a few
times and we haven't seen any repeats, the present problem is frequent and
ongoing.
RE: Serial device server timeouts, overwhelmed by load? jon
Prev: Serial device server timeouts, overwhelmed by load? jon
Next: read waveform data using ca_create_subscription 吴煊
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  <20142015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Next: RE: Serial device server timeouts, overwhelmed by load? jon
ANJ, 17 Dec 2015 · Home · News · About · Talk · Base · Modules · Extensions ·
