1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <20152016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <20152016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: scalcout fails to write to bo
To: Isabella Rey <[email protected]>, "[email protected]" <[email protected]>
Date: Fri, 15 May 2015 17:08:39 +0000
Hi Isabella,
There are three ways to get the behavior you want in this situation:
1. Have the calc _expression_ produce a string value that is one of the bo record's ZNAM or ONAM strings:
record(scalcout, "BS:CAMS_OK") {
  field(SCAN, ".1 second")
  field(CALC, "AA==CC ? 'ON' : 'OFF' ")         <---<<
  field(INAA, "CAM1:TRAFFIC_LIGHT")
  field(OUT, "BS:AUTO PP")
  field(OOPT, "When Zero")
  field(CC, "OK")
2. Have the calc _expression_ explicitly produce a string value that is '0' or '1':
  field(CALC, "AA==CC ? '1' : '0' ")             <---<<
  field(CC, "OK")
3. Make the scalcout record's conversion from number to string produce zero decimal digits:
  field(PREC, "0")                                  <---<<
  field(CALC, "AA==CC")
  field(CC, "OK")
Tim Mooney ([email protected]) (630)252-5417
Software Services Group (www.aps.anl.gov)
Advanced Photon Source, Argonne National Lab
From: [email protected] [[email protected]] on behalf of Isabella Rey [[email protected]]
Sent: Friday, May 15, 2015 11:21 AM
To: [email protected]
Subject: scalcout fails to write to bo
Hi All,
I have a scalcout record whose output should go into a bo record, as follows:
  field(CC, "OK")
record(bo, "BS:AUTO") {
  field(PINI, "YES")
  field(VAL, "0")
  field(ZNAM, "OFF")
  field(ONAM, "ON")
When I run the IOC, I get this error message:
Illegal choice PV: BS:AUTO 0.00000000
After looking at other posts, I think the scalcout is trying to write a string in the bo, which generates the error. But my understanding of the scalcout documentation is that the conversion to int should be done automatically, and this should just work.
Interestingly, this workaround does the job:
  field(CC, "OK")
record(calcout, "BS:CAMS_OK_FAN") {
  field(INPA, "BS:CAMS_OK PP")
  field(PINI, "YES")
  field(VAL, "0")
  field(ZNAM, "OFF")
  field(ONAM, "ON")
So it looks like if a record "pulls" the result from scalcout it's OK, but scalcout doesn't "push" it correctly.
I could live with the workaround, but it's a bit of a hack...
Any thoughts on why this is not working?
Cheers,
Isabella
scalcout fails to write to bo Isabella Rey