1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: Question about the connection refused
To: lzfneu <[email protected]>, "[email protected]" <[email protected]>
Date: Tue, 29 Mar 2016 10:51:48 +0000
Hi Zhefu,
I am sending this message again without the embedded images so it is much smaller.  In the future please use cut-and-paste from your IOC output, not screen shots.
It looks to me like your device is accepting the socket connection on port 502, but then it is not responding to the messages that the IOC is sending.  The driver is waiting 2 seconds and not getting any reply from your device.  This is probably for 1 or more of the following 3 reasons:
1) You are not using the correct protocol.  You are using Modbus TCP.  Have you studied the manual for your device carefully and verified that it uses Modbus TCP, and not Modbus RTU?
2) You are not using the correct Modbus function codes.  Are you sure that your device supports functions codes 3 and 16?
3) You are not using the correct Modbus addresses.  Are you sure that your device supports reading 95 words at address 0 and writing 8 words at address 48?
Sent: Tuesday, March 29, 2016 1:40 AM
To: Mark Rivers; [email protected]
Hi Mark,
Thanks for your respond.
Sorry, I lost to modified the error and re-sent this email, in layer type TCP/IP no delay is needed,
so the command changed as follows:
> modbusInterposeConfig("UCOS123",0,0,0)
The modified input files are as follows:
#!../../bin/linux-x86_64/modbusApp
< envPaths
dbLoadDatabase("../../dbd/modbus.dbd")
modbus_registerRecordDeviceDriver(pdbbase)
# Use the following commands for TCP/IP
#read   Device ID 2
drvAsynIPPortConfigure("UCOS123","192.168.1.125:502",0,0,1)
asynSetTraceIOMask("UCOS123",0,4)
asynSetTraceMask("UCOS123",0,9)
# Read 100 words (1600 bits).  Function code=3.
drvModbusAsynConfigure("read123", "UCOS123", 0, 3, 0, 95, 0, 100,"M22A")
# Write 8 words (128 bits).  Function code=16
drvModbusAsynConfigure("write123", "UCOS123", 0, 16, 48, 8, 0, 1,"M22A")
iocInit
and the the error messages are shown below:
Question about the softioc connection refused ? lzfneu
RE: Question about the softioc connection refused ? Mark Rivers
RE: Question about the connection refused lzfneu
RE: Question about the connection refused Mark Rivers
Prev: RE: About Pilatus IOC Error Messgae.. Mark Rivers
Next: Re: FFT and waveform Jan Marjanovic
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: RE: Question about the connection refused lzfneu
Next: caget pv with a space 梁雅翔
ANJ, 15 Jul 2016 · Home · News · About · Talk · Base · Modules · Extensions ·