1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: Motor Module, Deferred Movement, .VAL field set to .RBV after motion
To: Torsten Bögershausen <[email protected]>, Mark Rivers <[email protected]>
Date: Thu, 30 Jun 2016 08:41:45 -0700
@Torsten
It is a servo motor with an internal encoder that has 4,000 count per revolution resolution The problem is this not the standard behavior if the motor doesn't reach the setpoint, the setpoint should not change, or at least this is how I understand it. I think this would be confusing for a user driving the motors.
The MRES field is set to 0.0001. But this is arbitrary for now since setpoint values are converted to counts.
 dbpr SMOTOR:AXIS:1 10
ACCL: 0.2           ACKS: NO_ALARM      ACKT: YES           ADEL: 0
ALST: 0             ASG: MC_MAINT       ASP: (nil)          ATHM: 0
BACC: 0.5           BDST: 0             BKPT: 00            BVEL: 0.1
CARD: 0             CBAK: 0x85dd6f8     CDIR: 0             CNEN: Disable
DCOF: 0             DESC:               DHLM: 0             DIFF: 0.4905
DINP:CONSTANT       DIR: Neg            DISA: 0             DISP: 0
DISS: NO_ALARM      DISV: 1             DLLM: 0             DLY: 0
DMOV: 1             DOL:CONSTANT        DPVT: 0x85e3db8     DRBV: 4.0e-04
DSET: 0x98b960      DTYP: asynMotor     DVAL: 0.4909        EGU: mm
ERES: 1.0e-04       EVNT: 0             FLNK:CONSTANT 0     FOF: 0
FOFF: Frozen        FRAC: 1             HHSV: NO_ALARM      HIGH: 0
HIHI: 0             HLM: 0              HLS: 0              HLSV: NO_ALARM
HOMF: 0             HOMR: 0             HOPR: 0             HSV: NO_ALARM
HVEL: 0.1           ICOF: 0             INIT:               JAR: 2.5
JOGF: 0             JOGR: 0             JVEL: 0.5           LCNT: 0
LDVL: 0.4909        LLM: 0              LLS: 0              LLSV: NO_ALARM
LOCK: NO            LOLO: 0             LOPR: 0             LOW: 0
LRLV: 0             LRVL: 4909          LSET: 0x85e5750     LSPG: Go
LSV: NO_ALARM       LVAL: -0.4909       LVIO: 0             MDEL: 0
MIP: 0              MISS: 0
MLIS: b0 b0 61 08 d8 a1 61 08 49 00 00 00 MLOK: d8 b9 5d 08
MLST: 0             MMAP: 0             MOVN: 0             MRES: 1.0e-04
MSTA: 2306          NAME: SMOTOR:AXIS:1 NMAP: 0             NSEV: NO_ALARM
NSTA: NO_ALARM      NTM: YES            NTMF: 2             OFF: 0
OMSL: supervisory   OUT:INST_IO @asyn(SM1,1)                PACT: 0
PCOF: 0             PHAS: 0             PINI: NO POST:
PP: 0               PPN: (nil)          PPNR: (nil)         PREC: 4
PREM:               PRIO: HIGH          PROC: 0             PUTF: 0
RBV: -4.0e-04       RCNT: 0             RDBD: 1.0e-04 RDBL:CONSTANT
RDES: 0x85a6310     RDIF: 4905          REP: 4              RHLS: 0
RINP:CONSTANT       RLLS: 0             RLNK:CONSTANT       RLV: 0
RMOD: Default       RMP: 4              RPRO: 0             RRBV: 4
RRES: 0             RSET: 0x98b880      RTRY: 0             RVAL: 4909
RVEL: 0             S: 25               SBAK: 5             SBAS: 5
SCAN: Passive       SDIS:CONSTANT       SET: Use            SEVR: NO_ALARM
SMAX: 183.5         SPMG: Go            SPVT: (nil)         SREV: 200
SSET: 0             STAT: NO_ALARM      STOO:CONSTANT       STOP: 0
STUP: OFF           SUSE: 0             SYNC: 0             TDIR: 0
TIME: 2016-06-30 08:23:12.109352047     TPRO: 0             TSE: 0
TSEL:CONSTANT       TWF: 0              TWR: 0              TWV: 0.1
UDF: 0              UEIP: No            UREV: 0.02          URIP: No
VAL: -0.4909        VBAS: 0.1           VELO: 0.5           VERS: 6.9
VMAX: 3.67          VOF: 0
The motorStatusDone_ field is updated by
sprintf(pC_->outString_, REPORTSTATUS0, canAddr_); // Report 16-bit status word
  status = pC_->writeReadController();
  if (status) goto skip;
  currentStatus_ = atoi(pC_->inString_);
  setIntegerParam(pC_->smartStatus_,currentStatus_);
done = (currentStatus_ & MOVING)?0:1; // Trajectory in progress, MOVING is a bit mask
  *moving = done ? false:true;
  setIntegerParam(pC_->motorStatusDone_, done);
If I create a public repo I will post on the thread
On 6/30/2016 8:28 AM, Torsten Bögershausen wrote:
Hej again,
I can’t reproduce it here.
What does
dbpr SMOTOR:AXIS:1
give ?
And another question:
What does your driver put into
setIntegerParam(pC_->motorStatusMoving_
and what into
Can you send us a copy of the driver code, or is it somewhere on a public repo ?
Am 30.06.2016 um 13:54 schrieb Mark Rivers <[email protected]>:
Hi Jacob,
You did not answer this question:
Does the controller ever report that the position is equal to the requested position, or is it always off by that small amount, i.e. even after a move is complete and the controller is reporting its position at the slow poll rate?
Some more questions:
- Is this a motor that accepts and reports its positions in steps, or does it use engineering units?  If it uses steps then if you tell the motor to go to a step position does it always report that it reached that exact position?  If not then I think there is a bug in the controller.   If the controller is programmed in engineering units, then it is the responsibility of your driver to convert motor record positions (in steps) to engineering units for move commands, and to convert engineering units to steps for readback commands.  It is also your driver's responsibility to ensure that the motor record step positions are actually positions that are reachable by the controller, i.e. that they are integer numbers of controller steps.
What controller is this?
Sent: Wednesday, June 29, 2016 7:13 PM
To: Mark Rivers; 'Ron Sluiter'
Cc: [email protected]
Okay so in the original poll function the readback is set before the
status. So I changed the order. Unfortunately this did not produce
better results. I then placed in a delay before  the  readback when the
DMOV goes from 0 to 1. The behavior persists.
SMOTOR:AXIS:1                      2016-06-29 17:04:30.658694 30
SMOTOR:AXIS:1.DMOV          2016-06-29 17:04:30.658894 1
SMOTOR:AXIS:1.RBV              2016-06-29 17:04:31.135564 25.0821
SMOTOR:AXIS:1.DMOV          2016-06-29 17:04:31.135564 0
SMOTOR:AXIS:1.RBV              2016-06-29 17:04:33.578796 26.3076
SMOTOR:AXIS:1.RBV              2016-06-29 17:04:36.021029 27.529
SMOTOR:AXIS:1.RBV              2016-06-29 17:04:38.463166 28.7494
SMOTOR:AXIS:1.RBV              2016-06-29 17:04:40.903696 29.9656
SMOTOR:AXIS:1                      2016-06-29 17:04:43.142160 29.9656
SMOTOR:AXIS:1.DMOV          2016-06-29 17:04:43.142160 1
SMOTOR:AXIS:1.RBV              2016-06-29 17:04:45.823197 29.9996
You can see that the last readback updates a few seconds after the DMOV
goes high, but the setpoint still is changed to the readback. This
happened under single motion with 0 retries.
The delay works as follows, prevDone is a field of  the axis class, done
is a local variable
  if(done && !prevDone_ ){
     prevDone_ = done;
     goto skip;
   prevDone_ = done;
   pollPosition();
  skip:
  callParamCallbacks()
Jacob
On 6/29/2016 2:21 PM, Mark Rivers wrote:
So this problem really has nothing to do with deferred moves.  The same undesired behavior is seen when using a normal move if retries is 0.
Does the controller ever report that the position is equal to the requested position, or is it always off by that small amount, i.e. after a move is complete and the motor is reporting its position at the slow poll rate?
In your poller are you reading the position before or after you read the done moving status?  If you are reading it before then perhaps that is the problem?  What if you read the position after the done moving status?  Perhaps even add a small delay when you detect that a move has just completed before reading the position.  I have done that in some of my drivers in the past.
-----Original Message-----
Sent: Wednesday, June 29, 2016 3:15 PM
@Ron
Version 6.9
@Mark
This is not necessarily the case for example, this is a single move with
a non-zero number of retries
SMOTOR:AXIS:1.DMOV         2016-06-29 13:10:48.487763 1
SMOTOR:AXIS:1.VAL              2016-06-29 13:10:48.487763 19.9926
SMOTOR:AXIS:1.RBV              2016-06-29 13:10:48.487763 19.9936
SMOTOR:AXIS:1.DMOV         2016-06-29 13:10:48.487763 0
SMOTOR:AXIS:1.VAL              2016-06-29 13:10:55.927566 25
SMOTOR:AXIS:1.RBV              2016-06-29 13:10:57.765592 20.0858
SMOTOR:AXIS:1.RBV              2016-06-29 13:10:59.962699 21.1839
SMOTOR:AXIS:1.RBV              2016-06-29 13:11:02.159951 22.283
SMOTOR:AXIS:1.RBV              2016-06-29 13:11:04.357444 23.382
SMOTOR:AXIS:1.RBV              2016-06-29 13:11:06.555026 24.4807
SMOTOR:AXIS:1.RBV              2016-06-29 13:11:08.753050 24.9996
SMOTOR:AXIS:1.RBV              2016-06-29 13:11:13.147318 24.9993
SMOTOR:AXIS:1.DMOV          2016-06-29 13:11:23.890093 1
/*no setpoint change*/
But a single move with a zero number of retries
SMOTOR:AXIS:1.DMOV           2016-06-29 13:11:24.378107 1
SMOTOR:AXIS:1.VAL               2016-06-29 13:11:24.378107 25
SMOTOR:AXIS:1.RBV              2016-06-29 13:11:24.378107 24.9993
SMOTOR:AXIS:1.DMOV          2016-06-29 13:11:24.378107 0
SMOTOR:AXIS:1.VAL               2016-06-29 13:12:26.321196 30
SMOTOR:AXIS:1.DMOV          2016-06-29 13:12:26.321564 1
SMOTOR:AXIS:1.RBV              2016-06-29 13:12:26.795562 25.0862
SMOTOR:AXIS:1.DMOV          2016-06-29 13:12:26.795562 0
SMOTOR:AXIS:1.RBV              2016-06-29 13:12:28.992570 26.1841
SMOTOR:AXIS:1.RBV              2016-06-29 13:12:31.190003 27.2832
SMOTOR:AXIS:1.RBV              2016-06-29 13:12:33.387377 28.3824
SMOTOR:AXIS:1.RBV              2016-06-29 13:12:35.584989 29.4812
SMOTOR:AXIS:1.RBV              2016-06-29 13:12:37.782270 29.9996
SMOTOR:AXIS:1.VAL              2016-06-29 13:12:37.782270 29.9996 <-
setpoint change
SMOTOR:AXIS:1.DMOV         2016-06-29 13:12:37.782270 1
Unfortunately setting a non-zero retry does not help when it comes to
deferred motion. I should mention at this point I have been using a work
around which stops this behavior. If the OMSL field is set to
closed_loop this behavior does not show. This field is unrelated to
motion,but it will avoid the branch of logic that is executed in the
motor record.
I am not using an encoder the controller reports back step counts, those
are then translated via MRES (UEIP = No). I think the controller is
moving to the correct position and the setpoint is within the resolution
of the motor.  Ultimately the EPICs side should trust the controller
with is special synchronized motion algorithm.
On 6/29/2016 12:39 PM, Mark Rivers wrote:
I think the motor record does always sets the VAL field to match the RBV field when motion completes.  This is true regardless of whether you are using deferred moves or not.
What happens if you do the same camonitor on a normal move of this axis, not a deferred move?
Why your controller is saying that the position is 3.993 and that the move is complete, when it was told to go to 4.000?  Does this motor have an encoder?  Are you using the encoder for readback, i.e. what is the value of the UEIP field?
From: [email protected] [mailto:[email protected]] On Behalf Of Ron Sluiter
Sent: Wednesday, June 29, 2016 2:23 PM
To: Jacob DeFilippis
Hello Jacob,
What version (VERS field) of the motor record are you using?
The folks at Diamond are the experts in the use of the motor record
deferred move function. I defer to them on this topic.
Ron
On 6/29/2016 1:32 PM, Jacob DeFilippis wrote:
Hello,
      I am working on implementing a multiple axis synchronized motion
using the motor module's asynController base class (model 3). The move
function is set up such that  it stores the .VAL to variables inside
the physical controller when the deferredMove flag is 1, and when
there is a transition from 1-> 0 on the flag I issue the controller
command that moves the motors synchronously to the commanded target.
      My problem is when the move completes the .VAL field is set to the
.RBV field.  This happens when the .DMOV is returned to 1. I tracked
down the cause, which is found in motorRecord.cc in function
postProcess(motorRecord * pmr) line 762 (In the github repo). It
executes "pmr->val = pmr->rbv" . I am unsure why this postprocess is
occurring.  Is there anything extra I should implement in my function
that issues synchronized motion?  or possibly something extra in the
polling function. Is this because the RTRY field is set to 0?
An example of the bad behavior:
SMOTOR:AXIS:1.VAL                 2016-06-29 11:05:24.259733 4
SMOTOR:AXIS:1.DMOV            2016-06-29 11:05:24.474977 1
SMOTOR:AXIS:1.RBV                2016-06-29 11:05:27.892752 3.0181
SMOTOR:AXIS:1.DMOV            2016-06-29 11:05:27.892752 0
SMOTOR:AXIS:1.RBV                2016-06-29 11:05:30.090092 3.4665
SMOTOR:AXIS:1.RBV                2016-06-29 11:05:32.287451 3.9155
SMOTOR:AXIS:1.RBV                2016-06-29 11:05:34.484984 3.9993
SMOTOR:AXIS:1.VAL                 2016-06-29 11:05:34.484984 3.9993
<--My problem
SMOTOR:AXIS:1.DMOV            2016-06-29 11:05:34.484984 1
My motor record
record(motor, "$(P):$(M):$(ADDR)") {
    field(SCAN, "Passive")
    field(DTYP, "asynMotor")
    field(DISS, "NO_ALARM")
    field(DIR, "$(DIR)")
    field(VELO, "$(VELO)")
    field(VBAS, "$(VBAS)")
    field(VMAX, "$(VMAX)")
    field(URIP, "No")
    field(PREC, "4")
    field(EGU, "mm")
    field(MRES, "$(MRES)")
    field(OUT, "@asyn($(PORT),$(ADDR))")
    field(TWV, ".1")
    field(ASG, "MC_MAINT")
    field(FOFF, "Frozen")
    field(PRIO, "HIGH")
    field(OMSL, "closed_loop")
    field(RTRY, "0")
My function that triggers synchronized motion
asynStatus Axis::processDeferredMoves()
    asynStatus status;
    /*resets controller flag*/
     status = resetFlags();
     if(status) goto skip;
    /*sends command to start synchronized motion*/
     sprintf(pC_->outString_,GOSYNC);
     status = pC_->writeController();
     skip:
     setIntegerParam(pC_->motorStatusDone_, 0);
     setIntegerParam(pC_->motorStatusCommsError_, status ? 1:0);
     callParamCallbacks();
     pC_->wakeupPoller();
     return asynSuccess;
Thanks in advance,
Jacob
Re: Motor Module, Deferred Movement, .VAL field set to .RBV after motion Pearson, Matthew R.
Re: Motor Module, Deferred Movement, .VAL field set to .RBV after motion Torsten Bögershausen
Motor Module, Deferred Movement, .VAL field set to .RBV after motion Jacob DeFilippis
Re: Motor Module, Deferred Movement, .VAL field set to .RBV after motion Ron Sluiter
RE: Motor Module, Deferred Movement, .VAL field set to .RBV after motion Mark Rivers
Re: Motor Module, Deferred Movement, .VAL field set to .RBV after motion Jacob DeFilippis
Prev: Re: Motor Module, Deferred Movement, .VAL field set to .RBV after motion Torsten Bögershausen
Next: Re: Motor Module, Deferred Movement, .VAL field set to .RBV after motion Jacob DeFilippis
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Next: Re: Motor Module, Deferred Movement, .VAL field set to .RBV after motion Pearson, Matthew R.
ANJ, 15 Jul 2016 · Home · News · About · Talk · Base · Modules · Extensions ·
