Hi Florian,
here at DESY we have a couple of S7-300 and S7-1200/S7-1500 PLCs. All of
these
are connected to EPICS via the s7plc Support from PSI. More info you can
find at
http://epics.web.psi.ch/software/s7plc/
This works great for us, but you need to have a communications processor
connected
to your plc. For the S7-1200 this is built in. For the S7-300 you need, for
example, the
CP 343-1 respective the CP 1543-1 for the S7-1500.
In my opinion the s7plc is the more secure way, because you send a dedicated
number of variables to your plc. The s7nodave writes directly to the memory
of the
plc. If I am wrong here please correct this, but I don’t like the idea that
someone
writes into the memory of my plc ;-)
Greetings, Joachim
>-----Original Message-----
>From: [email protected] [mailto:tech-talk-
>[email protected]] On Behalf Of Florian Feldbauer
>Sent: Tuesday, May 23, 2017 11:17 AM
>To: EPICS Tech Talk
>Subject: Siemens S7-300 PLC and EPICS
>Hey all,
>for the vacuum system of our tracking detector we want to use a PLC. We
>decided to use a Siemens S7-300 which should control the pumps, gauges
>and valves of our system.
>The main question now is how to connect the PLC to our EPICS system?
>I've seen that the CPU module has PROFINET or PROFIBUS DP interfaces. Is
>there a device support available for those? Is there a better/easier
>interface available maybe via an additional communication processor?
>Any feedback appreciated!
>Best regards,
>Florian
>| Dr. Florian Feldbauer |
>| Ruhr-Universität Bochum |
>| Experimentalphysik I AG |
>| Universitätsstr 150 |
>| D-44801 Bochum |
>| Office: NB 2/134 |
>| Phone: (+49)234 / 32-23563 |
- Siemens S7-300 PLC and EPICS Florian Feldbauer