1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
Subject: Re: Modbus for Huber Pilotone
From: Florian Feldbauer via Tech-talk <[email protected]>
Date: Fri, 20 May 2022 17:19:39 +0200
Hey Mark,
I have now changed the driver to
drvModbusAsynConfigure( "chillerReadReg",  "chiller", 0xff, 3, 0, 116, "INT16", 1000, "Huber PilotOne" )
and set all input records to I/O Intr.
I still get the "Resource temporarily unavailable" error from time to time:
2022/05/20 17:06:59.344 drvModbusAsyn::doModbusIO port chillerReadReg error calling writeRead, error=PilotONE-187144:502 TCP timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
2022/05/20 17:07:00.443 drvModbusAsyn::doModbusIO port chillerReadReg writeRead status back to normal having had 1 errors, nwrite=6/6, nread=232
2022/05/20 17:09:53.845 drvModbusAsyn::doModbusIO port chillerReadReg error calling writeRead, error=PilotONE-187144:502 TCP timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
2022/05/20 17:09:54.943 drvModbusAsyn::doModbusIO port chillerReadReg writeRead status back to normal having had 1 errors, nwrite=6/6, nread=232
2022/05/20 17:10:14.846 drvModbusAsyn::doModbusIO port chillerReadReg error calling writeRead, error=PilotONE-187144:502 TCP timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
2022/05/20 17:10:15.943 drvModbusAsyn::doModbusIO port chillerReadReg writeRead status back to normal having had 1 errors, nwrite=6/6, nread=232
2022/05/20 17:10:18.345 drvModbusAsyn::doModbusIO port chillerReadReg error calling writeRead, error=PilotONE-187144:502 TCP timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
2022/05/20 17:10:19.444 drvModbusAsyn::doModbusIO port chillerReadReg writeRead status back to normal having had 1 errors, nwrite=6/6, nread=232
I experimented with the poll interval (using smaller and larger values) but it doesn't change. Every now and then I get those errors in between, but it is much less frequent then before using absolute addressing.
I searched the manual again, if it says anything about polling times, but it just says:
"Once the master has received the response from the thermostat, the next command can be transmitted immediately."
But in general it seems to be working now.
Cheers,
Florian
On 5/20/22 14:30, Mark Rivers wrote:
Hi Florian,
This is recent tech-talk thread with a Eurotherm device that also needed ASLO like your device:
https://epics.anl.gov/tech-talk/2022/msg00476.php
It looks like your output record is now working.  What about your input record, is that working?
Regarding absolute vs relative addressing, relative addressing is well suited to devices that contain several blocks of register address that each contain a number of registers to be written or read.  Each block is typically fewer than 125 16-bit words or 2000 single bits.  In that case the entire block can be read in a single Modbus operation.  The Modbus driver can poll the entire block and only do callbacks on the registers or bits that have changed.  For a PLC with many input status bits that is much more efficient than absolute addressing which requires a periodically scanned record for each bit which just reads the value of a single bit as a separate Modbus transaction.  The polling can also be done faster than the typical 10 Hz fastest scan rate, and by using SCAN=I/O Intr you can much lower latency in detecting that a bit or register value has changed state.
Absolute addressing is normally used when there are a large number of isolated Modbus addresses scattered around the 16-bit address space.  Then it may be more efficient in memory and CPU to not create a separate polling asynDriver for each of these.
Sent: Friday, May 20, 2022 3:16 AM
Cc: [email protected]
Hey Mark,
thanks for your reply.
I'm using tag R3-2 from github. I'm new to modbus, and wasn't aware that it makes a difference if I use absolute or relative addressing.
In my first try relative did not work, I guess I did something wrong with calculating the offsets correctly. I will give it another try.
As for the ao record: those who can read are at a clear advantage
From the record reference manual
Conversion proceeds as follows:
1. If LINR==LINEAR or LINR==SLOPE, then X = (VAL - EOFF) / ESLO, else if LINR==NO_CONVERSION, then X = VAL, else X is obtained via breakpoint table.
2. X = (X - AOFF) / ASLO
3. RVAL = round(X) - ROFF
15/100 = 0.15....round(0.15) = 0.....I thought VAL is multiplied by ASLO not divided.
Setting ASLO to 0.01 instead of 100 leads to the expected output:
epics> dbpf SCATTERCHAMBER:COOLING:Setpoint 15
2022/05/20 10:06:23.565 drvModbusAsyn::doModbusIO port chillerWriteReg WRITE_SINGLE_REGISTER address=00 value=0x5dc
DBF_DOUBLE:         15
2022/05/20 10:06:23.565 PilotONE-187144:502 TCP write 12
15 75 00 00 00 06 ff 06 00 00 05 dc
2022/05/20 10:06:23.618 PilotONE-187144:502 TCP read 12
2022/05/20 10:06:23.620 drvModbusAsyn::doModbusIO port chillerWriteReg called pasynOctetSyncIO->writeRead, status=0, requestSize=6, replySize=5, nwrite=6, nread=5, eomReason=1
2022/05/20 10:06:23.621 drvModbusAsyn::writeInt32 port chillerWriteReg function=0x6, modbusAddress=00, buffer[0]=0x5dc, bufferLen=1
VG Florian
On 5/19/22 21:03, Mark Rivers wrote:
Hi Florian,
1.      For reading out the status of the chiller, I have set the SCAN field of the first input record and use a chain of forward links to all the other input records.
2.      My guess is, the forward links are processed "too fast" for the controller and it cannot reply.
Is this plausible or could this error messages have a different cause?
What would be a good idea to "slow down" the readout?
Using a seq record with delays instead of forward links?
I see you defined your driver to use absolute addressing.  That is not the way it is typically used.  If you change to relative addressing then when you process your input records they don’t actually cause any Modbus I/O, they just return the most recent poll reading from the driver.  That means there is no reason to “slow down” the readout, since it is not affecting the Modbus communications.  If your drivers are polling (not absolute addresses) then you should probably not set your input records to periodically scan, but rather set them SCAN=I/O Intr.  Then the records will only process when the polled value changes.
I am not sure why it is not sending the correct value for the temperature.
What version of the Modbus driver are you using?  If the device sends a Modbus exception then I believe some older versions of the driver would not show you that, and it would appear that you received no response.
From: Tech-talk <[email protected]> On Behalf Of Florian Feldbauer via Tech-talk
Sent: Thursday, May 19, 2022 10:15 AM
To: [email protected]
Subject: Modbus for Huber Pilotone
Hey all,
we have a Huber Unistat chiller with "PilotOne" Controller. The Controller has a modbus/TCP interface.
Sometimes I can see messages of the following type in my IOC:
epics> 2022/05/19 16:46:36.370 drvModbusAsyn::doModbusIO port chillerReadReg error calling writeRead, error=PilotONE-187144:502 TCP timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
2022/05/19 16:46:36.370 SCATTERCHAMBER:COOLING:FillLevel devAsynInt32::processCallbackInput process read error
2022/05/19 16:46:36.469 drvModbusAsyn::doModbusIO port chillerReadReg writeRead status back to normal having had 1 errors, nwrite=6/6, nread=4
Another issue, that I have is writing the Setpoint of the device. From the manual:
The client sends the following request to the Modbus slave:
  00 02 00 00 00 06 FF 06 00 00 05 DC
The command is made up as follows:
00 02    TID (any number that can be used to assign a response to a query)
00 00    PID (always 0x0000)
00 06    The message length is 6 bytes. Of these, 1 byte is used for the unit identifier, 1 byte
          for the function code, 2 bytes for the PB address and 2 bytes are used for the value
          to be written.
FF      Unit identifier (UID, always 0xFF)
06      Function code 0x06 is used for Writing Single Holding Registers
00 00    PB address (vSP 0x00)
05 DC    The setpoint temperature is to be set to 15.00 °C. The value 1500 equals 0x05DC in
         hex notation.
The Modbus slave returns the following response:
For me it looks like this:
DBF_DOUBLE:         15
2022/05/19 17:04:09.078 drvModbusAsyn::doModbusIO port chillerWriteReg WRITE_SINGLE_REGISTER address=00 value=0x0
epics> 2022/05/19 17:04:09.078 PilotONE-187144:502 TCP write 12
a2 3e 00 00 00 06 ff 06 00 00 00 00
2022/05/19 17:04:09.078 PilotONE-187144:502 TCP read 0
2022/05/19 17:04:09.079 drvModbusAsyn::doModbusIO port chillerWriteReg called pasynOctetSyncIO->writeRead, status=3, requestSize=6, replySize=5, nwrite=6, nread=0, eomReason=0
epics>
First, the value (15) is not send, instead 00 00 is send. Second I do not get a reply from the device.
I load the driver with
drvAsynIPPortConfigure( "chiller", "PilotONE-187144:502 TCP", 0, 0, 0 )
modbusInterposeConfig( "chiller", 0, 300, 0 )
drvModbusAsynConfigure( "chillerWriteReg",  "chiller", 0xff, 6, -1, 1, "INT16", 0, "Huber PilotOne" )
The record looks like this:
record( ao, "$(H):$(N):Setpoint" ) {
  field( DTYP, "asynInt32" )
  field( OUT,  "@asyn($(PORT_W) 0x00)INT16" )
  field( EGU,  "degC" )
  field( PREC, "2" )
  field( ADEL, "1" )
  field( MDEL, "1" )
  field( ASLO, "100" )
  field( AOFF, "0" )
Any idea what am I doing wrong here?
Thanks for your help,
Florian
Ruhr-Universität Bochum
AG der Experimentalphysik I
Dr. Florian Feldbauer
NB 2/131 / Fach 125
Universitätsstr. 150
D-44801 Bochum
Office: NB 2/134
Phone:  (+49)234 / 32-23563
Fax:    (+49)234 / 32-14170
https://paluma.ruhr-uni-bochum.de
NB 2/131 / Fach 125
D-44801 Bochum
Office: NB 2/134
NB 2/131 / Fach 125
D-44801 Bochum
Office: NB 2/134
Modbus for Huber Pilotone Florian Feldbauer via Tech-talk
RE: Modbus for Huber Pilotone Mark Rivers via Tech-talk
Re: Modbus for Huber Pilotone Florian Feldbauer via Tech-talk
Prev: Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Wang, SuYin Grass via Tech-talk
Next: RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
Prev: RE: Modbus for Huber Pilotone Mark Rivers via Tech-talk
Next: procServer unix socket configuration Han Lee via Tech-talk
