1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026
Subject: RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
To: Michael Davidsaver <[email protected]>
Date: Sat, 21 May 2022 18:05:24 +0000
Hi Michael
Ø  What specific board is involved?  (eg. mvme3100?)
The test crate is an MVME5100.  But the production crates that were also failing include several MVME2700 boards as well as some MVME5100.
Ø  Although you haven't mentioned the presence of an EVR card or timing driver.
There is no EVR card or timing driver.  The following cards seem to work fine:
-          SIS3801 and SIS3820 VME cards.  These are scalers/multichannel scalers.  I have tested them a lot and it does not crash.
-          IpUnidig digital I/O Industry Pack module with interrupts on inputs.  I cannot get any failures flipping these bits.  It is on the same carrier card as the IP330.
Ø  I still wonder if this isn't somehow resulting from an incomplete rebuild.
I don’t think so.  I did a “make clean” at the top of the synApps/support tree, which includes my specific application directory.  I then did a “find” for .o files and there were none leftover.
Ø  Since the error seems to come from a CAS-event thread, I would be interested to know which CA client is associated.  Running "casr 5" will show this (and more).  eg.
I have attached a file which shows the following:
Ø  Ran casr 5 right after IOC finishes startup.  It shows a client which is connected to a few records from the iocStats module.
Ø  Opened medm screen for IP330, got VME bus error
Ø  Ran casr 5 again showing connections for that medm screen.
Sent: Saturday, May 21, 2022 12:39 PM
Cc: [email protected]
Subject: Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
On 5/21/22 09:42, Mark Rivers via Tech-talk wrote:
My production VME crates are now running base 7.0.5 and working fine.
I have one test crate which I just started with base 7.0.6.1.  Fortunately it also fails, so it should be possible to debug this issue.
In this case...
This crate has 7 Industry Pack modules, including an IP300 ADC.  That module uses interrupts at 2 kHz to read the ADC values.  There was a VME bus error as soon as I opened an medm screen to look at the ai records for this device.  This was the error:
[Sat May 21 10:06:18 2022] VME Bus Error accessing A16: 0x325e
[Sat May 21 10:06:18 2022] machine check
[Sat May 21 10:06:18 2022] Exception next instruction address: 0x03606bd4
[Sat May 21 10:06:18 2022] Machine Status Register: 0x0008b032
[Sat May 21 10:06:18 2022] Condition Register: 0x48000884
[Sat May 21 10:06:18 2022] Task: 0x58e8e10 "CAS-event"
[Sat May 21 10:06:18 2022] 0x58e8e10 (CAS-event): task 0x58e8e10 has had a failure and has been stopped.
[Sat May 21 10:06:18 2022] 0x58e8e10 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
I remain surprised that a CAS-event thread seems to be involved.  I don't think this thread would be running driver code.  Though it might be calling things like generalTime providers or server side filter hooks, which might be making VME access.  Although you haven't mentioned the presence of an EVR card or timing driver.
I say "seems to be" because there is a chance that vxworks is somehow messing up and capturing wrong thread.  eg. a driver makes a VME access, then posts a monitor, which causing a context switch to CAS-event.  Then somehow the CPU exception arrives late, with the wrong instruction pointer address.  This is probably possible w/ some powerpc and out of order execution.
Why would the CAS-event task be doing VME I/O, since I was not doing a CA put, I just opened an medm screen that would be doing CA monitors?
epics> casr 5
Channel Access Server V4.13
1 client connected:
   TCP client at 192.168.1.175:48972 'md-laptop':
       User 'mdavidsaver', V4.13, Priority = 0, 1 Channel
       Task Id = 0x7f2274005ea0, Socket FD = 7
       0.48 secs since last send, 4.21 secs since last receive
       Unprocessed request bytes = 0, Undelivered response bytes = 0
       State = up
       Channel: 'cnt'
 I tested this several times.  It always fails within 1 second, but not always with the same error.  Sometimes I get the same A16 bus error with the same 0x325e address.  But sometimes I get this error:
If you've identified a particular record, try setting TPRO to see if anything else is happening.
VME Bus Error accessing A32: 0xbfa1ee10
machine check
Exception next instruction address: 0x0368cec0
Condition Register: 0x42000884
Task: 0x5529e10 "CAS-event"
0x5529e10 (CAS-event): task 0x5529e10 has had a failure and has been stopped.
0x5529e10 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
I also tested opening an MEDM screen to adjust the D/A values on the DAC128V.  After a few seconds of doing that I got this error:
[Sat May 21 11:08:25 2022] VME Bus Error accessing A32: 0xbfd76a40
[Sat May 21 11:08:25 2022] machine check
[Sat May 21 11:08:25 2022] Exception next instruction address: 0x0368cea0
[Sat May 21 11:08:25 2022] Machine Status Register: 0x0008b032
[Sat May 21 11:08:25 2022] Condition Register: 0x48000884
[Sat May 21 11:08:25 2022] Task: 0x564bf20 "CAS-event"
[Sat May 21 11:08:25 2022] 0x564bf20 (CAS-event): task 0x564bf20 has had a failure and has been stopped.
[Sat May 21 11:08:25 2022] 0x564bf20 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
This error is in the A32 address space. I am not sure if the DAC128V driver uses the A32 address space or not.  However, I have not been able to reproduce this error, usually I can adjust the DAC for a long time with no crash, so this could have been a coincidence.
Sent: Friday, May 20, 2022 5:39 PM
To: [email protected]
The A16 VME bus errors are all in the 0x3xxx range, which is the address of the first IP carrier card.  That card holds 4 modules, and these each have 256 bytes of A16 address space.
Module
First address
Last address
0
0x3000
0x30ff
1
0x3100
0x31ff
2
0x3200
0x32ff
3
0x3300
0x33ff
There are 4 VME crates that are generating VME bus errors, and 3 which are not.  These have different Industry Pack modules installed in each slot, listed in this table.  I have highlighted in red the modules corresponding to the bus failure addresses.
VME crate
Carrier card
Failing bus address
Module 0
Module 1
Module 2
Module 3
13IDA
VIPC616_01
0x300e 0x3146
tyGSOctal
tyGSOctal
IpUnidig
DAC128V
13IDC
TVME200
None
tyGSOctal
tyGSOctal
IP330
IpUnidig
13IDD
VIPC616_01
0x3206
tyGSOctal
tyGSOctal
IpUnidig
IP330
13IDE
TVME200
0x317e
tyGSOctal
IP330
IpUnidig
DAC128V
13BMA
VIPC616_01
0x3136
tyGSOctal
tyGSOctal
DAC128V
13BMC
VIPC616_01
None
tyGSOctal
IP330
DAC128V
IpUnidig
13BMD
VIPC616_01
0x3046 0x315e 0x317e 0x3316
tyGSOctal
IP330
IpUnidig
tyGSOctal
The failures are only on the tyGSOctal and the IP300.
The tyGSOctal is an 8-channel RS-232 module which has lots of activity polling serial devices.
The IP330 is an interrupt driven ADC which is being read at 1 kHz.  This also has lots of VME bus activity.
The IpUnidig is an interrupt driver digital I/O module.  Because its inputs are not changing, and there are no clients writing the outputs there is very little VME bus activity.
The DAC128V is an 8-channel D/A.  Since there are no clients writing to it there is very little VME bus activity.
The failures appear to be limited to the addresses of modules with lots of VME bus activity, and not to a single module since the tyGSOctal, IP330, and IpUnidig all seem to fail.
I have not yet looked at the A32 VME bus address errors.
Sent: Friday, May 20, 2022 8:07 AM
I have now tested using base 7.0.5 rather than 7.0.6.1.  The problem does not occur with base 7.0.5.  I have switched back and forth twice, being certain to completely clean and rebuild all synApps modules and my own application first when doing so.
I am running 7 VME crates with vxWorks 6.9.4.1.  I am logging the IOC output for each of them with procServ.
I was running base 7.0.6.1 between about Wed May 18 15:00 and Thu May 19 15:00.  During that time I observed the following VME bus errors.
/home/epics/logs/13BMD.log:[Wed May 18 15:46:12 2022] VME Bus Error accessing A16: 0x3316
/home/epics/logs/13IDE.log:[Wed May 18 16:07:12 2022] VME Bus Error accessing A16: 0x317e
/home/epics/logs/13IDA.log:[Wed May 18 16:50:32 2022] VME Bus Error accessing A16: 0x3146
/home/epics/logs/13IDE.log:[Wed May 18 17:23:08 2022] VME Bus Error accessing A16: 0x317e
/home/epics/logs/13IDC.log:[Wed May 18 18:11:58 2022] VME Bus Error accessing A32: 0xbf57c014
/home/epics/logs/13BMD.log:[Wed May 18 18:12:43 2022] VME Bus Error accessing A16: 0x317e
/home/epics/logs/13BMA.log:[Wed May 18 18:16:04 2022] VME Bus Error accessing A16: 0x3136
/home/epics/logs/13IDE.log:[Wed May 18 18:20:22 2022] VME Bus Error accessing A32: 0xbf140014
/home/epics/logs/13IDA.log:[Wed May 18 20:23:06 2022] VME Bus Error accessing A16: 0x300e
/home/epics/logs/13BMD.log:[Thu May 19 11:13:34 2022] VME Bus Error accessing A16: 0x3046
/home/epics/logs/13IDC.log:[Thu May 19 12:03:54 2022] VME Bus Error accessing A32: 0xbf7db01c
/home/epics/logs/13BMD.log:[Thu May 19 12:42:30 2022] VME Bus Error accessing A32: 0xbffcac70
/home/epics/logs/13IDA.log:[Thu May 19 12:44:11 2022] VME Bus Error accessing A16: 0x300e
/home/epics/logs/13IDC.log:[Thu May 19 13:01:55 2022] VME Bus Error accessing A32: 0xbf554014
/home/epics/logs/13IDE.log:[Thu May 19 13:11:16 2022] VME Bus Error accessing A32: 0xbf2e001c
/home/epics/logs/13IDE.log:[Thu May 19 13:11:45 2022] VME Bus Error accessing A16: 0x315e
/home/epics/logs/13IDD.log:[Thu May 19 13:18:03 2022] VME Bus Error accessing A32: 0xbf390018
/home/epics/logs/13IDE.log:[Thu May 19 13:25:25 2022] VME Bus Error accessing A32: 0xbf140014
/home/epics/logs/13BMD.log:[Thu May 19 13:40:38 2022] VME Bus Error accessing A16: 0x317e
/home/epics/logs/13IDE.log:[Thu May 19 14:09:56 2022] VME Bus Error accessing A32: 0xbf140014
So there were about 20 errors in 24 hours.  I did reboot the IOCs a few times during this period, and the probability of an error is definitely higher in the few minutes after a reboot, perhaps as OPI displays reconnect their CA links.
At about Thu May 19 15:00 I switched to base 7.0.5 and ran for 3 hours, until about 18:00.  There were no bus errors.
At Thu May 19 17:45 I switched back to 7.0.6.1 for about 3 hours until 21:00.  I observed the following errors during this time.
/home/epics/logs/13IDE.log:[Thu May 19 17:58:59 2022] VME Bus Error accessing A32: 0xbf2e001c
/home/epics/logs/13BMD.log:[Thu May 19 18:09:48 2022] VME Bus Error accessing A16: 0x315e
/home/epics/logs/13IDD.log:[Thu May 19 19:16:00 2022] VME Bus Error accessing A16: 0x3206
At about Thu May 19 21:00 I switched to base 7.0.5 again.  That was 11 hours ago, and there have been no bus errors in that time.
It is clear that my systems fail with 7.0.6.1 and work fine with 7.0.5, all other software being identical. It is certainly possible that 7.0.6.1 is exposing a problem with the other software which 7.0.5 does not.  I cannot afford to experiment or test more with these 7 VME systems, since beam comes back soon.  I do have one other VME crate that can be used for testing.  It is not currently running, so I don’t know if it fails with 7.0.6.1, but I will turn it on today.
Note that prior to this week I had been running base 7.0.4 on these systems for over a year with no issues.  This week I did update to the latest versions of the synApps modules, but I did not change my IOC specific code at all.
Sent: Thursday, May 19, 2022 8:34 AM
To: Johnson, Andrew N. <[email protected]>
Subject: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
Folks,
I updated my VME crates from base 7.0.4 to 7.0.6.1, and also updated to the latest version of synApps modules. 5 of the 7 crates are now giving VME bus errors within a few minutes of booting.  Since it is happening on 5 crates it is highly unlikely to be a hardware problem.
The errors are all for a small set of addresses:
A16: 0x300e, 0x3136, 0x3172
These are in the address space of the first Industry Pack module on a VIPC616_01 or TVME200 IP carrier card
A32:  0xbf57c014
I am not sure what device this is.  The Joerger scalars are configured to start at address  0xB0000000, but I don’t think they use that much memory space.
The task generating the error is always “CAS-event”.
These are the errors:
13IDA crate:
[Wed May 18 20:23:06 2022] machine check
[Wed May 18 20:23:06 2022] Exception next instruction address: 0x03604600
[Wed May 18 20:23:06 2022] Machine Status Register: 0x0008b032
[Wed May 18 20:23:06 2022] Condition Register: 0x42000884
[Wed May 18 20:23:06 2022] Task: 0x55d8aa0 "CAS-event"
[Wed May 18 20:23:06 2022] 0x55d8aa0 (CAS-event): task 0x55d8aa0 has had a failure and has been stopped.
[Wed May 18 20:23:06 2022] 0x55d8aa0 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
[Wed May 18 20:48:19 2022] 0x4d50400 (timerQueue): callbackRequest: cbLow ring buffer full
13BMA crate
[Wed May 18 18:16:04 2022] machine check
[Wed May 18 18:16:04 2022] Exception next instruction address: 0x0141b5b8
[Wed May 18 18:16:04 2022] Machine Status Register: 0x0008b032
[Wed May 18 18:16:04 2022] Condition Register: 0x42000884
[Wed May 18 18:16:04 2022] Task: 0x3545520 "CAS-event"
[Wed May 18 18:16:04 2022] 0x3545520 (CAS-event): task 0x3545520 has had a failure and has been stopped.
[Wed May 18 18:16:04 2022] 0x3545520 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
13IDC crate:
[Wed May 18 18:11:58 2022] machine check
[Wed May 18 18:11:58 2022] Exception next instruction address: 0x013962a0
[Wed May 18 18:11:58 2022] Machine Status Register: 0x0008b032
[Wed May 18 18:11:58 2022] Condition Register: 0x42000884
[Wed May 18 18:11:58 2022] Task: 0x395e4b0 "CAS-event"
[Wed May 18 18:11:58 2022] 0x395e4b0 (CAS-event): task 0x395e4b0 has had a failure and has been stopped.
[Wed May 18 18:11:58 2022] 0x395e4b0 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
13BMD crate:
[Wed May 18 18:12:43 2022] machine check
[Wed May 18 18:12:43 2022] Exception next instruction address: 0x01395e40
[Wed May 18 18:12:43 2022] Machine Status Register: 0x0008b032
[Wed May 18 18:12:44 2022] Condition Register: 0x48000884
[Wed May 18 18:12:44 2022] Task: 0x3c73ae0 "CAS-event"
[Wed May 18 18:12:44 2022] 0x3c73ae0 (CAS-event): task 0x3c73ae0 has had a failure and has been stopped.
[Wed May 18 18:12:44 2022] 0x3c73ae0 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
13IDE crate:
[Wed May 18 16:07:12 2022] machine check
[Wed May 18 16:07:12 2022] Exception next instruction address: 0x01395c20
[Wed May 18 16:07:12 2022] Machine Status Register: 0x0008b032
[Wed May 18 16:07:12 2022] Condition Register: 0x48000884
[Wed May 18 16:07:12 2022] Task: 0x3a13c60 "CAS-event"
[Wed May 18 16:07:12 2022] 0x3a13c60 (CAS-event): task 0x3a13c60 has had a failure and has been stopped.
[Wed May 18 16:07:12 2022] 0x3a13c60 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
[Wed May 18 18:20:22 2022] machine check
[Wed May 18 18:20:22 2022] Exception next instruction address: 0x013959c0
[Wed May 18 18:20:22 2022] Machine Status Register: 0x0008b032
[Wed May 18 18:20:22 2022] Condition Register: 0x48000884
[Wed May 18 18:20:22 2022] Task: 0x3a2d780 "CAS-event"
[Wed May 18 18:20:22 2022] 0x3a2d780 (CAS-event): task 0x3a2d780 has had a failure and has been stopped.
[Wed May 18 18:20:23 2022] 0x3a2d780 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
This is the result of “tt” and “ti” on a couple of the crashed tasks:
ioc13ida> tt 0x55d8aa0
0x0012489c vxTaskEntry  +0x48 : epicsThreadEntry ()
0x036a6afc epicsThreadEntry+0x80 : 0x03604e20 ()
0x036050f8 db_start_events+0x458: db_delete_field_log ()
value = 0 = 0x0
ioc13ida> ti 0x55d8aa0
  NAME         ENTRY       TID    PRI   STATUS      PC       SP     ERRNO  DELAY
CAS-event   epicsThread>  55d8aa0 139 STOP+I      3604600  55d89b0       0     0
full task name : CAS-event
task entry     : epicsThreadEntry
process        : kernel
options        : 0x1009001
VX_SUPERVISOR_MODE  VX_DEALLOC_TCB      VX_FP_TASK          VX_DEALLOC_EXC_STACK
STACK      BASE     END       SP      SIZE    HIGH   MARGIN
execution  55d8aa0  55d5bc0  55d89b0   12000    3568    8432
exception  55d9bf0  55d8d80             3696    1344    2352
VxWorks Events
Events Pended on    : Not Pended
Received Events     : 0x0
Options             : N/A
r0         = 0x40050000   sp         = 0x055d89b0   r2         = 0x002f1ac0
r3         = 0x04e56c70   r4         = 0x05293e20   r5         = 0x00000001
r6         = 0x00000001   r7         = 0x00000000   r8         = 0x00000000
r9         = 0x0368a8b8   r10        = 0x00000000   r11        = 0x055d8920
r12        = 0x22000884   r13        = 0x00321e60   r14        = 0x036a5e98
r15        = 0x03fb9a44   r16        = 0x035ec8c0   r17        = 0x03fb99fc
r18        = 0x00000000   r19        = 0x036a3f3c   r20        = 0x03fb99bc
r21        = 0x0360461c   r22        = 0x00000001   r23        = 0x036045b4
r24        = 0x04341544   r25        = 0x0369d438   r26        = 0x0369d698
r27        = 0x05156b28   r28        = 0x03639dc8   r29        = 0x05b15c98
r30        = 0x05293e20   r31        = 0x05293e20   msr        = 0x0008b032
lr         = 0x036050f8   ctr        = 0x036045b4   pc         = 0x03604600
cr         = 0x42000884   xer        = 0x00000000   pgTblPtr   = 0x02310000
scSrTblPtr = 0x0230fe74   srTblPtr   = 0x0230fe74
fpcsr  =        0
fr0    =       -1   fr1    =      NaN   fr2    =      NaN   fr3    =      NaN
fr4    =      NaN   fr5    =      NaN   fr6    =      NaN   fr7    =      NaN
fr8    =      NaN   fr9    =      NaN   fr10   =      NaN   fr11   =      NaN
fr12   =      NaN   fr13   =      NaN   fr14   =      NaN   fr15   =      NaN
fr16   =      NaN   fr17   =      NaN   fr18   =      NaN   fr19   =      NaN
fr20   =      NaN   fr21   =      NaN   fr22   =      NaN   fr23   =      NaN
fr24   =      NaN   fr25   =      NaN   fr26   =      NaN   fr27   =      NaN
fr28   =      NaN   fr29   =      NaN   fr30   =      NaN   fr31   =      NaN
machine check
Exception next instruction address: 0xva0lue = 3604600
Machine Status Register: 0x00008b032
Condition Register: 0x = 420008840x
ioc13ide> tt 0x3a2d780
0x00121e7c vxTaskEntry  +0x48 : epicsThreadEntry ()
0x01437ebc epicsThreadEntry+0x80 : 0x013961e0 ()
0x013964b8 db_start_events+0x458: db_delete_field_log ()
value = 0 = 0x0
ioc13ide> ti 0x3a2d780
CAS-event   epicsThread>  3a2d780 133 STOP+I      13959c0  3a2d690       0     0
process        : kernel
options        : 0x1009001
execution  3a2d780  3a2a8a0  3a2d690   12000    2800    9200
exception  3a2e8d0  3a2da60             3696    1344    2352
VxWorks Events
Options             : N/A
r0         = 0x40050000   sp         = 0x03a2d690   r2         = 0x002e5010
r3         = 0x02dc8530   r4         = 0x0366ac00   r5         = 0x00000001
r6         = 0x00000001   r7         = 0x00000000   r8         = 0x00000002
r9         = 0x0141bc78   r10        = 0x00000000   r11        = 0x03a2d600
r12        = 0x28000884   r13        = 0x00313850   r14        = 0x01437258
r15        = 0x01d4ae04   r16        = 0x0137dc80   r17        = 0x01d4adbc
r18        = 0x00000000   r19        = 0x014352fc   r20        = 0x01d4ad7c
r21        = 0x013959dc   r22        = 0x00000001   r23        = 0x01395974
r24        = 0x020d2904   r25        = 0x0142e7f8   r26        = 0x0142ea58
r27        = 0x0351b4c8   r28        = 0x013cb188   r29        = 0x03a98e70
r30        = 0x0366ac00   r31        = 0x0366ac00   msr        = 0x0008b032
lr         = 0x013964b8   ctr        = 0x01395974   pc         = 0x013959c0
cr         = 0x48000884   xer        = 0x00000000   pgTblPtr   = 0x00af7000
scSrTblPtr = 0x00af65c4   srTblPtr   = 0x00af65c4
fpcsr  =        0
fr0    = -7.62951e-05   fr1    =      NaN   fr2    =      NaN   fr3    =      NaN
machine checkvalue =
Exception next instruction address: 0x0013959c0
Machine Status Register: 0x = 0008b032
Condition Register: 0x048000884x
Any ideas?
Done executing startup script '/home/epics/devel/CARS/iocBoot/ioc13lab/st.cmd'.
ioc13lab> casr 5
1 client connected:
    TCP client at 164.54.160.82:36816 'corvette':
        User 'epics', V4.13, Priority = 0, 4 Channels
        Task Id = 0x553fdb0, Socket FD = 53
        0.40 secs since last send, 1348.17 secs since last receive
        State = up
        Channel: '13LAB::UPTIME'
            field_type=DBF_STRING (40 bytes), dbr_type=DBF_STRING, 1 element, no filters
            # on eventq=1, access=rw
        Channel: '13LAB::CA_CONN_CNT'
            field_type=DBF_DOUBLE (8 bytes), dbr_type=DBF_DOUBLE, 1 element, no filters
        Channel: '13LAB::SYS_CPU_LOAD'
        Channel: '13LAB::MEM_FREE'
        1176 bytes allocated
        Send Lock:
            epicsMutexId 0x54bba70 source ../rsrv/caservertask.c line 1254
Semaphore Id        : 0x54ecda0
Semaphore Name      : N/A
Semaphore Type      : MUTEX
Task Queuing        : PRIORITY
Pended Tasks        : 0
Owner               : NONE
Options             : 0xd       SEM_Q_PRIORITY
                                SEM_DELETE_SAFE
                                SEM_INVERSION_SAFE
VxWorks Events
Registered Task     : NONE
Event(s) to Send    : N/A
Options             : N/A
        Put Notify Lock:
            epicsMutexId 0x54ef960 source ../rsrv/caservertask.c line 1255
Semaphore Id        : 0x54ece20
Pended Tasks        : 0
Owner               : NONE
                                SEM_DELETE_SAFE
                                SEM_INVERSION_SAFE
VxWorks Events
Options             : N/A
        Address Queue Lock:
            epicsMutexId 0x54c54e0 source ../rsrv/caservertask.c line 1256
Semaphore Id        : 0x54edd20
Pended Tasks        : 0
Owner               : NONE
                                SEM_DELETE_SAFE
                                SEM_INVERSION_SAFE
VxWorks Events
Options             : N/A
        Event Queue Lock:
            epicsMutexId 0x54ed6e0 source ../rsrv/caservertask.c line 1257
Semaphore Id        : 0x54edda0
Pended Tasks        : 0
Owner               : NONE
                                SEM_DELETE_SAFE
                                SEM_INVERSION_SAFE
VxWorks Events
Options             : N/A
        Block Semaphore:
Semaphore Id        : 0x54ed330
Semaphore Type      : BINARY
Task Queuing        : FIFO
Pended Tasks        : 0
State               : EMPTY
Options             : 0x0       SEM_Q_FIFO
VxWorks Events
Options             : N/A
 CAS-TCP server on 0.0.0.0:5064 with
    CAS-UDP name server on 0.0.0.0:5064
        Last name requested by 164.54.160.64:53062:
        User '', V4.13, Priority = 0, 0 Channels
        Task Id = 0x530d590, Socket FD = 40
        1351.35 secs since last send, 0.03 secs since last receive
        Unprocessed request bytes = 0, Undelivered response bytes = 16
        State = up
Sending CAS-beacons to 1 address:
    164.54.160.255:5065
Free-lists total 283312 bytes, comprising
    6 client(s), 508 channel(s), 508 monitor event(s), 0 putNotify(s)
    14 small (16384 byte) buffers, 4294967295 jumbo (500024 byte) buffers
Server resource id table:
    Bucket entries in use = 4 bytes in use = 16468
    Bucket entries/hash id - mean = 0.000977 std dev = 0.031235 max = 1
value = 0 = 0x0
ioc13lab>
ioc13lab>
ioc13lab>
ioc13lab>
ioc13lab>
ioc13lab>
VME Bus Error accessing A16: 0x327e
machine check
Exception next instruction address: 0x0368ce90
Task: 0x55394d0 "CAS-event"
0x55394d0 (CAS-event): task 0x55394d0 has had a failure and has been stopped.
0x55394d0 (CAS-event): The task has been terminated because it triggered an exception that raised the signal 10.
ioc13lab>
ioc13lab> casr 5
1 client connected:
        User 'epics', V4.13, Priority = 0, 68 Channels
        13.22 secs since last send, 18.70 secs since last receive
        State = up
        Channel: '13LAB:IP330_1.SCAN'
            field_type=DBF_MENU (2 bytes), dbr_type=DBF_ENUM, 1 element, no filters
        Channel: '13LAB:IP330_1.VAL'
        Channel: '13LAB:IP330_1.PREC'
            field_type=DBF_SHORT (2 bytes), dbr_type=DBF_SHORT, 1 element, no filters
        Channel: '13LAB:IP330_2.SCAN'
        Channel: '13LAB:IP330_2.VAL'
        Channel: '13LAB:IP330_2.PREC'
        Channel: '13LAB:IP330_3.SCAN'
        Channel: '13LAB:IP330_3.VAL'
        Channel: '13LAB:IP330_3.PREC'
        Channel: '13LAB:IP330_4.SCAN'
        Channel: '13LAB:IP330_4.VAL'
        Channel: '13LAB:IP330_4.PREC'
        Channel: '13LAB:IP330_5.SCAN'
        Channel: '13LAB:IP330_5.VAL'
        Channel: '13LAB:IP330_5.PREC'
        Channel: '13LAB:IP330_6.SCAN'
        Channel: '13LAB:IP330_6.VAL'
        Channel: '13LAB:IP330_6.PREC'
        Channel: '13LAB:IP330_7.SCAN'
        Channel: '13LAB:IP330_7.VAL'
        Channel: '13LAB:IP330_7.PREC'
        Channel: '13LAB:IP330_8.SCAN'
        Channel: '13LAB:IP330_8.VAL'
        Channel: '13LAB:IP330_8.PREC'
        Channel: '13LAB:IP330_9.SCAN'
        Channel: '13LAB:IP330_9.VAL'
        Channel: '13LAB:IP330_9.PREC'
        Channel: '13LAB:IP330_10.SCAN'
        Channel: '13LAB:IP330_10.VAL'
        Channel: '13LAB:IP330_10.PREC'
        Channel: '13LAB:IP330_11.SCAN'
        Channel: '13LAB:IP330_11.VAL'
        Channel: '13LAB:IP330_11.PREC'
        Channel: '13LAB:IP330_12.SCAN'
        Channel: '13LAB:IP330_12.VAL'
        Channel: '13LAB:IP330_12.PREC'
        Channel: '13LAB:IP330_13.SCAN'
        Channel: '13LAB:IP330_13.VAL'
        Channel: '13LAB:IP330_13.PREC'
        Channel: '13LAB:IP330_14.SCAN'
        Channel: '13LAB:IP330_14.VAL'
        Channel: '13LAB:IP330_14.PREC'
        Channel: '13LAB:IP330_15.SCAN'
        Channel: '13LAB:IP330_15.VAL'
        Channel: '13LAB:IP330_15.PREC'
        Channel: '13LAB:IP330_16.SCAN'
        Channel: '13LAB:IP330_16.VAL'
        Channel: '13LAB:IP330_16.PREC'
        Channel: '13LAB:IP330_1.DESC'
            field_type=DBF_STRING (41 bytes), dbr_type=DBF_STRING, 1 element, no filters
        Channel: '13LAB:IP330_2.DESC'
        Channel: '13LAB:IP330_3.DESC'
        Channel: '13LAB:IP330_4.DESC'
        Channel: '13LAB:IP330_5.DESC'
        Channel: '13LAB:IP330_6.DESC'
        Channel: '13LAB:IP330_7.DESC'
        Channel: '13LAB:IP330_8.DESC'
        Channel: '13LAB:IP330_9.DESC'
        Channel: '13LAB:IP330_10.DESC'
        Channel: '13LAB:IP330_11.DESC'
        Channel: '13LAB:IP330_12.DESC'
        Channel: '13LAB:IP330_13.DESC'
        Channel: '13LAB:IP330_14.DESC'
        Channel: '13LAB:IP330_15.DESC'
        Channel: '13LAB:IP330_16.DESC'
        17048 bytes allocated
        Send Lock:
Pended Tasks        : 0
Owner               : NONE
                                SEM_DELETE_SAFE
                                SEM_INVERSION_SAFE
VxWorks Events
Options             : N/A
        Put Notify Lock:
Pended Tasks        : 0
Owner               : NONE
                                SEM_DELETE_SAFE
                                SEM_INVERSION_SAFE
VxWorks Events
Options             : N/A
        Address Queue Lock:
Pended Tasks        : 0
Owner               : NONE
                                SEM_DELETE_SAFE
                                SEM_INVERSION_SAFE
VxWorks Events
Options             : N/A
        Event Queue Lock:
Pended Tasks        : 0
Owner               : NONE
                                SEM_DELETE_SAFE
                                SEM_INVERSION_SAFE
VxWorks Events
Options             : N/A
        Block Semaphore:
Task Queuing        : FIFO
Pended Tasks        : 0
State               : EMPTY
VxWorks Events
Options             : N/A
        Last name requested by 164.54.160.111:54303:
        32.85 secs since last send, 0.22 secs since last receive
        State = up
    164.54.160.255:5065
Free-lists total 276656 bytes, comprising
    6 client(s), 444 channel(s), 444 monitor event(s), 0 putNotify(s)
    Bucket entries in use = 68 bytes in use = 17492
    Bucket entries/hash id - mean = 0.016602 std dev = 0.127773 max = 1
value = 0 = 0x0
ioc13lab>
RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Michael Davidsaver via Tech-talk
Prev: Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Michael Davidsaver via Tech-talk
Next: RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026
