1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026
Subject: Re: Phoebus alarm does not honor filter
From: "Kasemir, Kay via Tech-talk" <[email protected]>
To: "[email protected]" <[email protected]>, "Zhang, Tong" <[email protected]>
Date: Thu, 9 Jun 2022 20:35:40 +0000
Well, I can't reproduce this.
Under https://github.com/ControlSystemStudio/phoebus/tree/master/app/alarm/examples, there's a demo.db and associated display.
I'm running a softIoc with that demo.db, add the test_alarm PV with enabling filter "test_enable>0" to the alarm tree, and then use the demo.bob display for the following:
1) Set test_alarm = 10, it shows up as MAJOR alarm in alarm table and tree
2) Set test_enable to 0. test_alarm is shown in gray with "(disabled)" in alarm tree, and not at all in alarm table
3) Set test_enable back to 1, and test_alarm shows back up as it looked in step 1
Did you somewhere configure the alarm server to run with the CA mask set to only pass alarm changes?
There is a preference setting https://control-system-studio.readthedocs.io/en/latest/preference_properties.html
org.phoebus.pv.ca/monitor_mask=ALARM
If you set that, the alarm server will subscribe to PVs by only listening to alarm severity changes.
That's more efficient than monitoring any VALUE changes, but also means that the PVs used in filters will only send a new value when they change alarm state.
The default is thus
org.phoebus.pv.ca/monitor_mask=VALUE
for filters to "work".
-Kay
From: Tech-talk <[email protected]> on behalf of Zhang, Tong via Tech-talk <[email protected]>
Sent: Wednesday, June 8, 2022 2:37 PM
To: [email protected] <[email protected]>
Subject: [EXTERNAL] Phoebus alarm does not honor filter
Dear Colleagues,
Recently, when I was working with Phoebus Alarm system to develop the alarms, I found the alarm filter does not work as expected, here is the example:
Let’s say ‘alm_pv’ is a non-latched alarm PV, and ‘alm_pv_filter’ is the filter PV which is used to enable/disable ‘alm_pv’;
The filter is “alm_pv_filter==1”, ‘alm_pv_fitler’ is initialized with 1, ‘alm_pv’ is set to 1 (1 is MAJOR, and 0.5 is MINOR, 0 is OK)
>From the Phoebus Alarm table, I see ‘alm_pv’ is major, and listed in the alarm table;
Now I set ‘alm_pv_filter’ as 0 to disable alarm ‘alm_pv’, I see ‘alm_pv’ is removed from the alarm table;
Now I set ‘alm_pv_filter’ as 1 to enable alarm ‘alm_pv’ again, and expected that the ‘alm_pv’ would be showing up in the alarm table again, but it was not! It does not show up, until, see next line;
Then I changed ‘alm_pv’ to 0 to make it OK, and changed it to MAJOR again by setting with 1, it appeared in the alarm table again.
So it seems that alarm is only triggered when the status is changed.
Is that true that what 5. described is exactly how the Phoebus alarm system works?
Tong
RE: Phoebus alarm does not honor filter Zhang, Tong via Tech-talk
Prev: RE: PyEpics: Cannot connect to DEVICE Mark Rivers via Tech-talk
Next: Re: [EXTERNAL] Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Hartman, Steven via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026
Prev: Phoebus alarm does not honor filter Zhang, Tong via Tech-talk
Next: RE: Phoebus alarm does not honor filter Zhang, Tong via Tech-talk
