1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <2023>  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <2023>  2024  2025  2026
Subject: RE: Alarm Topics Time out on system with network interface
From: CAOUEN Loic via Tech-talk <[email protected]>
Date: Tue, 1 Aug 2023 07:48:21 +0000
Hello Merrill,
First check your configuration is correct.
Alarm server uses the CA_ADDR_LIST in the settings.ini given when you start the service with
java -jar service-alarm-server-*.jar  -settings ${SERVER}/settings.ini
In this settings.ini you should have all the ip with IOC running
#  Channel Access
org.phoebus.pv.ca/addr_list=127.0.0.1 192.168.0.12 192.168.0.13:5066
It doesn't use the environment variable $EPICS_CA_ADDR_LIST
Alarm Server reads the PV status and then writes to kafka. Phoebus is not connected to the alarm server, but directly to Kafka.
By default, Kafka listens only on localhost:9092, which means kafka, alarm server and phoebus must be on the same server.
If phoebus is on another server you must modify the server.properties in kafka and add:
listeners = PLAINTEXT://your.host.name:9092
In settings.ini you should change
org.phoebus.applications.alarm/server=localhost:9092
by
org.phoebus.applications.alarm/server=your.host.name:9092
and of course open your firewall on 9092
I use a java program to check my kafka server is running and messages are written regularly :
https://github.com/kumait/kafkavisualizer
By the way, Phoebus keeps the settings when a tab is open. I recommend to close all your tabs in phoebus and then open a new alarm tree to be sur your settings are correct.
Regards
Loïc
-----Message d'origine-----
De : Tech-talk <[email protected]> De la part de Charles Merrill Jenkins via Tech-talk
Envoyé : lundi 31 juillet 2023 20:42
À : Phoebus Tech Talk <[email protected]>
Objet : Alarm Topics Time out on system with network interface
Hello Everyone,
I have been able to setup a EPICS softIoc, setup Alarm Topics with kafka/zookeeper, configure the alarms with alarm-server.sh and then get phoebus to run with the alarm tree, alarm table and  alarm area panel on a system with no network interface using localhost.
When I set up EPICS softIoc, zookeeper/kafka and alarm server that does has network interface, I find that the alarm topics disconnect soon after the alarm-server is started.
I found that I had to set EPICS_CA_AUTO_ADDR_LIST="NO"  for EPICS to access the softIoc PV's.  However, I can't find a way to get the alarm-topics to connect to the PV's.
Can someone point me in a direction on how to setup the alarm  topic configuration to connect to the PV's or to the diagnotic programs or statements to look at so I can see what I have not setup?
Thanks for the help!
Merrill Jenkins
Merrill Jenkins
Professor of Physics
==== Mailing Address ====
Physics
411 University Blvd. N.
MSPB RM 115
Mobile, AL 36688
phone 251.414.8013
Dept: 251.460.6224
Alarm Topics Time out on system with network interface Charles Merrill Jenkins via Tech-talk
Prev: epics-debhelper Daykin, Evan via Tech-talk
Next: Re: epics-debhelper Christoph Schröder via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <2023>  2024  2025  2026
Prev: Alarm Topics Time out on system with network interface Charles Merrill Jenkins via Tech-talk
Next: epics-debhelper Daykin, Evan via Tech-talk