What is happening to the .DMOV field when you move the motor the first time? It should be 1 before you start the move, 0 during the move, and 1 again when the move is done.
Can you send a screenshot of the motorx_all OPI screen when the first move is complete?
I don't think there is another method to be overridden. Perhaps your poller is not setting motorStatusDone_ to indicate that the move is complete. Here are some examples:
Hi Zhibang,
That is not true. You can write the axis::poll function to use the doModbusIO with an absolute address.
And the registers are so far that exceed the maximum of modbusLength of function 3, one modbus port driver is not enough.
This is not a problem if you use absolute addresses and call doModbusIO. You only need to create a single driver. The function code you specify when creating the driver is not important, because you give the function code in each call to doModbusIO.
I have tried to establish 3 mobdus port drivers to read the registers, but only one can work correctly and the other two do not send messages.
That should not happen, so something is configured wrong. But I don't recommend this
approach.
I see the problem with your driver, and why you are getting the error messages.
pModbus_ = new drvModbusAsyn(DM2CAsynPortName, "DM2C", 1, 3, -1, 256, dataTypeUInt16, 0, "DM2C_stepper");
You have the order of the first 2 arguments reversed. It should be:
pModbus_ = new drvModbusAsyn("DM2C", DM2CAsynPortName, 1, 3, -1, 256, dataTypeUInt16,
0, "DM2C_stepper");
Yes, it is definitely possible to use doModbusIO and I think this is what you should do.
Dear Mark,
Thank you for your enlightening advice!
I finally get the motor controller hardware. And I am told that the registers needed to be read locate at 0x0179, 0x1003 and 0x602C.
Since a polling thread of reading should be started in the motor driver, the absolute addressing cannot be used. And the registers are so far that exceed the maximum of modbusLength of function 3, one
I also tried using drvModbusAsyn::doModbus in the motor driver like done in modbusApp/testClient.cpp. But there is also a core dumped.
DM2CDriver.cpp
DM2CController::DM2CController(const char *portName, const char *DM2CAsynPortName, int numAxes, double movingPollPeriod, double idlePollPeriod):
asynMotorController(portName, numAxes, NUM_DM2C_PARAMS, 0, 0, ASYN_CANBLOCK | ASYN_MULTIDEVICE, 1, 0, 0)
asynStatus status;
DM2CAxis *pAxis;
static const char *functionName = "DM2CController::DM2CController";
/* Connect to DM2C controller */
modbusInterposeConfig(DM2CAsynPortName, modbusLinkRTU, 5000, 0);
//startPoller(movingPollPeriod, idlePollPeriod, 2);
The output is as the followings.
#!../../bin/linuxx86_64/leadshine
< envPaths
epicsEnvSet("IOC","iocLeadshine")
epicsEnvSet("TOP","/home/specadm/epics/synApps_6_1/support/motor-R7-1/modules/motorLeadshine/iocs/leadshineIOC")
epicsEnvSet("MOTOR","/home/specadm/epics/synApps_6_1/support/motor-R7-1")
epicsEnvSet("ASYN","/home/specadm/epics/synApps_6_1/support/asyn-R4-36")
epicsEnvSet("SNCSEQ","/home/specadm/epics/synApps_6_1/support/seq-2-2-6")
epicsEnvSet("BUSY","/home/specadm/epics/synApps_6_1/support/busy-R1-7-2")
epicsEnvSet("IPAC","/home/specadm/epics/synApps_6_1/support/ipac-2-15")
epicsEnvSet("MODBUS","/home/specadm/epics/synApps_6_1/support/modbus-R3-0")
epicsEnvSet("EPICS_BASE","/home/specadm/epics/base-3.15.9")
cd "/home/specadm/epics/synApps_6_1/support/motor-R7-1/modules/motorLeadshine/iocs/leadshineIOC"
dbLoadDatabase "dbd/leadshine.dbd"
leadshine_registerRecordDeviceDriver pdbbase
cd "/home/specadm/epics/synApps_6_1/support/motor-R7-1/modules/motorLeadshine/iocs/leadshineIOC/iocBoot/iocLeadshine"
## motorUtil (allstop & alldone)
asynSetAutoConnectTimeout(2)
drvAsynIPPortConfigure("L0","192.168.212.233:502",0,0,1)
asynWaitConnect("L0", 2)
asynSetTraceIOMask("L0",0,4)
asynSetTraceMask("L0",0,9)
DM2CCreateController(DM2C_1_1, L0, 1, 100, 0)
In function DM2CController::DM2CController
asynCommon:registerDriver L0 already registered
asynPortDriver:asynPortDriver ERROR: Can't register port: L0
terminate called after throwing an instance of 'std::runtime_error'
what(): asynPortDriver:asynPortDriver ERROR: Can't register port: L0
Aborted (core dumped)
Do you think it is possible to use drvModbusAsyn::doModbus directly in the motor driver? Or should I focus on how to use multiple modbus read port in one driver?
Best regards,
Zhibang
You should look at testClient.cpp:
You could use the main() function as a model for your constructor. It will be passed just the IP address of the modbus server (ipAddr). The constructor will then have lines like this:
drvAsynIPPortConfigure("DMC2_IP", ipAddr, 0, 0, 0);
modbusInterposeConfig("DMC2", modbusLinkTCP, 5000, 0);
drvModbusAsyn *pModbus = new drvModbusAsyn("DMC2", "DMC2_IP", 0, 2, -1, 256, dataTypeUInt16, 0, "DMC2_stepper");
You now have a pointer to a modbus driver, and can call its public functions.
Your driver then just makes calls like this to do the actual Modbus IO:
epicsInt16 data[45];
pModbus->doModbusIO(0, MODBUS_READ_MULTIPLE_REGISTERS, 0x6000, data, 45);
I think this should be simpler than the model you are using now.
In the ANG1Axis::poll method, the first step is to execute a forced read operation.
ANG1Driver.cpp: line 546
>> status = pasynInt32SyncIO->write(pasynUserForceRead_, 1, DEFAULT_CONTROLLER_TIMEOUT);
I would like to ask why this operation must be performed in order to start a new communication.
What is the purpose of the member pasynUserForceRead_?
If you look at the startup script for the ANG1 example IOC, you will see that the poll time is set to 100 ms.
That means that the modbus driver has created a background thread that is polling those registers at 10 Hz. I believe that the purpose of the pasynUserForceRead_ is to force an immediate read in case the 10 Hz poller data is too stale.
Note that around the time that this motor driver was written I added support for "absolute" addressing to the Modbus driver. That is documented here:
You enable absolute addressing by passing -1 as the start address in the drvModbusAsynConfigure command. In that case your driver can call this function in the driver:
asynStatus doModbusIO(int slave, int function, int start, epicsUInt16 *data, int len);
In the mode you are currently using you need to create multiple modbus drivers in your startup script, each for a single function code and address range. That is convenient when using Modbus with standard EPICS records (ai, ao, mbbi, mbbo, etc.). However,
in the case of a motor driver absolute addressing may be better.
In the absolute mode you can create a single driver and use if for any function code and any address. That might make more sense for this application. You can even create the modbus driver inside the constructor of your motor driver, hiding it from the user.
You just need to pass the asyn port name of the IP port to your constructor.
Dear Mark,
I would like to ask why this operation must be performed in order to start a new communication. What is the purpose of the member pasynUserForceRead_?
The comment in ANF2Driver.cpp at line 504 mentions it, but it also says not sure why this is necessary.
Could you help explain the principle behind it?
By the way, regarding the modbus slave simulator mentioned before, since I haven't received the motor controller yet, the simulator is quite useful for me to start coding.
This is the simulator I am using:
https://modbustools.com/modbus_slave.html
Best regards,
Zhibang
- I change the modbusLength to 4 as what is done in motorAMCI. And I continuously read the values of 5 neighbor registers, like:
If you set the length to 4 then you can’t read 5 registers, you can only read 4. You need to increase the length to at least 5.
This is the first I heard that you are using a Modbus simulator, not the actual motor controller. Is this correct?
- The modbus slave simulator shows that the master and slave only communicated once. And the autoConnect issue is reported at the last time.
Looking back at your original message I understand why they only communicated once. You set the poll time in this command to 0, which means it does not poll.
- drvModbusAsynConfigure("DM2C_1_1_In_Word", "L0", 1, 3, 24576, 2, 0, 0, "DM2C_stepper")
You need to set a non-zero poll time. For example, this will poll every 100 ms.
- drvModbusAsynConfigure("DM2C_1_1_In_Word", "L0", 1, 3, 24576, 2, 0, 100, "DM2C_stepper")
Dear Mark,
Thank you for your response. I can tell when will this issue happen with an example.
> status = pC_->readReg16(0, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
> status = pC_->readReg16(1, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
> status = pC_->readReg16(2, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
> status = pC_->readReg16(3, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
> status = pC_->readReg16(4, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
> readReg16: reg = 0, value= 2020
> readReg16: reg = 1, value= 2021
> readReg16: reg = 2, value= 2022
> readReg16: reg = 3, value= 2023
> 2024/11/23 06:24:07.881 DM2C_1_1_In_Word 4 autoConnect could not connect:
> readReg16: reg = 4, value= 2023
I mean this autoConnect error occurs when I want to send message for the second time.
Best regards,
Zhibang
发件人: "Mark Rivers" <[email protected]>
发送时间: 2024-11-22 23:03:21
收件人: "[email protected]"
<[email protected]>,
沈治邦 <[email protected]>
主题: [SPAM] Re: autoConnect could not connect
when reading a register by modbus relative addressing
I think I see the problem.
That creates a driver that will use function code 3 to read from register location 24576 (0x6000). It will read 2 registers (the Modbus length argument), so it will read
registers 0x6000 and 0x6001.
status = pC_->readReg16(44, &read_val, DEFAULT_CONTROLLER_TIMEOUT);
However, here you are telling it to read relative register 44 (0x2c) which is absolute register 0x602c. That is invalid because you only configured the driver to read 2 registers.
You need to increase the number of registers in the drvModbusAsynConfigure to include all registers you will be accessing.
I am encountering an issue while developing a modbus communication-based motor controller program, similar to the module motorAMCI.
I am attempting to read the values in registers with function code 3 by relative address. For instance, if I want to read the value located in 0x602C, which represents the current position
of the motor. I set the starting address to 0x6000 by the command in st.cmd
Then to read the motor position, I called the function in driver.cpp with sentence
24657 is 0x6000 and 44 is 0x2C, then I believe that the value at 0x602c could be accessed.
The definition of the readReg16 is the same with the method ANG1Controller::readReg16()
Consequently, I am unable to retrieve the correct register value, and an error is showed:
2024/11/22 17:57:00.751 DM2C_1_1_In_Word 2 autoConnect could not connect:
Could someone please help me figure out what might be causing this issue?
Thank you!
Best regards,
Shen Zhibang
