1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024 Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024
Subject: RE: Galil advice for servo motors
From: Mark Rivers via Tech-talk <tech-talk at aps.anl.gov>
To: "Pearson, Matthew" <pearsonmr at ornl.gov>, "tech-talk at aps.anl.gov" <tech-talk at aps.anl.gov>
Date: Wed, 17 Jan 2024 19:58:04 +0000
Hi Matt,
I was able to get the motor to basically move using the motor record PCOF and ICOF fields.  I think I need to use the Galil GDK tuning program to optimize them, and then either save in non-volatile memory or use DPPF as you suggested.  There are other parameters besides just P,I,D, for example notch filter coefficients to avoid resonances.
Sent: Wednesday, January 17, 2024 1:51 PM
To: Mark Rivers <rivers at cars.uchicago.edu>; tech-talk at aps.anl.gov
Hi Mark,
I seem to remember the PID fields in the motor record are restricted to 0-1 values, which is of limited use. The motor record documentation mentions scaling can be done by the driver, but I’m not aware of any model 3 driver doing this and it would be confusing.
In the Galil driver it seems like the functions were implemented:
grep -r set.Gain *
GalilSup/src/GalilAxis.h:  asynStatus setPGain(double pGain);
GalilSup/src/GalilAxis.h:  asynStatus setIGain(double iGain);
GalilSup/src/GalilAxis.h:  asynStatus setDGain(double dGain);
But they are not called in the GalilController class, and there are no associated records for setting KP, KI or KD in the galil_motor_extras.template. So I suspect it was never fully implemented.
It wouldn’t take too much to add driver parameters and records to call those functions, but a quick work around would be to manually set KP, KI or KD by sending strings to $(P)SEND_STR_CMD after IOC init, either via a few ‘dbpf’ commands or a set of stringout records.
Cheers,
Matt
From: Tech-talk <tech-talk-bounces at aps.anl.gov> On Behalf Of Mark Rivers via Tech-talk
Sent: Wednesday, January 17, 2024 1:54 PM
To: tech-talk at aps.anl.gov
Subject: [EXTERNAL] Galil advice for servo motors
Folks,
I have been using the Galil DMC-4183 controllers for stepper motors, both with pulse/direction outputs and on-board amplifiers.
I now am setting up my first servo system with on-board amplifiers and quadrature encoders.   I have a question about the best way to configure and save the PID parameters.  Do people generally using the motor record to configure KP, KI, and KD, or do you use the Galil GDK to configure those and then just save in the non-volatile memory on the controller?
I did not find any discussion of this in the EPICS Galil documentation.
Galil advice for servo motors Mark Rivers via Tech-talk
RE: Galil advice for servo motors Pearson, Matthew via Tech-talk
Prev: RE: Galil advice for servo motors Pearson, Matthew via Tech-talk
Next: Linux for VME devLiv, mca libSIS38XX.a Rong Huang via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <2024
Next: RE: Galil advice for servo motors Mark Rivers via Tech-talk
ANJ, 18 Jan 2024 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·
