Hi, Andrew,
Modified
# source files
(1) base-3.14.9/src/db/dbAccess.c
dbPutSpecial() is added for CCE. This function is just a pipe to
call the static function putSpecial(). dbPutSpecial() is written
by John L. Dalesio and Bernd Schoeneburg originally.
Rather than add a new function, rename the existing static
putSpecial() function to dbPutSpecial() and remove the static
keyword. All callers to the static putSpecial() routine are local to
this source file.
Yes, it's better.
(2) base-3.14.9/src/db/dbScan.c
Register periodic scan tasks at RMT. When the IOC is SLAVE, these
tasks are changed to be inactive.
The #ifndef vxWorks block will not be accepted.
We will remove this block and change the relevant codes.
The changes here that provide the ability to stop periodic scan tasks
represent functionality that should be part of Base, although I may
want to change their implementation somewhat.
The code that registers the periodic scan tasks with the RMT should be
replaced with a call through a global function pointer that the RMT
initialization code can set before iocInit(). By removing any need
for the scan code to perform the registration itself this also drops
the requirement for epicsFindSymbol() and for the rmtDrvIf.h header to
be included in Base.
See comments for Redundancy Patch: rsrv
(3) base-3.14.9/src/dbStatic/dbBase.h
enum type "redUp" and the element of struct dbFldDes "red_update"
are added for CCE. They are added by Bernd Schoeneburg originally.
(4) base-3.14.9/src/dbStatic/dbLexRoutines.c
Deal with pdbFldDes->red_update for CCE, by Bernd Schoeneburg
originally.
This change adds 2 bytes to the field description structure of every
field of every record type in every IOC (that's about 1.7 KBytes for all
the record types in Base, which will be completely wasted on IOCs that
are not redundant) and provides the means for these values to be set
from the DBD file that defines the record type. We might want to
include a switch in the site configuration to turn on/off whether this
structure should include the red_update field.
I note that you did not include any modified record.dbd files; was that
an oversight, or do redundant IOCs have to use a completely different
set of record types? If you have to add a redUp() line to any of the
base record.dbd files then those changes need to go into Base too — you
should never use a record.dbd file in an IOC if a different record.dbd
file was used to generate the record.h file.
This additional property of fields is dedicated to control the updating
of the slave IOC. Up to now we have done only some tests but do not
really know which fields are not to be updated. It is built-in that
fields which have NO_ACCESS set are not updated. Fields which are links
are updated only, if the update-mode is selected to be “Full” in the RMT
settings.
The set of record types is of course same as non-redundant IOCs. If the
red_update property is not specified, the default “RED_CONT_UPDATE” applies.
If the overhead of this feature is too big for some small systems a
compilation switch would be a solution. If a site has no problems with
memory in the IOCs, then the binaries compiled with the switch set, can
be used for redundant as well as non-redundant IOCs. If redundancy is
not needed, the switch can be left off.
In future, when we and others have learned which fields of the records
must not be updated between the redundant IOC nodes, the dbd-files must
be changed. The dbd-files can be the same for all because the additional
text inside will be ignored if the parser in dbLexRoutines has no
information about “red_update”. When the dbd-files are modified these
dbd-changes have to become part of the base of course.
Added
(1) base-3.14.9/src/db/rmtDrvIf.h
The head file for RMT driver interface.
This header is not required if the task registration code is moved into
the redundancy application and hooked into the IOC by setting a global
function pointer before iocInit(). In any case it also appears in the
rsrv patch; only one instance of any header file should be included.
Yes.
- Andrew
Bernd Schoeneburg and Gongfa Liu
Gongfa Liu MKS-2, DESY
phone: +49-40-8998-1642 Notkestr. 85
fax: +49-40-8998-4388 22607 Hamburg
e-mail: [email protected] Germany
- Redundancy Patch: db Andrew Johnson
- Re: Redundancy Patch: db Andrew Johnson
Re: Redundancy Patch: iocsh Liu, Gongfa
Re: Redundancy Patch: libCom Liu, Gongfa
<2007>
2025
2026
Redundancy Patch: iocsh Andrew Johnson
<2007>
2025
2026