Subject: |
Conversion issues (analog device support with float type raw data) |
Ralph Lange <[email protected]> |
To: |
EPICS Core-Talk <[email protected]> |
Date: |
Fri, 09 Jan 2015 11:04:04 +0100 |
All,
The standard conversions that are being done in analog record types
convert between RVAL (integer type) and VAL (float type).
All device supports that are handling float-type raw data (mostly field
buses, PLCs, ASYN, ...) cannot use the record support's conversion
because of the mismatch in data types. They have to clone the code and
do the conversion as part of the device support, RVAL is usually ignored.
This leads to the situation that for some input records (if they are
connected to integer type raw data) the conversion can be tested by
doing caputs to the RVAL field, for the other records caputs to the RVAL
field are just being ignored.
Does anyone have a good idea how to straighten this out in a reasonable
and compatible way?
We could add a second RVAL field of type double to the analog records,
and define yet another DSET.read() return code to trigger a float-float
conversion. That would at least move the conversion code back into the
record scope, where it belongs.
Admittedly this is not really cleaning things up a lot, but as long as
there are no variable type fields in records, I don't see a way around
adding a field for a double type raw value.
What do you think?
~Ralph
- Re: Conversion issues (analog device support with float type raw data) Michael Davidsaver
- Re: Conversion issues (analog device support with float type raw data) Andrew Johnson
Re: dbl output and record name aliases Johnson, Andrew N.
<2015>
2025
2026
Re: dbl output and record name aliases J. Lewis Muir
<2015>
2025
2026
ANJ, 16 Dec 2015 |
Home
News
About
Talk
Base
Modules
Extensions
Distributions
Download
Documents
Links
Licensing