$ALARMCOUNTFILTER count seconds on each PV. Basically, it suppresses the triggering of the alarm until at least 'count' transitions have occurred within a window 'seconds' or the alarm level must hold for 'seconds' long. So if you get a 'nuisance' MINOR once every 30 seconds that lasts about 10 seconds, try count=2, seconds=60. Great for water bubbles in your cooling system... Another techniques is to set up a big chain of dfanout records to push alternately MINOR or NOALARM to the SEVR field (HIGH, HIHI, whatever you are using) based on a top-level bo record with labels like "TUNE" and "RUN". At 8:08 AM -0400 2006/04/05, Terry Carlino wrote: As an AlarmHandler user it has always struck me that there should be a better way to manage alarms. In the real world it is quite common to have a device sitting just on the edge of the MINOR alarm point, creating nuisance alarms. We do not generally manage alarms by actively changing HIGH or LOW, since these are set by system experts. This leaves the user with the choice of disabling the alarm, which means that if the device reaches the MAJOR parameter no alarm will be heard or dealing with the nuisance alarms. Bad enough when a single channel behave such. When you have thousands of channels, not uncommon for a few to have this problem, especially during times of general machine instability, such as start up. It would be nice to be able to separately acknowledge or bypass MINOR alarms, a kind of "yeah we know we need to look at you, you're alright for now call us when you get to the MAJOR setpoint.
ANJ, 02 Sep 2010 |
![]() · Download · Search · IRMIS · Talk · Documents · Links · Licensing · |
