Subject: Re: Sequencer remote pvPut CA delay (specified behavior?)
To: Tobin Weber <[email protected]>, <[email protected]>
Date: Mon, 13 Feb 2017 16:53:03 -0600
Hi Toby,
On 02/13/2017 03:53 PM, Tobin Weber wrote:
> Basically, when the sequencer does a "pvPut" to a PV that
> is located in an IOC that is not local to the machine, the write doesn't
> appear to happen until after a subsequent "pvPut" is performed on a
> local PV.
I don't agree with your analysis of what's actually happening,
discussion below...
> For example, running the template in,
> epics/template/makeBaseApp/top/example
> and modifying the sncExample.stt file to read:
A few inline comments:
> user@pc:~/example$ more exampleApp/src/sncExample.stt
> program sncExample
> int local_pv;
> int remote_pv;
> assign local_pv to "Local:PV";
> assign remote_pv to "Remote:PV";
> monitor local_pv;
> monitor remote_pv;
Since both local_pv and remote_pv are being used with pvPut, you almost
certainly don't want their values to be updated by changes in their
remote values as well, as that causes questions about who wins if you
change the value in your code and the monitor fires at the same time.
There is actually a defined answer to that particular question, but in
most cases variables tend to be used as either inputs (which are
monitored) or outputs (which are pvPut); I would recommend not using a
single variable for both input and output at the same time, so just
remove both monitor statements.
> ss ss1 {
>     state init {
>         when (delay(5)) {
>             printf("sncExample: Startup delay over\n");
>         } state low
>     state low {
>         when (delay(5)) {
>             // Setting a remote PV to 1
>             remote_pv=1;
>             pvPut(remote_pv);
>             // Waiting for 5 seconds
>             epicsThreadSleep(5.0);
>             // Setting a local PV to 1
>             local_pv=1;
>             pvPut(local_pv);
>         } state high
Calling epicsThreadSleep() is also worth avoiding in sequencer actions,
it holds up the sequencer in the middle of the action block and thus
prevents it from processing other transitions that might be triggered
while the delay is in flight. Consider rewriting the state machine and
using a separate when(delay(5)) state transition for the delay instead.
I think doing this will also have an effect on your results; I don't
know the internals of the sequencer, but I suspect it flushes the CA
output queue at the end of each set of actions, not between individual
action statements. Your epicsThreadSleep() call appears in the middle of
the set of actions though, so a flush at the end of the when() {} block
won't have a chance to run until after the second pvPut() call has run
anyway, thus causing the effect that you're seeing.
If you split this transition action into two separate states with a
when(delay(5)) state transition between them (and just don't use
epicsThreadSleep() at all in sequence programs), the flush will happen
before the delay, so the state machine should then do what you're expecting.
>     state high {
>         when (0) {
>         } state low
> with a "bo" record "Local:PV" running in local database, and a "bo"
> record, "Remote:PV" on a different PC, here is what I observed with
> camonitor when I ran the sequencer:
> user@pc:~/EPICS_Apps/example/exampleApp/src$ camonitor Remote:PV
> Local:PV
> Local:PV  2017-02-08 13:58:41.904252 0
> Remote:PV 2017-02-08 13:58:31.645527 0
> Local:PV  2017-02-08 13:58:56.939562 1
> Remote:PV 2017-02-08 13:58:56.940262 1
> It seems like the PV located on a different machine, "Remote:PV", does
> not get written until after "Local:PV" is written. It should be 5
> seconds before. The behavior is the same if states are changed in
> between PV puts.
Ignoring the question of how well synchronized your two IOC's clocks are
(since you're probably running both on the same PC) you should also be
aware that the CA connection to a local PV will usually be faster than
that to a remote one. It's not unexpected that Local:PV processes first
even though the put to Remote:PV was queued first.
This does assume my point about flushing the CA output queue that I
discussed above though, so the 0.0007 second time-difference between
your two processing times is due to the fact that there's more work
involved when the sequencer sends CA messages to an IOC running in a
different process than when it sends them to another thread running in
the same process as the sequence program.
HTH,
- Andrew
Re: Sequencer remote pvPut CA delay (specified behavior?) Tobin Weber
Re: Sequencer remote pvPut CA delay (specified behavior?) Benjamin Franksen
Prev: Sequencer remote pvPut CA delay (specified behavior?) Tobin Weber
Next: Re: Sequencer remote pvPut CA delay (specified behavior?) Tobin Weber
