The problem is the PROBLEM bit, as far as I can see.
Which exact version of the motorRecord are you using ?
The code on latest master looks like this:
/* Get motor-now-moving indicator. */
if (ls_active == true || msta.Bits.RA_DONE || msta.Bits.RA_PROBLEM)
pmr->movn = 0;
if (ls_active == true || msta.Bits.RA_PROBLEM)
clear_buttons(pmr);
if (msta.Bits.RA_PROBLEM)
pmr->stop = 1;
MARK(M_STOP);
else
pmr->movn = 1;
And this was changed here:
commit 303a9208e368ef07839afff67bac69e429af7332
Author: Ron Sluiter <[email protected]>
Date: Fri May 23 15:39:57 2014 +0000
- Set "stop" field true if driver returns RA_PROBLEM true.
- Increment version to 6.9
So my suggestion would be to
a) revert that commit in your motor code base
(git revert 303a9208e368ef07839afff67bac69e429af7332)
b) Remove the line in the model 3 driver that sets the PROBLEM bit
HTH
/Torsten
On 06/07/18 17:13, Mark Davis wrote:
Working with some new equipment here and having some problems getting things
working correctly and hoping someone can give me some tips on what to look for.
We have a couple of new Delta Tau Power Brick LV-IMS controllers that I need to
get working ASAP.
Here is where I am at the moment:
- I have an EPICS 3.14.12.2 IOC running the following:
- The powerPMAC driver from
http://www.observatorysciences.co.uk/deltatau_downloads.php,
- The ssh2 library as described in the manual for the driver
- Version 6-9 of the motor module
- Version 4-23 of the asyn module
- The records included in the example/test IOC config included with the
driver (which includes a motor record)
- The latest PowerMAC IDE application from Delta Tau running on a Windows 7
computer
- A FESTO stepper motor (Model EMMS-ST-57-S-SEB-G2), which includes a brake
and an encoder
- The appropriate power supply from Delta Tau to provide the power for the
controller and (through it) the motor
- A very basic configuration/program running on the Delta Tau (one which I
was told is basically a copy of one of the examples provided by Delta Tau)
which includes definitions for 8 open-loop axes (where the reported position is
based on the # of steps) and 8 read-only virtual axes that report the position
based on the encoder counts.
Both the IOC and the IDE application can connect to the Delta Tau, and I can
open a command-line shell to it via SSH (the controller runs some version of
Linux)
If the IOC is not running, when I use the IDE application to jog the motor it
will move until it reaches the the specified position.
When the IOC is running, if I change the setpoint for the motor record, the
motor moves a bit in the correct direction but quickly stops. This is
presumably because the PROBLEM bit in the motor record's MSTA field is always
set so the motor record is in the major STATE alarm state, causing the record
logic to stop the motor movement.
The brief description of the PROBLEM bit simply says "driver stopped polling,
or hardware problem". But fields in the motor record are frequently updating,
showing any changes in the position of the motor, so I wouldn't think it would
be a polling problem. And the fact that everything appears to work fine when
using the IDE application would seem to imply that there are no hardware problems.
I will be digging through the code trying to trace this back to some
identifiable cause, but if anyone has any experience with this controller and
has some tips on what I might check or should be looking for, that would be
much appreciated.
Mark Davis
NSCL/FRIB
- The ssh2 library
I have this driver installed on a Linux box running EPICS 3.14.12.2 and (as
explained in the doco for this driver) installed the libssh2 library it needs
to open an SSH connection to the controller.
I know almost nothing about the controller itself, but was provided with a very
basic "project" with some code that I was told is mostly a copy of some example
from Delta Tau.
I have
- Delta Tau Power Brick LV-IMS driver Mark Davis
RE: Delta Tau Power Brick LV-IMS driver Mark Rivers
Re: Delta Tau Power Brick LV-IMS driver Pearson, Matthew R.
<2018>
2025
2026
Re: Delta Tau Power Brick LV-IMS driver Mark Davis
<2018>
2025
2026
ANJ, 20 Jul 2018 |
Home
News
About
Talk
Base
Modules
Extensions
Distributions
Download
Documents
Links
Licensing