1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <2018>  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <2018>  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: Parse a variable-length, multi-column waveform in stream device
To: <[email protected]>
Date: Mon, 13 Aug 2018 17:45:18 +0200
Hi Abdalla,
just copying the Makefile isn't enough at least for 8.42 and I guess
it's the same for 8.32. The best way is to follow the steps described in
the following file which is distributed with pcre:
NON-AUTOTOOLS-BUILD.txt
I have just done it for one of my projects so you can just clone the
module and try it:
https://github.com/chrschroeder/pcre
I didn't follow the whole discussion, but if StreamDevice isn't
sufficient to parse something another option could be to read is as an
octet stream and parse the data inside an aSub record. Of course doing
it directly with StreamDevice would be more elegant.
Best regards,
Christoph
On 08/13/2018 03:41 PM, Dirk Zimoch wrote:
On 13.08.2018 14:41, Abdalla  Ahmad wrote:
Dear Ralph
I edited configure/Release and ran make inside stream-master, I got:
Makefile: No such a file or directory
No rule to make target Makefile. Stop
Dear Dirk
I commented PCRE from the configure/RELEASE but I got undefined
reference errors despite the location of PCRE libraries is defined in
/etc/ld.so.conf.d/. "rpm -qa | grep pcre" gave me the same libraries
except version 8.32 and for x86_64, no i686.
I have both, 32 and 64 bit libraries installed, because I build EPICS
for both. You don't need both.
StreamDevice uses the host's native PRCE if either PCRE_INCLUDE
(directory of pcre.h) or PCRE_LIB (location of libpcre.so) is defined
in RELEASE (or both). The problem is that the locations differ between
Linux distros. It uses the EPICS module PRCE if PCRE defined in RELEASE.
It does not use PRCE if neither is defined.
I don't know if anything is different in PCRE version 8.32. What
exactly are your undefined reference errors?
To build PCRE as an EPICS module, I had downloaded the source code
from https://www.pcre.org and added this Makefile:
http://epics.web.psi.ch/software/streamdevice/pcre/Makefile
Worked with PRRE version 7.2.
Thank you all.
Abdalla.
-----Original Message-----
[mailto:[email protected]] On Behalf Of Dirk Zimoch
Sent: Monday, August 13, 2018 2:39 PM
To: [email protected]
device
On 13.08.2018 13:12, Ralph Lange wrote:
If I remember correctly,
the epics-modules/stream does not require you to run configure in the
pcre directory.
Have you tried just building it?
Exactly. The EPICS Makefile replaces the ./configure stuff.
If you have PCRE already installed on your system, you should not
need to build it. PCRE should be available for all Linux systems and
for Windows as well. Install the development package (the once with
the header files).
For example, I have this for my Linux system:
$ rpm -qa | grep pcre
pcre-devel-7.8-7.el6.i686
pcre-devel-7.8-7.el6.x86_64
pcre-7.8-7.el6.x86_64
pcre-7.8-7.el6.i686
Cheers,
~Ralph
On Mon, 13 Aug 2018 at 12:17, Abdalla Ahmad
<[email protected] <mailto:[email protected]>>
wrote:
     Hello Dirk
     No the device does not echo any command.
     I downloaded the latest stream device from github but It needs
PCRE,
     which I got from epics-modules/stream , I took the folder "pcre",
     did "./configure" and make and I get the error
     No rule to make target doc/html/NON-AUTOTOOL-Build.txt needed
by all-am.
     Could there be an option to pass to the configure script do
disable
     doc files? Or maybe I got PCRE module? There is a yum package
     installed called pcre so I added the libraries to ldconfig but
still
     I get undefined reference errors.
     Best Regards,
     Abdalla.
     <mailto:[email protected]>]
     Sent: Monday, August 13, 2018 1:05 PM
     To: Abdalla Ahmad <[email protected]
     <mailto:[email protected]>>; [email protected]
     stream device
     On 13.08.2018 11:33, Abdalla  Ahmad wrote:
      > Hello Dirk
      > That is really impressive, thank you very much. I will
integrate
     your protocol in the IOC and provide you with feedback.
      > Regarding your assumptions:
      > 1. We used the LF terminator with setpoints and readings and it
     works fine so I suppose that is the correct terminator.
      > 2. Will this work with variable buffer length? I mean
instead of
     "3" for example we pass the PV for buffer length.
     Yes. Just make sure that NELM is big enough for your longest
     possible reply.
      > 3. Since the rest are passive scan, If I understand correctly
     processing the first one will process the others right?
     The input from the first one will make the "I/O Intr" records
process.
     However, any input from any other record will be given to the "I/O
     Intr"
     records. Thus if you have other data that matches the format,
those
     records will be processed falsely.
     Does the device echo the command "TBT_IQ <n>"? If not, there is no
     way for the "I/O Intr" records to find out if they should parse
     input or not. Thus they will try to parse everything and if they
     succeed, they will process the record.
      > Best Regards,
      > Abdalla.
      > From: Dirk Zimoch [mailto:[email protected]
      > Sent: Monday, August 13, 2018 12:15 PM
     stream device
      > Hello Ahmad,
      > I have tested a solution using regexp to isolate the
columns. But
     while doing that I found a bug in the regexp converter. Thus to
make
     it work you need to use the latest commit from
     [email protected]:paulscherrerinstitute/StreamDevice.git
      > What I do is the following:
      > 8 waveform records read the 8 columns. One is active, the
other 7
     read the data with "I/O Intr".
      > 8 protocols use regsub (%#/regexp/subst/) to remove the 7
values
     not needed for each waveform.
      > Process waveform 1 and all 8 will get their column.
      > I had to assume some details, e.g. line terminator "\n" and
space
     after each value, including the last column. If that is wrong, the
     protocols need to me modified a bit.
      > As I can't see any special marker for the last line, I do
NOT use
     an InTerminator, because I need to read the whole table as one
     string. In case there is a marker, e.g. an empty line, you may set
     inTerminator accordingly ("\n\n") and remove the "\n" at the
end of
     the 'in' commands.
      > See attached files.
      > Dirk
      > On 12.08.2018 08:22, Abdalla  Ahmad wrote:
      >> Hello Dirk
      >> Thank you for your reply, looking forward for your results. I
     would like to point out some notes:
      >> 1. Regarding variable size, you can expect for sure way larger
     buffer sizes than 1000.
      >> 2. Why the protocol parse you mentioned won't work? I may have
     understood you wrong but In a single line you can parse any number
     you want by skipping the others and I managed to do that by the
same
     format you provided. The first "%i" will get the first number. But
     the problem is if I don't use "ExtraInput = Ignore" the IOC shell
     will be flooded with "x bytes surplus input" error.
      >> 3. Will you implement new parser in stream device to parse
     interlaced arrays? After many trials with stream device, it's
either
     this or to develop a new EPICS driver for the device.
      >> Best Regards,
      >> Abdalla
      >> Sent: Wednesday, August 08, 2018 12:37 PM
     stream
      >> device
      >> Hello Ahmad,
      >> StreamDevice can read variable length arrays. You need to set
     NELM to the maximum number of elements. StreamDevice will set NORD
     to the number of elements found. Modern EPICS versions are able to
     handle variable length arrays when the client sets up a monitor
     using 0 for the requested array length. It should then use the
     current NORD value.
      >> However StreamDevice reads arrays in rows, not columns. If you
     have a waveform record and use { separator=" "; in "%i"; }, stream
     device will repeat the "%i" up to NELM times (or until end of
line,
     until the separator is not found any more or until the conversion
     fails).
      >> But in your case it seems you have interlaced arrays:
      >> a[0] b[0] c[0] d[0] e[0] f[0] g[0] h[0] a[1] b[1] c[1] d[1]
e[1]
     f[1]
      >> g[1] h[1] a[2] b[2] c[2] d[2] e[2] f[2] g[2] h[2]
      >> So StreamDevice will see the first elements of each array, not
     all elements of one array.
      >> StreamDevice would be able to read rows with variable length:
      >> a[0] a[1] a[2] ...
      >> b[0] b[1] b[2] ...
      >> c[0] c[1] c[2] ...
      >> d[0] d[1] d[2] ...
      >> e[0] e[1] e[2] ...
      >> f[0] f[1] f[2] ...
      >> g[0] g[1] g[2] ...
      >> h[0] h[1] h[2] ...
      >> Also this will not help:
      >> in "%i %*i %*i %*i %*i %*i %*i %*i";
      >> Because the first %i reads all the elements in the row before
     even parsing the first %*i.
      >> I need a new syntax to specify interlaces arrays.
      >> The only way I can think to at the moment is to pre-process
the
     input with a regsub which removed the "other" array elements from
     the input, but I need to test that first. It may be quite
     inefficient. Thus if <N> becomes huge (say >1000) parsing may be
     quite slow.
      >> I will tell you soon if I can find a solution...
      >> Dirk
      >> On 08.08.2018 11:09, Abdalla  Ahmad wrote:
      >>> Hi
      >>> We are trying to implement an IOC for the Libera Spark BPM
using
      >>> stream device, one of the tricky commands for example is
TBT_IQ <N>
      >>> which returns a variable-length buffer of turn-by-turn
data. An
     example:
      >>> TBT_IQ 3
      >>> 22 -36  19 -38  16 -31  -3  -31
      >>> 39 -212 29 -212 26 -163 -37 -150
      >>> 39 -175 36 -176 27 -133 -21 -129
      >>> As you can see the output is an array of fixed columns (IQ
      >>> parameters) and variable rows (waveforms length). In a
single line
      >>> you can easily parse and skip any value, but in this
format we
     have two problems:
      >>> 1.Is it possible to parse variable number of IN commands
in the
      >>> protocol file?
      >>> 2.Variable "IN" commands mean variable waveform length, is
this
      >>> possible in EPICS?
      >>> Best Regards,
      >>> Abdalla Ahmad
      >>> Control Engineer
      >>> SESAME
      >>> Allan, Jordan.
      >>> Tel: (+962-5) 3511348 , ext. 265
      >>> Fax: (+962-5) 3511423
      >>> Mob: (+962-7)88183296
      >>> www.sesame.org.jo <http://www.sesame.org.jo>
     <http://www.sesame.org.jo/>
(bb|[^b]{2})
Aufsichtsrat: Vorsitzender Dr. Karl Eugen Huthmacher, stv. Vorsitzende Dr. Jutta Koch-Unterseher
Geschäftsführung: Prof. Dr. Bernd Rech (kommissarisch), Thomas Frederking
Postadresse:
Hahn-Meitner-Platz 1
D-14109 Berlin
https://www.helmholtz-berlin.de
Abonnieren Sie unseren monatlichen Newsletter!<https://www.helmholtz-berlin.de/aktuell/pm/newsletter/>
Subscribe to our monthly newsletter!<https://www.helmholtz-berlin.de/aktuell/pm/newsletter/index_en.html>
Parse a variable-length, multi-column waveform in stream device Abdalla Ahmad
Re: Parse a variable-length, multi-column waveform in stream device Dirk Zimoch
RE: Parse a variable-length, multi-column waveform in stream device Abdalla Ahmad
Re: Parse a variable-length, multi-column waveform in stream device Ralph Lange
Prev: Re: Parse a variable-length, multi-column waveform in stream device Dirk Zimoch
Next: RE: EDM X/Y Plot segfaults Sinclair, John William
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <2018>  2019  2020  2021  2022  2023  2024  2025  2026
Next: RE: Parse a variable-length, multi-column waveform in stream device Abdalla Ahmad
ANJ, 14 Aug 2018 · Home · News · About · Talk · Base · Modules · Extensions ·