1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025
Subject: RE: Weird stream device behavior when using the IOC shell's exit function
To: "'Abdalla Ahmad'" <[email protected]>, 'Dirk Zimoch' <[email protected]>
Cc: "'[email protected]'" <[email protected]>
Date: Wed, 6 Feb 2019 19:27:32 +0000
Hi Abdalla,
I tried one more test.  I changed so my 10 records are not processed periodically but rather the last record in the FLNK block loops back to the first record.  This means the records run as fast as possible, there is no wait between any record processing.
I observed the same behavior as with periodic scanning.  The IOC exited cleanly with both Stream 2.7.7 and 2.8.8.  Again 2.7.7 produced write error messages and 2.8.8 did not.
The difference between our systems is:
-          I am using asyn 4.34 you are using 4.33.  There have been some changes (from Dirk) for error handling in drvAsynIPPort.c.
-          Our databases and devices are different
Sent: Wednesday, February 6, 2019 1:09 PM
To: 'Abdalla Ahmad' <[email protected]>; 'Dirk Zimoch' <[email protected]>
Cc: '[email protected]' <[email protected]>
Hi Abdalla,
I just tried to reproduce your problem.  I have a TCP device that I am using StreamDevice to talk to.  There is a set of 10 input records using Stream that are FLNKed together to read the status information.
I ran 2 IOCs, one built with Stream 2.7.7 and the other with Stream 2.8.8.  I am running R4-34 of asyn on both systems.
This is what I see when the database has SCAN=0.5 second and I type “exit”
Stream 2.7.7
2019/02/06 12:53:59.067 164.54.160.146:5025 write 13
:SENS:PRES?\r\n
2019/02/06 12:53:59.071 164.54.160.146:5025 read 23
:SENS:PRES -0.3308113\r\n
2019/02/06 12:53:59.073 164.54.160.146:5025 write 13
:UNIT:PRES?\r\n
2019/02/06 12:53:59.076 164.54.160.146:5025 read 16
:UNIT:PRES PSI\r\n
2019/02/06 12:53:59.078 164.54.160.146:5025 write 13
:OUTP:STAT?\r\n
2019/02/06 12:53:59.081 164.54.160.146:5025 read 14
:OUTP:STAT 0\r\n
2019/02/06 12:53:59.083 164.54.160.146:5025 write 23
:SOUR:PRES:SLEW:MODE?\r\n
2019/02/06 12:53:59.088 164.54.160.146:5025 read 26
:SOUR:PRES:SLEW:MODE LIN\r\n
2019/02/06 12:53:59.089 164.54.160.146:5025 write 18
:SOUR:PRES:SLEW?\r\n
2019/02/06 12:53:59.097 164.54.160.146:5025 read 27
:SOUR:PRES:SLEW 1.0000000\r\n
2019/02/06 12:53:59.098 164.54.160.146:5025 write 17
:SOUR:PRES:EFF?\r\n
2019/02/06 12:53:59.114 164.54.160.146:5025 read 20
:SOUR:PRES:EFF 0.0\r\n
2019/02/06 12:53:59.115 164.54.160.146:5025 write 26
:SOUR:PRES:LEV:IMM:AMPL?\r\n
2019/02/06 12:53:59.128 164.54.160.146:5025 read 29
:SOUR:PRES:LEV:IMM:AMPL 0.0\r\n
2019/02/06 12:53:59.129 164.54.160.146:5025 write 31
:SOUR:PRES:LEV:IMM:AMPL:VENT?\r\n
2019/02/06 12:53:59.136 164.54.160.146:5025 read 32
:SOUR:PRES:LEV:IMM:AMPL:VENT 0\r\n
2019/02/06 12:53:59.138 164.54.160.146:5025 write 12
:SYST:ERR?\r\n
2019/02/06 12:53:59.143 164.54.160.146:5025 read 23
:SYST:ERR 0, No error\r\n
// Here is where I typed exit
2019/02/06 12:53:59.567 164.54.160.146:5025 write 13
:SENS:PRES?\r\n
2019/02/06 12:53:59.571 164.54.160.146:5025 read 23
:SENS:PRES -0.3330191\r\n
2019/02/06 12:53:59.573 164.54.160.146:5025 write 13
:UNIT:PRES?\r\n
2019/02/06 12:53:59.576 164.54.160.146:5025 read 16
:UNIT:PRES PSI\r\n
2019/02/06 12:53:59.578 164.54.160.146:5025 write 13
:OUTP:STAT?\r\n
2019/02/06 12:53:59.582 164.54.160.146:5025 read 14
:OUTP:STAT 0\r\n
2019/02/06 12:53:59.583 164.54.160.146:5025 write 23
2019/02/06 12:53:59.588 164.54.160.146:5025 read 26
2019/02/06 12:53:59.589 164.54.160.146:5025 write 18
2019/02/06 12:53:59.594 164.54.160.146:5025 read 27
2019/02/06 12:53:59.595 164.54.160.146:5025 write 17
:SOUR:PRES:EFF?\r\n
2019/02/06 12:53:59.603 164.54.160.146:5025 read 20
2019/02/06 12:53:59.604 164.54.160.146:5025 write 26
2019/02/06 12:53:59.618 164.54.160.146:5025 read 29
2019/02/06 12:53:59.619 164.54.160.146:5025 write 31
2019/02/06 12:53:59.636 164.54.160.146:5025 read 32
2019/02/06 12:53:59.637 164.54.160.146:5025 write 12
:SYST:ERR?\r\n
2019/02/06 12:53:59.641 164.54.160.146:5025 read 23
2019/02/06 12:54:00.067 164.54.160.146:5025 write 13
:SENS:PRES?\r\n
2019/02/06 12:54:00.071 164.54.160.146:5025 read 23
:SENS:PRES -0.3326800\r\n
2019/02/06 12:54:00.092 164.54.160.146:5025 write 13
:UNIT:PRES?\r\n
2019/02/06 12:54:00.091928 PACE5000 13BMC_PACE5000:PC1:Units_RBV: asynError in write. Asyn driver says: 164.54.160.146:5025 disconnected
:OUTP:STAT?\r\n
2019/02/06 12:54:00.092161 PACE5000 13BMC_PACE5000:PC1:Control_RBV: asynError in write. Asyn driver says: 164.54.160.146:5025 disconnected
2019/02/06 12:54:00.092 164.54.160.146:5025 write 23
2019/02/06 12:54:00.092386 PACE5000 13BMC_PACE5000:PC1:SlewMode_RBV: asynError in write. Asyn driver says: 164.54.160.146:5025 disconnected
2019/02/06 12:54:00.092 164.54.160.146:5025 write 18
2019/02/06 12:54:00.092536 PACE5000 13BMC_PACE5000:PC1:Slew_RBV: asynError in write. Asyn driver says: 164.54.160.146:5025 disconnected
2019/02/06 12:54:00.093 164.54.160.146:5025 write 17
:SOUR:PRES:EFF?\r\n
2019/02/06 12:54:00.092713 PACE5000 13BMC_PACE5000:PC1:Effort_RBV: asynError in write. Asyn driver says: 164.54.160.146:5025 disconnected
2019/02/06 12:54:00.093 164.54.160.146:5025 write 26
2019/02/06 12:54:00.092909 PACE5000 13BMC_PACE5000:PC1:Setpoint_RBV: asynError in write. Asyn driver says: 164.54.160.146:5025 disconnected
2019/02/06 12:54:00.093 164.54.160.146:5025 write 31
2019/02/06 12:54:00.093123 PACE5000 13BMC_PACE5000:PC1:Vent_RBV: asynError in write. Asyn driver says: 164.54.160.146:5025 disconnected
2019/02/06 12:54:00.093 164.54.160.146:5025 write 12
:SYST:ERR?\r\n
2019/02/06 12:54:00.093252 PACE5000 13BMC_PACE5000:PC1:Error_RBV: asynError in write. Asyn driver says: 164.54.160.146:5025 disconnected
Stream 2.8.8
2019/02/06 13:00:02.070 164.54.160.146:5025 write 13
:SENS:PRES?\r\n
2019/02/06 13:00:02.074 164.54.160.146:5025 read 23
:SENS:PRES -0.3553209\r\n
2019/02/06 13:00:02.076 164.54.160.146:5025 write 13
:UNIT:PRES?\r\n
2019/02/06 13:00:02.080 164.54.160.146:5025 read 16
:UNIT:PRES PSI\r\n
2019/02/06 13:00:02.081 164.54.160.146:5025 write 13
:OUTP:STAT?\r\n
2019/02/06 13:00:02.085 164.54.160.146:5025 read 14
:OUTP:STAT 0\r\n
2019/02/06 13:00:02.087 164.54.160.146:5025 write 23
2019/02/06 13:00:02.092 164.54.160.146:5025 read 26
2019/02/06 13:00:02.093 164.54.160.146:5025 write 18
2019/02/06 13:00:02.101 164.54.160.146:5025 read 27
2019/02/06 13:00:02.103 164.54.160.146:5025 write 17
:SOUR:PRES:EFF?\r\n
2019/02/06 13:00:02.117 164.54.160.146:5025 read 20
2019/02/06 13:00:02.118 164.54.160.146:5025 write 26
2019/02/06 13:00:02.132 164.54.160.146:5025 read 29
2019/02/06 13:00:02.133 164.54.160.146:5025 write 31
2019/02/06 13:00:02.141 164.54.160.146:5025 read 32
2019/02/06 13:00:02.142 164.54.160.146:5025 write 12
:SYST:ERR?\r\n
2019/02/06 13:00:02.147 164.54.160.146:5025 read 23
exit  // Here is where I typed exit
2019/02/06 13:00:02.570 164.54.160.146:5025 write 13
:SENS:PRES?\r\n
2019/02/06 13:00:02.574 164.54.160.146:5025 read 23
:SENS:PRES -0.3560564\r\n
2019/02/06 13:00:02.595 164.54.160.146:5025 write 13
:UNIT:PRES?\r\n
:UNIT:PRES?\r\n
:OUTP:STAT?\r\n
:OUTP:STAT?\r\n
2019/02/06 13:00:02.595 164.54.160.146:5025 write 23
2019/02/06 13:00:02.596 164.54.160.146:5025 write 18
2019/02/06 13:00:02.596 164.54.160.146:5025 write 17
:SOUR:PRES:EFF?\r\n
:SOUR:PRES:EFF?\r\n
2019/02/06 13:00:02.596 164.54.160.146:5025 write 26
2019/02/06 13:00:02.596 164.54.160.146:5025 write 31
2019/02/06 13:00:02.597 164.54.160.146:5025 write 31
2019/02/06 13:00:02.597 164.54.160.146:5025 write 12
:SYST:ERR?\r\n
In both cases the IOC exited cleanly.  However, with 2.7.7 I got write error messages, with 2.8.8 I did not.
I then increased the scan rate to SCAN=0.1 second.  The messages came much faster, but the IOC again exited cleanly with both 2.7.7 and 2.8.8.  Again, 2.7.7 printed write error messages before it exited, 2.8.8 did not.
Sent: Wednesday, February 6, 2019 12:09 PM
The first test I would like you to run is with the recent code, ie. base 3.15.6, asyn 4.33 and stream 2.8.8. Set asynTraceIOMask=2 and asynTraceMask=9 for the TCP port.  Then we will see all communication with the device.  When that is running type “exit”.  Send the complete output, for a few seconds before you type exit, and a few seconds after you type exit.
Sent: Wednesday, February 6, 2019 8:32 AM
To: 'Abdalla Ahmad' <[email protected]>; Dirk Zimoch <[email protected]>
Cc: [email protected]
Ø  I thought the while loop is causing the block so I removed the while loop and put the poll function just like what is done in version 4.18 but I got the same behavior.
Ø  So I think that poll here never returns.
Ø  As the documentation says, poll will block if a negative timeout is provided.
Ø  So I think somehow stream device is passing a negative timeout but I could not verify the timeout value received in the readIt function.
You could edit that code to print the value of readPollmsec just before the while() statement.  That will tell you if stream device is passing a negative timeout.  The purpose of the loop is to retry the poll in case it terminates early with errno=EINTR.  But it will only loop for readPollsec ms at longest.
I suggest you also try independently changing the versions of asyn and Stream to see which has changed to cause the problem.  I suggest using these 2 configurations:
-          Base 3.15.6, asyn 4.16 Stream 2.8.8
-          Base 3.15.6, asyn 4.33, Stream 2.5.1
I have a simple StreamDevice IOC that I will test today to see if I can reproduce the problem.
Sent: Wednesday, February 6, 2019 6:45 AM
To: Mark Rivers <[email protected]>; Dirk Zimoch <[email protected]>
Hello Mark
Just would like to share some findings:
I cloned the latest stream device 2.8.8 and I still get the same behavior. So I investigated the backtrace a little bit specifically the thread you mentioned it is causing the deadlock.
In asyn 4.33 file asyn/drvAsynSerial/drvAsynIPPort.c function "readIt", line 725 is the poll function call causing the deadlock. I thought the while loop is causing the block so I removed the while loop and put the poll function just like what is done in version 4.18 but I got the same behavior. So I think that poll here never returns.
As the documentation says, poll will block if a negative timeout is provided. So I think somehow stream device is passing a negative timeout but I could not verify the timeout value received in the readIt function.
Best Regards,
Abdalla.
Sent: Wednesday, February 06, 2019 9:12 AM
To: 'Mark Rivers' <[email protected]>
Hello Mark
This is just to confirm that I re-built the old setup on CentOS 7 x64; base 3.14.12.3, asyn 4.18 and stream 2.5.1 and everything works fine. I don't even get the asynWrite error messages.
Best Regards,
Abdalla.
Sent: Tuesday, February 05, 2019 5:47 PM
To: Abdalla Ahmad <[email protected]>
You can now use asynSetTraceIOMask and asynSetTraceMask to monitor the communication.  If you enable that before you type “exit” we can see what is happening.
I view the problem exiting the IOC as an annoyance but not something that has to be fixed immediately.  You can always just type CTRL-C.
Sent: Tuesday, February 5, 2019 8:17 AM
Subject: Re: Weird stream device behavior when using the IOC shell's exit function
Well I never thought of checking the client, I will test it and come back.
I forgot to mention that the device is being controlled through standard telnet port 23. Does it make a difference for stream device to work with a well known port number?
On Tue, Feb 5, 2019 at 4:14 PM +0200, "Mark Rivers" <[email protected]> wrote:
Is your device working correctly, or is it timing out? I wonder if the exit problem is because Stream is polling constantly and never releasing the lock so the epicsExit thread can never run?
Sent from my iPhone
> On Feb 5, 2019, at 7:23 AM, Abdalla Ahmad  wrote:
> Hello Mark
> Including asyn.dbd file did the trick. Looking forward for your thoughts on the exit issue.
> Thank you for your time.
> Abdalla.
> -----Original Message-----
> From: Mark Rivers [mailto:[email protected]]
> Sent: Tuesday, February 05, 2019 3:19 PM
> To: Abdalla Ahmad
> OK, I understand the problem with the missing asyn commands.  You do have these commands in your help output:
> drvAsynIPPortConfigure          drvAsynIPServerPortConfigure
> drvAsynSerialPortConfigure
> That tells me that your application dbd file is including drvAsynIPPort.dbd and drvAsynSerialPort.dbd, but it is not including asyn.dbd.  It also explains why it used to work, and now it does not.  Previously drvAsynIPPort.dbd and drvAsynSerialPort.dbd themselves included asyn.dbd.  However, recent EPICS base releases no longer allow a dbd file to be loaded more than once, so asyn.dbd was removed from drvAsynIPPort.dbd and drvAsynSerialPort.dbd.  Now your application must explicitly include asyn.dbd.
> I think this is independent of the IOC exiting issue, but please include asyn.dbd and see if you still have that problem.
> Mark
> ________________________________
> From: Abdalla Ahmad
> Sent: Tuesday, February 5, 2019 6:34 AM
> To: Mark Rivers
> Hi Mark
> I attached the help output in help.txt. For the database nothing is I/O scanned, standard 1 second rate as in the attached database. I also checked the protocol file but nothing seems strange.
> While writing the email I thought of increasing the scan rate to 5 seconds and it works. I still get the same asynError in write but the IOC eventually exits. Even if it exits gracefully now, it is still a problem because we need the scan rate to match the IMG ones. As I told you before it used to work on the old setup without any problems. Is there anything we can investigate?
> Best Regards,
> Abdalla.
> Sent: Tuesday, February 05, 2019 2:20 PM
> To: Abdalla Ahmad
> Hi Abdalla,
> Your IOC is clearly built OK with asyn because you have threads that are in asyn functions.
> Thread 13 (Thread 0x7fffed943700 (LWP 29173)):
> #0  0x00007ffff6034f0d in poll () from /lib64/libc.so.6
> #1  0x00007ffff7926c14 in readIt (drvPvt=0x70eb30, pasynUser=0x79e4a8, data="" ">", maxchars=2048, nbytesTransfered=0x7fffed942ba0, gotEom=0x7fffed942b90)
>    at ../../asyn/drvAsynSerial/drvAsynIPPort.c:726
> #2  0x00007ffff7930886 in readIt (drvPvt=0x70fbb0, pasynUser=0x79e4a8, data="" ">", maxchars=, nbytesTransfered=0x7fffed942ba0, eomReason=0x7fffed942b90)
>    at ../../asyn/interfaces/asynOctetBase.c:233
> #3  0x00007ffff793a563 in readIt (ppvt=0x70fcb0, pasynUser=0x79e4a8, data="" ">", maxchars=63, nbytesTransfered=0x7fffed942ca0, eomReason=0x7fffed942c70)
>    at ../../asyn/miscellaneous/asynInterposeEos.c:231
> #4  0x00007ffff7bab5f5 in AsynDriverInterface::readHandler (this=this@entry=0x79e2e0) at ../AsynDriverInterface.cc:960
> #5  0x00007ffff7bacd08 in handleRequest (pasynUser=) at ../AsynDriverInterface.cc:1503
> #6  0x00007ffff791c9f3 in portThread (pport=0x70ece0) at ../../asyn/asynDriver/asynManager.c:902
> #7  0x00007ffff6b6f7fc in start_routine (arg=0x70f290) at ../../../src/libCom/osi/os/posix/osdThread.c:403
> #8  0x00007ffff5d2ce25 in start_thread () from /lib64/libpthread.so.0
> #9  0x00007ffff603fbad in clone () from /lib64/libc.so.6
> Thread 12 (Thread 0x7fffeda44700 (LWP 29172)):
> #0  0x00007ffff5d30995 in pthread_cond_wait@@GLIBC_2.3.2 () from /lib64/libpthread.so.0
> #1  0x00007ffff6b71f3b in epicsEventWait (pevent=0x70d520) at ../../../src/libCom/osi/os/posix/osdEvent.c:103
> #2  0x00007ffff6b6b029 in epicsEventMustWait (id=) at ../../../src/libCom/osi/epicsEvent.cpp:125
> #3  0x00007ffff791c40c in portThread (pport=0x70d050) at ../../asyn/asynDriver/asynManager.c:788
> #4  0x00007ffff6b6f7fc in start_routine (arg=0x70d590) at ../../../src/libCom/osi/os/posix/osdThread.c:403
> #5  0x00007ffff5d2ce25 in start_thread () from /lib64/libpthread.so.0
> #6  0x00007ffff603fbad in clone () from /lib64/libc.so.6
> I don't understand why the asyn iocsh commands would not be available.
> Please send the complete output of the iocsh "help" command.
> The hang at shutdown appears to be caused by this thread:
> Thread 1 (Thread 0x7ffff7fda740 (LWP 29161)):
> #0  0x00007ffff5d3351d in __lll_lock_wait () from /lib64/libpthread.so.0
> #1  0x00007ffff5d2ee36 in _L_lock_870 () from /lib64/libpthread.so.0
> #2  0x00007ffff5d2ed2f in pthread_mutex_lock () from /lib64/libpthread.so.0
> #3  0x00007ffff6b71a76 in mutexLock (id=0x70ef60) at ../../../src/libCom/osi/os/posix/osdMutex.c:46
> #4  epicsMutexOsdLock (pmutex=0x70ef60) at ../../../src/libCom/osi/os/posix/osdMutex.c:130
> #5  0x00007ffff7917e9b in lockPort (pasynUser=0x710668) at ../../asyn/asynDriver/asynManager.c:1741
> #6  0x00007ffff7925876 in cleanup (arg=0x70eb30) at ../../asyn/drvAsynSerial/drvAsynIPPort.c:246
> #7  0x00007ffff6b65ce3 in epicsExitCallAtExitsPvt (pep=) at ../../../src/libCom/misc/epicsExit.c:95
> #8  epicsExitCallAtExits () at ../../../src/libCom/misc/epicsExit.c:113
> #9  0x00007ffff6b66088 in epicsExit (status=0) at ../../../src/libCom/misc/epicsExit.c:181
> #10 0x000000000040544d in main (argc=, argv=) at ../iocMain.cpp:21
> So the epicsExit function is hung up in the drvAsynIPPort::cleanup function.  It has called lockPort, but cannot get that mutex.
> No other thread is waiting for a mutex, so it is not a traditional deadlock.  But it seems that some other thread does have that mutex and is blocking the epicsExit thread from continuing.
> It is probably this thread, which is in StreamDevice.
> Do you have StreamDevice records that are I/O Intr scanned?
> Mark
> From: Abdalla Ahmad
> Sent: Tuesday, February 5, 2019 5:53 AM
> To: Mark Rivers
> Hi Mark
> No command available which starts with asyn. I cloned the latest asyn from github with the same behavior.
> For the gdb part, attached is the stack trace from gdb for all pending threads.
> Best Regards,
> Abdalla.
> Sent: Monday, February 04, 2019 4:52 PM
> To: Abdalla Ahmad
> At the iocsh prompt when the IOC is still running type the command
> help
> It should show a complete list of commands that the iocsh understands.  See which ones start with "asyn".
> Mark
> From: Abdalla Ahmad <[email protected]>
> Sent: Monday, February 4, 2019 8:44 AM
> Hello Mark
> I will apply the gdb tip and get back to you. For the asyn commands, I don't see any asyn command when I type exit.
> Get Outlook for Android
> On Mon, Feb 4, 2019 at 4:33 PM +0200, "Mark Rivers" <[email protected]> wrote:
> Hi Abdalla,
>> asynError in write. Asyn driver says: device:port disconnected.
> During IOC shutdown asyn does close all TCP ports.  However, record processing should have already been shut down, so I don't understand why you are getting that message from Stream.
> Another problem we are facing with this new setup is that I can't find some asyn IOC shell function like asynTraceMask for example. The IOC is configured properly in RELEASE and src/Makefile. Is there anything we miss in the new setup?
>> But eventually the IOC exits. For the gamma controllers we get something really strange.
>> There a point in the database where the IOC never exits, the exit command just freezes and Ctrl-C is the only way to shut down the IOC.
> I don't think I have seen that with Stream on any version of Stream/asyn/base that I have used.  That includes base 3.14.12, 3.15.5, 7.0.2.
> If you run the IOC with gdb then when you type exit and it hangs do the following:
> - Type Ctrl-C
> - Enter the gdb command
> thread apply all bt
> That will show you the current stack trace for all threads.  You can then see what is blocking the threads.
> The command is not "asynTraceMask" it is "asynSetTraceMask" or "asynSetTraceIOMask".
> What asyn commands do you see if you type "help" at the iocsh prompt?
> Mark
> From: [email protected]  on behalf of Abdalla Ahmad via Tech-talk
> Sent: Monday, February 4, 2019 1:41 AM
> To: [email protected]
> Subject: Weird stream device behavior when using the IOC shell's exit function
> Hi
> We are using the following setup to test control of the agilent XGS gauge controllers and Gamma ion pump controllers:
> 1.       EPICS Base 3.15.6
> 2.       Asyn R4-33
> 3.       Stream R2-7-7c
> For agilent controllers we get the following error:
> But eventually the IOC exits. For the gamma controllers we get something really strange. There a point in the database where the IOC never exits, the exit command just freezes and Ctrl-C is the only way to shut down the IOC. For now I can see that this behavior occurs because more DB substitutions are configured which means more PVs and more controllers. But that was not the case when we had:
> 1.       EPICS Base 3.14.12.3
> 2.       Asyn R4-18
> 3.       Stream R2-5-1
> Where the IOC exits with no errors or freezing. Should we upgrade our support modules or change the EPICS base?
> Best Regards,
> Abdalla Ahmad
> Control Engineer
> SESAME
> Allan, Jordan.
> Tel: (+962-5) 3511348 , ext. 265
> Fax: (+962-5) 3511423
> Mob: (+962-7)88183296
> http://www.sesame.org.jo/
</[email protected]</[email protected]</[email protected]
Weird stream device behavior when using the IOC shell's exit function Abdalla Ahmad via Tech-talk
Re: Weird stream device behavior when using the IOC shell's exit function Mark Rivers via Tech-talk
Re: Weird stream device behavior when using the IOC shell's exit function Abdalla Ahmad via Tech-talk
RE: Weird stream device behavior when using the IOC shell's exit function Mark Rivers via Tech-talk
RE: Weird stream device behavior when using the IOC shell's exit function Abdalla Ahmad via Tech-talk
Prev: RE: Weird stream device behavior when using the IOC shell's exit function Mark Rivers via Tech-talk
Next: Re: Weird stream device behavior when using the IOC shell's exit function Dirk Zimoch via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025
Next: RE: Weird stream device behavior when using the IOC shell's exit function Abdalla Ahmad via Tech-talk
ANJ, 07 Feb 2019 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions ·
